    Can someone tell me a formula for finding actual tonnage output on a chiller.
    in a tree looking in your window
    This is is what I use, screwed it up the first time.
    Delta T x gpm divided by 24 = tons
    Tons x 24 divided by delta t = gpm
    [Edited by chillrdude on 04-05-2006 at 12:16 AM]
    If you dont stand behind our troops, please feel free...........to stand in front of them.
    500 x gpm x delta T
    refrigeration workers of Ontario
    Oregon
    close but it is GPM x 500 x deltatemp divided by 12000BTU's
    thanks journey man. My head was starting to hurt.Duhhh!!!!
    Jan 2005
    SE Florida
    how do you solve for gpm
    Manufacturer should have curve chart for delta P that shows GPM.
    South Dakota
    You can't solve for gpm unless you know the BTUH and you can't solve for BTUH without an accurate gpm. The most accurate way of getting gpm is using a flow meter which involves cutting pipe and installing the meter.
    Apr 2002
    should be in ball park using pressure drop across barrel
    Apr 2002
    Dallas, TX
    Specific heat of water is essentially 1 Btu/lb-F
    There are about 8.337 lb water (60F)/gal
    8.337 * 1 = 8.337 Btu/gal-F
    There are 12,000 Btu/h or 200 Btu/min in a ton
    200 Btu/min-ton / 8.337 Btu/gal-F = 23.99 gpm-F / ton
    So multiply gpm by delta T and divide by 23.99 and you will get tons!
    [Edited by Andy Schoen on 04-05-2006 at 12:04 AM]
    what if you have Glycol in system? will your formula change by adding glycol?
    Jan 2005
    Yep, it'll change.
    Apr 2002
    Dallas, TX
    I see one source http://www.engineeringtoolbox.com/et...col-d_146.html which states specific heat of a 50/50 water ethylene glycol mix reduces specific heat to about 0.78 Btu/lb-F (below 32F) and has a specific gravity of 1.1. So we can figure:
    8.337 * 1.1 * 0.78 = 7.153 Btu/gal-F
    200 Btu/min-ton / 7.153 Btu/gal-F = 27.96 gpm-F / ton
    So in this case, multiply gpm by delta T and divide by 28 to get tons.