  1. #14
    Join Date
    Nov 2010
    Location
    Missouri
    Posts
    371
    http://www.spectroline.com/graphics_library_logos.html
    Some times The customer wants to see where leak is. I live in the show me state. found multiple leaks with bubbles and detek. when leak is in middle of coil
    with dye in system you will have a scenic view for customer to see. Boss bought these new kits and ultra violet light you carry around. It used to be a big light in box you had to retrieve it from shop to use. When you have windy conditions, it is ALMOST impossible to find leaks with sniffers, you need device to hear it or see it

  2. #15
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    290
    got a problem R-22 unit that I'm having problems locating a leak. holds 200 psi nitrogen for hours. yet loses refrigerant after a few months.

    normally soapy bubbles finds em right away. also using two different refrigerant detectors with heated diode tips.

    have not tried ultra sonic leak finder yet.

    besides oily spots, what else should I be looking for?

  3. #16
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    529
    Quote Originally Posted by cy View Post
    got a problem R-22 unit that I'm having problems locating a leak. holds 200 psi nitrogen for hours. yet loses refrigerant after a few months.

    normally soapy bubbles finds em right away. also using two different refrigerant detectors with heated diode tips.

    have not tried ultra sonic leak finder yet.

    besides oily spots, what else should I be looking for?
    Aircooled condenser or watercooled?

  4. #17
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    290
    Quote Originally Posted by koolkahuna View Post
    Aircooled condenser or watercooled?
    aircooled condenser ... trace R-22 installed before pressuring up. slowly moved tip set on high Tek Mate, top to bottom. copper lines run under crawspace. that's next ..

    ran out of time ... left 150 psi overnight .. really want to find this leak.

  5. #18
    Join Date
    May 2007
    Location
    Central NJ Area
    Posts
    870
    Quote Originally Posted by jpsmith1cm View Post
    Point is, unless there is no access to the piping, the leak can be found by other means.


    Dye is a lazy way out.
    It may be the lazy way out but i can be more cost effective because less labor is needed which is what is the major cost in leak location is.

    Now if the system is a R22, is 10 years or greater in age, the cost of location, repair, or replacement of a part, may not even be worth the time or effort. This is another story though

  6. #19
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Quote Originally Posted by jimj View Post
    Great post, very informative! I still would never put dye in a system,but that's just my opinion.
    So if presented with the challenge of leak searching a refrigeration system for an explosion proof HAZMAT vault where unstable VOC's are stored, how would you proceed?

    In this particular situation, attempting to walk into the vault with a heated diode type leak detector would likely get you tackled by a rather large man before you even got to the door, if it didn't get confiscated at the security checkpoint, and infrared sensor type detectors are set off by stuff stored in the vault.
    If more government is the answer, then it's a really stupid question.

  7. #20
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    290
    not a dye but a self sealer ... A/C Leak Freeze

    they claim not to hurt the system and that it stays totally inert until it gets activated by a leak. has anyone used A/C Leak Freeze?

  8. #21
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    290
    so is spectroline dye safe to use in an R-22 system? they claim it's compatible and has blessing of compressor mfg.

    normally would not put anything but refrigerant and oil into any system. have spent too much time already looking for this leak. dye will find it, but will it also destroy the system?

  9. #22
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    290
    dup....

  10. #23
    Join Date
    Jun 2003
    Location
    Virginia
    Posts
    376
    I haven't had much luck with refrigerant dyes. Of course I only used dye a few times 20 years ago. Maybe they're better now, but I have the best luck with an H-10 and soap bubbles...

  11. #24
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    290
    Quote Originally Posted by prorefco View Post
    I haven't had much luck with refrigerant dyes. Of course I only used dye a few times 20 years ago. Maybe they're better now, but I have the best luck with an H-10 and soap bubbles...
    got an old H-10 that has not been used in years....
    are you saying H-10 works better than newest heated diode detectors?

    are you using Dawn soap for bubbles?

    normally can find leaks with no problems... but got an old R-22 system with a leak that's eating my lunch. normally would not use dyes. but just about ready to for this one. purchased some Cal-Blue LT leak detector. willing to try out just about anything to keep from using dye.


  12. #25
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,916
    Quote Originally Posted by cy View Post
    got an old H-10 that has not been used in years....
    are you saying H-10 works better than newest heated diode detectors?

    are you using Dawn soap for bubbles?

    normally can find leaks with no problems... but got an old R-22 system with a leak that's eating my lunch. normally would not use dyes. but just about ready to for this one. purchased some Cal-Blue LT leak detector. willing to try out just about anything to keep from using dye.

    H-10 and Big Blue.

    Dtek and a lot of the others aren't up to the Gold Standard that the H-10 set a long time ago.

  13. #26
    Join Date
    Jun 2003
    Location
    Virginia
    Posts
    376
    The H-10 works very for me. I have three other types, the newest is a yellow jacket but the H-10 works better than the others...

    I only use calgon leak detector soap bubbles... They work best for me...

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event