Thread: GROUNDED B PHASE
-
03-24-2012, 02:18 PM #40
Professional Member*
- Join Date
- Oct 2009
- Location
- God's country - Shenandoah Valley, VA
- Posts
- 195
Interesting. I don't think I've ever seen a corner grounded secondary Delta used at a shopping center. The obvious reason being that a grounded neutral would be necessary for 120v loads and it would not seem make sense to have a separate corner grounded system to supply relatively small to medium hvac loads. But, I haven't seen everything either.
Are you certain it was corner grounded or could there have been a fault in a phase? Could someone have changed something not realizing the type of system it was?
I doubt if the poco would have changed phasing. They are very careful about that and one of their standard tools is a phase rotation meter.
-
03-24-2012, 02:21 PM #41
Professional Member*
- Join Date
- Oct 2009
- Location
- God's country - Shenandoah Valley, VA
- Posts
- 195
Corner grounded Delta Service
Are the transformers pole mounted? If so, can you post some pics of them clearly showing their wiring?
-
03-24-2012, 02:25 PM #42
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,434
-
03-24-2012, 02:28 PM #43
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,434
-
03-24-2012, 03:43 PM #44
How many transformers in the group?
To post a pic:
Store the pic on your computer.
Open the "post reply" box
Click on the "Manage Attachments" button below the reply box.
Click "browse" and find the file name on your computer.
Click "upload"
When the file is uploaded, the file name will appear below the second white box.
To post a large version of the pic, click on that file name, and a new browser window will open showing your picture. Right click on that picture, and click "copy."
Now, click in your already opened reply box and click "paste."
Now you will have a large picture and a thumbnail version when you finish your post.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
03-24-2012, 03:48 PM #45
.
Keep it simple to keep it cool!
-
03-24-2012, 08:52 PM #46
Professional Member
- Join Date
- Jul 2000
- Location
- Dallas,Texas
- Posts
- 4,819
Don't make anything out of my statement beyond what I said.
The transformer is grounded at "B" phase and IF "standards are maintained", every "B" phase throughout the system will have ZERO potential to ground. If you change the load wires at the motor contactor\ starter to change rotation - no harm, no foul. If you swap the grounded "B" phase somewhere else in the system, you have created a hazard for the next poor shmuck that has to work on this thing, because ZERO potential to ground on a live phase is now where it is not supposed to be. (assuming the poor shmuck understands what he is dealing with to start with)
-
03-25-2012, 07:28 AM #47
So, you were saying that A B and C should be kept in their expected positions? I agree with that.