    Hmm

    we use a brand called diversatech or something like that. You open a can like brake fluid can and pour into this special container. the container connects to nitrogen and the nitrogen generates the pressure. Then we purge with straight nitrogen.

    The other day we installed a 5 ton Carrier and coil but forgot to flush the line set. It didn't want to work right at all. sub cooling 50 and super heat 50. Recovered all 410a, flushed like crazy the entire system, new dryer, 400 micron vac, weighted in charge and then everything was fine.

    OOPPPS
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  2. #28
    Join Date
    Dec 2006
    Location
    Goodyear, AZ
    Posts
    197
    Read the MSDS for RX11 it will alarm the hell out of you. From the MSDS of rx11

    1,2-dichloroethylene 200 ppm, 8 & 12 hour TWA

    1,2-Dichloroethene, commonly called 1,2-dichloroethylene or 1,2-DCE, is an organochloride with the molecular formula C2H2Cl2. It is a highly flammable, colorless liquid with a sharp, harsh odor. It can exist as either of two geometric isomers, cis-1,2-dichloroethene or trans-1,2-dichloroethene, but is often used as a mixture of the two. It is minimally soluble (5090 mg/L for the cis-isomer[1]) in water, and soluble in ethanol, diethyl ether, acetone, benzene, and chloroform.
    1,2-DCE is used as a solvent for waxes, resins, polymers, fats, and lacquers. It is also used as an intermediate in the preparation of other chlorinated solvents.
    The major health effect of inhalation of vapors of 1,2-DCE is narcosis; it has been used in a combination with diethyl ether as an anesthetic. In high concentrations, exposure to 1,2-DCE causes central nervous system depression; in milder exposures, it can produce nausea, vomiting, weakness, tremor, epigastric cramps, burning of the eyes and vertig

  3. #29
    Join Date
    Jun 2007
    Location
    Greenwood Indiana (Indianapolis)
    Posts
    420

    Hmm

    Quote Originally Posted by rdholder View Post
    Read the MSDS for RX11 it will alarm the hell out of you. From the MSDS of rx11

    1,2-dichloroethylene 200 ppm, 8 & 12 hour TWA

    1,2-Dichloroethene, commonly called 1,2-dichloroethylene or 1,2-DCE, is an organochloride with the molecular formula C2H2Cl2. It is a highly flammable, colorless liquid with a sharp, harsh odor. It can exist as either of two geometric isomers, cis-1,2-dichloroethene or trans-1,2-dichloroethene, but is often used as a mixture of the two. It is minimally soluble (5090 mg/L for the cis-isomer[1]) in water, and soluble in ethanol, diethyl ether, acetone, benzene, and chloroform.
    1,2-DCE is used as a solvent for waxes, resins, polymers, fats, and lacquers. It is also used as an intermediate in the preparation of other chlorinated solvents.
    The major health effect of inhalation of vapors of 1,2-DCE is narcosis; it has been used in a combination with diethyl ether as an anesthetic. In high concentrations, exposure to 1,2-DCE causes central nervous system depression; in milder exposures, it can produce nausea, vomiting, weakness, tremor, epigastric cramps, burning of the eyes and vertig
    So don't be smoking at the other end of the pipes holding a booty over them, LOL
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  4. #30
    Join Date
    Mar 2012
    Location
    Orange City , Fl.
    Posts
    1
    We use the pressurized cans with the nozzel that has a rubber stopper on it then we shoot nitro three to five good blasts through both lines and have had very good results good luck .

  5. #31
    Join Date
    Dec 2006
    Location
    Goodyear, AZ
    Posts
    197
    Quote Originally Posted by Kevin Weaver View Post
    So don't be smoking at the other end of the pipes holding a booty over them, LOL
    Before using any of these chemical Read the MSDS.

    The major health effect of inhalation of vapors of 1,2-DCE is narcosis; it has been used in a combination with diethyl ether as an anesthetic. In high concentrations, (1,2-dichloroethylene 200 ppm, 8 & 12 hour TWA) exposure to 1,2-DCE causes central nervous system depression; in milder exposures, it can produce nausea, vomiting, weakness, tremor, epigastric cramps, burning of the eyes and vertig

    I used R-11 to flush back in 1975 until Carrier and other manufactory would not warranty system that was flush with R-11.

  6. #32
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    2,454
    Still waiting very patiently for any of the manufactures of these cleaning agent stuff to provide approvals from any of the major compressor manufactures.

