    RTAA 70 ton refrigerant storage to low side

    Serial number U96A32142

    Any chance I can migrate and recover over isolate and store charge in lowside (58 pounds) to change out a saturated condenser temp sensor?

    r404a

  2. #2
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    Never have tried it, I've always pulled the charge and used the oppurtunity to weigh the charge! Be interested to see if anyone says it possible!
    I'm good at making things cold...You can ask my first two wives!

  3. #3
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    Quote Originally Posted by r404a View Post
    Serial number U96A32142

    Any chance I can migrate and recover over isolate and store charge in lowside (58 pounds) to change out a saturated condenser temp sensor?

    r404a
    Absolutely, assuming the service valves hold.

  4. #4
    Join Date
    Aug 2006
    Location
    Columbus Ohio
    Posts
    1,980
    I have done it on the 100 ton compressors. No problems.
    UA LU189

    10mm, because it's better than .45acp

  5. #5
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,135
    thanks for the replies

    r404a

  6. #6
    Join Date
    Feb 2012
    Location
    EVERYWHERE
    Posts
    224
    You can if you run the other circuit so the evap is cold.

  7. #7
    Join Date
    Dec 2003
    Location
    45th Parallel
    Posts
    954
    I've done it also. When you start it up, pull the load solenoid wire and run unloaded for 5-10 min. Shouldn't have any problems.
    “If your work speaks for itself, don't interrupt.” ~Henry J. Kaiser

  8. #8
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    466
    if you can change the sensor without removing the saturated condenser r-22, there is indeed a respect SB

  9. #9
    Join Date
    Mar 2007
    Posts
    3,103
    If you have two chillers, and the loop is colder than the outside ambient temp. you can run chilled water through the chiller you are going to repair and that will migrate most of the liquid into the evaporator, but you have to manually open the EXV first. The alternative is to run the other circuit to get the evaporator cold. Either way, you will have to open the EXV, migrate the liquid, close the liquid and suction service valves, and vapor recover down to a couple PSI.

    If the valves hold, you should be outta there in a few hours.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event