Thread: Chiller/EEV

  1. #1
    Join Date
    Nov 2003
    Posts
    23
    Post Likes

    Chiller/EEV

    Whats a good way to test a exv to see if is working ok.
    thanks Herman

  2. #2
    Join Date
    Dec 2009
    Location
    Fort Worth, Texas
    Posts
    154
    Post Likes
    check discharge superheat or suction superheat depending on chiller. then load up chiller, and watch and see if exv maintains proper superheat.
    just say your discharge superheat is low like 15 degrees and you exv position is at the bottom range. This would be a good sign that the exv is probably sticking. Keep it simple the exv should maintain proper superheat. If in doubt pull it apart and in service mode run it from 0-100 steps. You can also ohm the windings, feel the pulsation as it drives up and down.

    Better yet get the service manual for the machine your working on and use the guide lines.

    Hope this helps

  3. #3
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by HJ Controls View Post
    check discharge superheat or suction superheat depending on chiller. then load up chiller, and watch and see if exv maintains proper superheat.
    just say your discharge superheat is low like 15 degrees and you exv position is at the bottom range. This would be a good sign that the exv is probably sticking. Keep it simple the exv should maintain proper superheat. If in doubt pull it apart and in service mode run it from 0-100 steps. You can also ohm the windings, feel the pulsation as it drives up and down.

    Better yet get the service manual for the machine your working on and use the guide lines.
    Hope this helps
    The highlighted portion of this quote and personal experience are the only sure things you have. Some run at 4 degrees, some at 15 degrees (superheat), some in between, depends on machine and application. Some don't do steps or have windings, others do, some you can pull apart, others you can't, some have service mode and some don't, all depends on manufacturer. Get the service info on what you have and use that as your guide.

  4. #4
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Agreed with everything so far....might be helpful for you to tell us what you are working on and why you are wanting to test the valve?

  5. #5
    Join Date
    Dec 2009
    Location
    Fort Worth, Texas
    Posts
    154
    Post Likes
    read the last part, get service manual. trying to give helpful hints and some ideas.

  6. #6
    Join Date
    Sep 2011
    Location
    BAJA AND CALIFORNIA
    Posts
    101
    Post Likes
    definitively you need the IOM manual of the unit , is different with every brand
    different method of test
    with model and serial of the unit may be we can share the manual

  7. #7
    Join Date
    Feb 2012
    Posts
    14
    Post Likes
    Check the actuator. Sometimes the inputs are fine but the actuator is not. Consider it like a jammed actuator. Actuator is the thing that moves the orifice plate according to superheat conditions.



  8. #8
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by jcistc View Post
    Check the actuator. Sometimes the inputs are fine but the actuator is not. Consider it like a jammed actuator. Actuator is the thing that moves the orifice plate according to superheat conditions.


    It's wise to refrain from giving advice if you don't know what you're giving advice about.......

  9. #9
    Join Date
    Feb 2012
    Posts
    14
    Post Likes
    Quote Originally Posted by klove View Post
    It's wise to refrain from giving advice if you don't know what you're giving advice about.......


    i have seen this problem . the chiller would just not reach rated capacity. every thing was fine .. we even checked for leakages , but there were none. then it was found that the orifice plate actuator travel was faulty. It was getting jammed .


    maybe what i am speaking about - the thing that connects the stepper motor and the orifice plate - is not an "actuator" .

  10. #10
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by jcistc View Post
    i have seen this problem . the chiller would just not reach rated capacity. every thing was fine .. we even checked for leakages , but there were none. then it was found that the orifice plate actuator travel was faulty. It was getting jammed .


    maybe what i am speaking about - the thing that connects the stepper motor and the orifice plate - is not an "actuator" .
    How do you know you've seen the problem the OP's having? He didn't give the least bit of info about what type or make chiller it is, or the manufacturer of the valve. It's impossible that you can give specific advice of any kind on this matter.

  11. #11
    Join Date
    Dec 2009
    Location
    Fort Worth, Texas
    Posts
    154
    Post Likes
    an exv is an exv. It has a motor, windings, some type of guide a orfice of some type and it recieves a signal or voltage to operate from a controller or source. And we are trying to help him with the info he gave us.
    It is a given that he reads the iom for a perticular unit or he is just asking a general question.

  12. #12
    Join Date
    Feb 2012
    Posts
    14
    Post Likes
    OK i'll have to admit that my reply was very very specific.

  13. #13
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by HJ Controls View Post
    an exv is an exv. It has a motor, windings, some type of guide a orfice of some type and it recieves a signal or voltage to operate from a controller or source. And we are trying to help him with the info he gave us. It is a given that he reads the iom for a perticular unit or he is just asking a general question.
    Then the first thing that should have been stated is that there wasn't enough info given to be able to give any real direction. Otherwise, I think you should explain the operation of every EXV by every different manufacturer that's on the market today 'cause I've got news for you - an EXV ain't an EXV except in very general terms. Some are close to others, but that's about as far as it goes. Service procedures can be totally different from one brand to the next. The only advice given that was credible (based on the question as asked) was to run the chiller and see if it holds it's superheat setpoint, and to get the literature on the valve/chiller and see how it's supposed to work. Past that was nothing more than shootin' in the dark. Ryan actually stated the obvious about what's needed.

    I didn't realize that it's a given that he's reading the IOM. Per your first post, neither did you.

    Now to the crux of the issue: HERMAN - if you'll tell us what you're trying to accomplish and give some specifics as to what you're working with, maybe someone can help get you going in the right direction. If you're just asking in general out of curiosity, then you can take all of the advice that's been given so far as different things that can happen depending on whose valve you're dealing with (but let us know that this is what you were asking for so we can quit wondering).

  14. #14
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by jcistc View Post
    OK i'll have to admit that my reply was very very specific.
    Hindsight's 20/20, and I've had to check mine far too often!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •