Looks like some flame impingement at the flue opening. Could be a partially blocked cross over vane on the in-shot burner or some other anomaly, like low gas pressure in the manifold. You say you're getting a really good deal on the house and expecting to have to fix up a lot of things isn't something that should be a surprise. Rest assured the heat exchanger has a lifetime warranty if you can convince the wholesaler you've owned the house since the unit was installed. That's the requirement on a "Limited" lifetime warranty. Otherwise, you can run it till it fails and then have a new one, properly sized using Manual 'J' installed for greater comfort.