Results 1 to 3 of 3
-
01-23-2012, 08:21 AM #1
Regular Guest
- Join Date
- Apr 2005
- Location
- somewhere out there
- Posts
- 63
Mod Con boiler catergory 4 venting though roof
I have a customer who would like there Lochnivar Knight boiler cvpc vent pipe changed from a side sill plate vent to a up though the roof vertical vent.
The snow line is a problem even though the vent and intake go up 2 feet from the sillplate. There is a bedroom closet 10 feet to the left of the boiler.
I was thinking of framining in a chase in the corner of the closet and going up though it and out the side at around 8 feet or up though the attic to roof. Lochnivar wants cpvc used for any closet or alcove install. cpvc is rated at a higher temp then pvc but i cant find a section in the fuel gas codebook on plastic venting up though the house. What does everyone think .
-
01-23-2012, 06:02 PM #2
Professional Member*
- Join Date
- Sep 2004
- Posts
- 113
We go by manufactures specs. Always. Even though I don't agree with all of it.
CYA!
-
01-23-2012, 06:30 PM #3
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251


Reply With Quote
