    Cool Are the dyes UV leak detectors good and which brandname is the best?

    I´ve read a lot about this A/C findind leaks methods but I haven´t tried anyone yet.
    What do you recommend on this issue please? is this method good?

    Thanks

  2. #2
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    I've been doing service in this field, for over thirty years. I'ved never used a dye in a system and never will. However, I've seen plenty of systems messed up from the dyes, and still leaking

  3. #3
    Join Date
    Feb 2009
    Posts
    115
    Post Likes
    i've never seen a system messed up from dye. Not saying it doesn't happen but i have never seen it. We do use dye. I personally try not to, but sometimes it is a good alternative. I carry the yellow jacket plunger type dye on my truck and have had success with it in the past. I don't believe it is the best way to leak check but when you have tried everything else it's a good alternative in my opinoin.

  4. #4
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    615
    Post Likes
    ALL dyes are not bad. Just like how mixing new refrigerants with old mineral oils can cause lack of lubrication problems, using the proper dye for a certain type of system is very important. We are talking about chemical reactions with both.

    You first want to ensure you are not voiding a manufacturer warranty, then ensure you obtain the proper dye suitable for both the refrigerant and lubricant type. Then ensure you have an applicator that will not fail, even when not under pressure, an applicator that fails can be very messy. Know exactly how to apply the dye by asking others that have actually done it before attempting the job. This is ESPECIALLY true for applications under system pressure!

    My bag of leak detection tools contains, Ultrasonic, halide, several types and brands of electronic, big blue soap, several brands of dyes, and the most useful - my EYES. I have found at least as many leaks on systems by first looking for refrig oil and obvious faults such as sketchy welds, pinched tubing, bad or overtightened flares, rubthroughs, cracks, pickled evaporator coils, etc, than I have with any other method.
    You really should perfect your leakchecking skills with other types before jumping into the dye pool.

    Generally speaking, except for preventive maintenance applications, I try dye applications when other avenues have been exhausted. I have found many leaks over the years that escaped other means as the dye will indicate where the refrigerant has leaked even if it is not leaking at the time I am there.

    When applied before there is a leak, a regular inspection with a UV light will catch small leaks before the sight glass or lack of performance indicates there is a leak. It also shows you where to start before pressuring up a flat system with nitro, sometimes allowing you to bypass nitro until the leak has been repaired.

    I had a supervisor who took pride in never using a computer by the time he retired. Once he retired and was bored, he started using computers and now builds them from scratch. He proudly said "I have been working for "x" amount of years and have never used a computer and never will, those things cause all sorts of problems!".

    The moral of the story is that sometimes you have to look past the "bad reports" of something to find out it's attributes.

    As for brandnames, I think highly of Ritchie YellowJacket dyes, dye applicators and most of their other tools for that matter. However I am always looking for better tools no matter what type.

  5. #5
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Great post, very informative! I still would never put dye in a system,but that's just my opinion.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  6. #6
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    Spectroline is the only dye approved by Copeland.. If Copeland approved it, why not use it?

    I have one of their kits that I've only used once or twice.

    http://www.racplus.com/news/emerson-...614383.article

    http://www.spectroline.com/hvacr/hvac_kits.html

  7. #7
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    615
    Post Likes

    Hmm

    Quote Originally Posted by jimj View Post
    Great post, very informative! I still would never put dye in a system,but that's just my opinion.
    Even if you couldn't find the leak by any other means?
    I am not saying they are the best option, just that they are an option. When a customer is losing money from lost refrigerant and downtime, I will try anything that is reasonable to make him happy.
    Have you had bad experiences with dye?

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by koolkahuna

    Even if you couldn't find the leak by any other means?
    I am not saying they are the best option, just that they are an option. When a customer is losing money from lost refrigerant and downtime, I will try anything that is reasonable to make him happy.
    Have you had bad experiences with dye?
    Point is, unless there is no access to the piping, the leak can be found by other means.

    Dye is a lazy way out.



  9. #9
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    I used dyetell in the early seventies ( don't tell anyone) and hated the red crap on everything. Today many manufactures recommend against it and as you say in your post there are a lots of other ways to find leaks, so far they have worked for me!
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  10. #10
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    615
    Post Likes
    Quote Originally Posted by jimj View Post
    I used dyetell in the early seventies ( don't tell anyone) and hated the red crap on everything. Today many manufactures recommend against it and as you say in your post there are a lots of other ways to find leaks, so far they have worked for me!
    I have run across a few of those red messes, your secret is safe with me.
    Like I said before, a guy needs to perfect and exhaust all other leak detecting skills before going with dye. I haven't had to use it for over 2 years now and hope I don't have to again.

    jpsmith1cms - keep up the good work!

