Are you putting the oil back in the system?
Do you do it something like this?
1) Valve off middle port on manifold
2) Hook up to a vapor port and purge your hoses then close ball valve at end of both hoses.
3) Hook up to oil ports, check oil pressure.
4) Close hose valves.
5) Hook up to suction and liquid line. Blow high side to low.
6) Close valve on high side hose fitting. Use suction to remove liquid from hoses.
7) Remove hose
Just wondering because I've never seen anyone else check oil pressure. I haven't been putting the oil back in the system but I'm gonna start doing it this way if that's how its done.
That's the correct way to do it. If by oil ports you mean outlet of oil pump and suction port so you can calculate the differential and determine the net oil pressure. You will want to find the specs for the type of compressor you have so you know what oil pressure is good and where the point is that the pump needs replacement (or other problem).
Ball valves on hose ends are great as you can control what enters or leaves your hoses. Not necessarily so with valveless hoses or sealquik hose ends.
Think the procedure through everytime as one missed step and you can introduce air, refrigerant or oil into the system if you do it wrong.
That's what I like about this site. I learned that procedure myself by thinking it out but reading posts on hvac-talk is like having a journeyman at your side teaching you! :beer:
Tapping the suction service valve for the net oil pressure is not the correct way. It.s crankcase pressure you want
Right you are. I should have clarified that.
For the reading to be accurate, take the suction reading on the compressor body. Do this because there is a small pressure drop across the service valve and barrel of the motor, which could affect the readings.
Good catch D√16!
Actually, when doing a lot of oil service on a piece of equipment, I'll connect my gauges from liquid to suction and allow refrigerant to flow through them for a short time.
This, effectively cleans the inside of the hoses.
The oil came from within the system. I'm putting it back there so that it doesn't wind up all over the floor or the back of my truck.
I'm with you on that. Only thing worse than POE everywhere is dye from some system charged with it and not labeled. You can only find out after it's everywhere where it shouldn't be. New customers always get the old gauges to find out if that $@#* is in there. I only put it in if I lose a contract. KIDDING! I never lose a contract.
also. lets say you have blow by and your inflating your crankcase. Between the motor barrel area and the crankcase, there is a quarter sized opening which allows oil returning from suction to drain into the crankcase chamber, which is fitted with a pressure actuated check valve. If the crankcase inflates, this check valve closes. So if you tapped your suction service valve and not your crankcase, you would not see this inflation.
I can not seem to get this through my guys heads. I carry taps and swivel t's just for this purpose. I never seen one compressor here which was tapped before I came here. It's a 5 minute deal. Just do it.
I wish racks would start being fitted with transducers so I can read net oil on all my pumps. I saw a Kroger where they had the lead pumps on freeq drive, and they were monitoring the net oil this way. They would only let the pump down to half spin, since net oil drops off on recips when you spin slower than that.
So far I have purchased 2 sets of SMAN3, 3 digimon, and 2 Testo. One SMAN3 and one digimon were broken due to static electricity on a roof. The other SMAN3 plastic piece broke on the manifold (probably because there was no hard case for it). 2 of the digimons are still working, and the Testos are damn near brand new.
The Testos are a little finicky. You have to have the thermocouple plugged in before you turn it on, and the settings are not entirely user friendly. I bought the Testos because they had very good reviews on Amazon and have a 2 year warranty.
There is no more to a Testo than any other digital. I have a Testo 570 that prints, measures amps and out door ambient. It does much more and for me that is a necessary option to have on a lot of my work.
I own SMAN 3 and 4 and two sets of Ak 900s. Yeah the AKs are durable but they don't have all the capabilities of my 570. But they get used a lot. I have one for evacuation and system test-out and one for service work only..
It boils down to what you need. If you have no need for documentation than stick with an AK or an Sman 4. Keep the SMAN in a case. I do.