    Bob, has there been attempts with your company to contact or get approval from Emerson/Copeland, for example. If so what was their response? I am being advised that Copeland, Tecumseh, Danfoss, Carlysle...all of which I have talked with concerning these products, will void any warranty if they find that these flushes have been used? I really wish to find the magic solution to improve burn out clean-ups or prep old linesets when converting from R22 to R410a. But true believer in following compressor manufacturer guidelines and just can get any of them to budge on approving this stuff.

    Let me know what your running into on your end with the manufactures, curious what their reasoning is for not approving your product. Maybe they wish not to sacrifice the funds to run lab tests and analysis? Who knows. Not for or against any flushes, just interested why compressor manufactures dislike them.

    Until I hear differently will just utilizing the current guidelines of the old R22 method. Even with the current hike in R22 pricing, still cheaper than half the flushes.

  7. #33
    Join Date
    Jan 2012
    Location
    Rockledge, Florida
    Posts
    52
    This is a great question. Look if the compressor manufacturers find any brand of flushing solution in their compressor they will invalidate the warrantee and they should since a flushing agent will destroy a compressor since it will remove the oil from the wear surfaces.

    However when a good flushing solution is used and followed by a proper evacuation then there will not be any flushing solution residue in the system. QwikSystemFlush evaporates completely and leaves no residue. QwikSystemFlush evaporates much much easier than water so if you pull even a slight vacuum, which is not enought to get the water out, the SystemFlush is still all gone.

  8. #34
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    2,454
    I can see your point and appreciate your reply. If the product(s) out there utilized for flushing linesets etc, if used properly, are worlds above the usual clean-out procedures manufactures outline, then just curious why they would not adopt them, but discourage it?

    If I was a flushing agent manufacturer, much like yourself, I would be all over the compressor manufactures to join forces to re-write the procedures. Kind of see this like the oil manufactures that are on the compressor manufactures preferred lists. Not that the oil from BVA, NuCalgon, or Virginia (Parker) is any different, but seems compressor manufactures like to suggest Mobil (Exxon) oil products...so Mobile outsells the rest by shear fact they are the chosen ones.

    Not sure if your dealing with politics, deaf ears, or what, but still love to see approval or acceptance from these guys.
    Last edited by slctech; 04-13-2012 at 09:52 AM.

  9. #35
    Join Date
    Dec 2006
    Location
    Goodyear, AZ
    Posts
    197
    Just got off the phone with Rex Martin of Tecumseh Compressor, he affirmed that Tecumseh will null and void the compressor warranty if they find out that a system been cleaned with a flush like rx11. They have found contaminants in systems that have been flush into Tecumseh systems and compressor.

  10. #36
    Join Date
    Jan 2012
    Location
    Rockledge, Florida
    Posts
    52
    Let's be clear, I am not talking about any flushing product except ours but if any manufacturer has any data to show QwikSystemFlush leaves a residue then I would like to see that data published so we can challenge the results. We would get an independent test laboratory to repeat their claims for validity. What I can tell you is that QwikSystemFlush leaves no reside in the system after evacuation and we have verified this in many many experiments. I challenge anyone with data to the contrary to show their data. Our independent test result data is at
    http://www.epatest.com/flush/test-results.pdf

    Also we are an OEM, Mainstream manufactures all the Improved Environmental Control Units (IECUs) and modular refrigeration units for the US military. We use both Copeland and Tecumsch compressors in the units and Require QwikSystemFlush be used after a burnout and this has never invalidated a compressor warrantee.NEVER!!! Just so you know you can't just get out of a financial responsibility to replace a compressor without technical data to support your invalidity. I have never seen an negative data on QwikSystemFlush

  11. #37
    Join Date
    Apr 2012
    Location
    Pasadena,Maryland
    Posts
    265
    Any company I ever worked for only used rx11.i can't say I've ever had any problems,but then again would I have any problems if I didn't flush at all.i have heard from a major refrigerant manufacter that flushing isn't doing any good.you just need to make sure you pull a good long evacuation.of course equipment manufacturer require the flush for their warrantys to apply.

  12. #38
    Join Date
    Jan 2012
    Location
    Rockledge, Florida
    Posts
    52
    Wish you would try QwikSystemFlush in the orange aerosol can. Independent tests show it works better and it cost quite a bit less! Send my your work address and I will send you a can to try for free
    We have nothing to hide

  13. #39
    Join Date
    Apr 2012
    Location
    Pasadena,Maryland
    Posts
    265
    Quote Originally Posted by Bob_Scaringe View Post
    Wish you would try QwikSystemFlush in the orange aerosol can. Independent tests show it works better and it cost quite a bit less! Send my your work address and I will send you a can to try for free
    We have nothing to hide
    My company's work address is bill
    Bill Myers heating & cooling
    15604 Darwin ct
    Laurel,md,20707

Page 3 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event