What Am I Missing?
Two Luxaire Furnaces- Model #PBFMD12F08501A and Model#PBFMD12F05501A.Both Furnaces Use The Same Blower Motor And Wheel With Different Airflow Ratings.Something Has To Regulating Flow On The Smaller Output Furnace.
-
01-28-2012, 07:34 PM #2
Regular Guest
- Join Date
- Jan 2012
- Location
- York,PA.
- Posts
- 34
No,All unit dimensions,filter & duct openings are identical.It almost has to be electrical.
-
01-28-2012, 08:21 PM #3
Regular Guest
- Join Date
- Jan 2012
- Location
- York,PA.
- Posts
- 34
-
01-29-2012, 08:49 AM #4
Smaller furnace has higher pressure drop across furnace section?
"Customer Service" is not a department, it's an attitude!
???
-
01-29-2012, 08:52 AM #5
Bigwave, This is the Ask Our Pro's or AOP forum. In order to post responses here, you must have verified qualifications and have been approved by the AOP Committee. Please see my signature line for links to register and review the AOP Forum Rules. Thank you. Your post will now be deleted. Further infractions may result in loss of posting privileges.
Keep the fire inside the fireplace.
-
01-29-2012, 11:01 AM #6
Probably has baffles in the smaller one to make sure air flow goes over the heat exchanger. And not bypass it.
-
01-29-2012, 01:11 PM #7
Regular Guest
- Join Date
- Jan 2012
- Location
- York,PA.
- Posts
- 34
Thanks beenthere.I have seen low firing rate baffles mentioned after searching it.This is the only PDF I have found:http://www.hamiltonhomeproducts.com/...s/Pfm-tech.pdf
-
01-29-2012, 02:12 PM #8
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
2 different airflows
means 2 different pressures with this twinned unit SO the unit with the higher pressure is stopping the air delivery from the smaller unit. Not good since winter operations could see high limit trips and cooling will have frozen coils.
The units need to be balanced airflow regardless of dischagre temp. The air will mix so no need to worry.You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!
-
01-29-2012, 02:56 PM #9
Regular Guest
- Join Date
- Jan 2012
- Location
- York,PA.
- Posts
- 34
I take it this is a bad design.Adding baffles to reduce airflow to save manufacturing costs.I am looking into natural gas.(line is appx.350' away) and hopefully get rid this fuel hog furnace.
-