  11. #11
    Join Date
    Jul 2010
    Location
    Denver, CO
    Posts
    458
    Post Likes
    I am under the same opinion that I would never put this in any system that I work on, but thats just an opinion. To me, refrigerant systems have to be very clean, thats why we are so critical with evacuation, vaccums, and filter dryers. I once pumped a system up to 750psi to find a leak, that I was more willing to do than to use a dye.

  12. #12
    Join Date
    Jan 2006
    Location
    McQueeney, Texas
    Posts
    5,088
    Post Likes
    In all my almost 40 years of doing this, I have never used dye (Or maybe I don't remember ).
    But I wish I did a few times.

    The thing is- I could have found the most problematic leaks by spending a little more time and effort the first time around.
    Whipping through the system with the H10 but not using the "tiny" leak sensitivity is a no-no. Not letting bubbles sit long enough. Not going through the extra work of getting in the 150* attic and doing a thorough test is not savvy. Just looking for traces of oil to leak check because there are other calls waiting isn't the best way.
    It's the bad habit of it being the first time at this house and using the old thinking that it is probably a tiny leak and if it runs low again- we'll take a look.
    Being lazy, using shortcuts, excuses because there are too many calls to do is a bad habit.

    If I use the new attitude I have promised and adopted the last two years, I find all of the leaks now using the H10, bubbles and the extra effort and time. I even found a leak in an evaporator I couldn't find three years in a row- I used more time and persistence.

    Might be why I am so slow right now, because the darn units are all working instead of leaking.

  13. #13
    Join Date
    Jan 2011
    Location
    Boston, MA
    Posts
    462
    Post Likes
    Quote Originally Posted by walterc;12380371....I find all of the leaks now[/U
    using the H10, bubbles and the extra effort and time...
    Even R410a with the H10..

    I know...

  14. #14
    Join Date
    Nov 2010
    Location
    Missouri
    Posts
    401
    Post Likes
    http://www.spectroline.com/graphics_library_logos.html
    Some times The customer wants to see where leak is. I live in the show me state. found multiple leaks with bubbles and detek. when leak is in middle of coil
    with dye in system you will have a scenic view for customer to see. Boss bought these new kits and ultra violet light you carry around. It used to be a big light in box you had to retrieve it from shop to use. When you have windy conditions, it is ALMOST impossible to find leaks with sniffers, you need device to hear it or see it

  15. #15
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    30,770
    Post Likes
    got a problem R-22 unit that I'm having problems locating a leak. holds 200 psi nitrogen for hours. yet loses refrigerant after a few months.

    normally soapy bubbles finds em right away. also using two different refrigerant detectors with heated diode tips.

    have not tried ultra sonic leak finder yet.

    besides oily spots, what else should I be looking for?

  16. #16
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    615
    Post Likes
    Quote Originally Posted by cy View Post
    got a problem R-22 unit that I'm having problems locating a leak. holds 200 psi nitrogen for hours. yet loses refrigerant after a few months.

    normally soapy bubbles finds em right away. also using two different refrigerant detectors with heated diode tips.

    have not tried ultra sonic leak finder yet.

    besides oily spots, what else should I be looking for?
    Aircooled condenser or watercooled?

  17. #17
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    30,770
    Post Likes
    Quote Originally Posted by koolkahuna View Post
    Aircooled condenser or watercooled?
    aircooled condenser ... trace R-22 installed before pressuring up. slowly moved tip set on high Tek Mate, top to bottom. copper lines run under crawspace. that's next ..

    ran out of time ... left 150 psi overnight .. really want to find this leak.

  18. #18
    Join Date
    May 2007
    Location
    Central NJ Area
    Posts
    1,248
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Point is, unless there is no access to the piping, the leak can be found by other means.


    Dye is a lazy way out.
    It may be the lazy way out but i can be more cost effective because less labor is needed which is what is the major cost in leak location is.

    Now if the system is a R22, is 10 years or greater in age, the cost of location, repair, or replacement of a part, may not even be worth the time or effort. This is another story though

  19. #19
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by jimj View Post
    Great post, very informative! I still would never put dye in a system,but that's just my opinion.
    So if presented with the challenge of leak searching a refrigeration system for an explosion proof HAZMAT vault where unstable VOC's are stored, how would you proceed?

    In this particular situation, attempting to walk into the vault with a heated diode type leak detector would likely get you tackled by a rather large man before you even got to the door, if it didn't get confiscated at the security checkpoint, and infrared sensor type detectors are set off by stuff stored in the vault.

  20. #20
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    30,770
    Post Likes
    not a dye but a self sealer ... A/C Leak Freeze

    they claim not to hurt the system and that it stays totally inert until it gets activated by a leak. has anyone used A/C Leak Freeze?

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •