Thread: Furnance kicked my rookie butt today

  1. #1
    Join Date
    Jan 2012
    Posts
    2
    Post Likes

    Furnance kicked my rookie butt today

    Guys I need some opinions this am. Working on a Tempstar NUG5075BFA2. It has a VR8204M1075 gas valve. The t-stat calls for heat, inducer goes and closes the pressure switch. They the direct spark ignightor starts sparking and there is a poof of gas that comes from the piliot tube that imd goes out. The gas valve is getting 24v on the red wire and 12v on the black. Do you guys think the valv is bad? This is the first one wire spark ignition system I have seen.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Dwarren2012 View Post
    Guys I need some opinions this am. Working on a Tempstar NUG5075BFA2. It has a VR8204M1075 gas valve. The t-stat calls for heat, inducer goes and closes the pressure switch. They the direct spark ignightor starts sparking and there is a poof of gas that comes from the piliot tube that imd goes out. The gas valve is getting 24v on the red wire and 12v on the black. Do you guys think the valv is bad? This is the first one wire spark ignition system I have seen.
    My first suggestion.

    Stop reading voltages to ground when you really want to read across the coil.

    What was the voltage from red to black on the gas valve?



  3. #3
    Join Date
    Jul 2009
    Location
    st louis mo
    Posts
    337
    Post Likes
    you need a new furnace, hive me a call, hurry, hurry, theres only a few thousand left

  4. #4
    Join Date
    Mar 2001
    Location
    Seattle
    Posts
    384
    Post Likes
    Does anything prove that there is a pilot flame? Thermocouple?

  5. #5
    Join Date
    Dec 2011
    Location
    Southern Oklahoma
    Posts
    55
    Post Likes
    Sometimes a puff of pressure then nothing, will happen when the gas is turned off{residual pressure buildup through an almost closed valve or plug left in by gas company}. When something is kicking your butt it's a good idea to start over and never assume even the simple things. You will be surprised how often it's something really simple...good luck

  6. #6
    Join Date
    Jan 2012
    Location
    St. Louis Missouri
    Posts
    60
    Post Likes
    Did you clean the pilot tube and pilot?

  7. #7
    Join Date
    Sep 2004
    Location
    Jersey
    Posts
    390
    Post Likes
    Quote Originally Posted by SuperDave89 View Post
    Did you clean the pilot tube and pilot?
    +1 and clean the orfice.
    Ride hard on a Harley!!

  8. #8
    Join Date
    Jan 2012
    Location
    St. Louis Missouri
    Posts
    60
    Post Likes
    Right some times its the simplest things!

  9. #9
    Join Date
    Jan 2009
    Location
    Fairfield county Connecticuit
    Posts
    803
    Post Likes
    LP gas or natural what was your gas pressure in out?

  10. #10
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,103
    Post Likes
    are you using a manometer?

  11. #11
    Join Date
    Jan 2009
    Location
    Fairfield county Connecticuit
    Posts
    803
    Post Likes
    I dont think he checked the gas pressure prob lp with no gas in the tank LOL

  12. #12
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,103
    Post Likes
    I've done the same!

  13. #13
    Join Date
    Jul 2009
    Location
    Northern area between Alantic and Pacific
    Posts
    112
    Post Likes
    What kind of control board u have? Is it a black box build of Honeywell smart valve? If positive,then check the board first before u condemn the valve. Good luck.

  14. #14
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Post Likes
    If I read your valve model correctly, it's an intermittent spark valve that can also be used as a universal valve.

    In your application, after the inducer closes the pressure switch, a Honeywell S8610 (or similar) module should open the pilot valve and initiate spark to light the pilot.

    It probably has a Honeywell ST9120 control board as well, to control the inducer and the blower.

    After the pilot proves, the module will open the main valve. The valve should have three terminals..."PV" (pilot valve), "PV/MV" (common), and "MV" (main valve).

    Selling them a new furnace won't teach you a thing. Figure it out and learn from it.

    Come back here for more help if need be.....we're here for you.
    Technical incompetence is NOT a sales tool....

  15. #15
    Join Date
    Sep 2002
    Posts
    4,979
    Post Likes
    1 post and you guys are giving advice ????????? I think this homeowner should call a reputable heating company and Quit playing like he is a tech

  16. #16
    Join Date
    Jan 2009
    Location
    Fairfield county Connecticuit
    Posts
    803
    Post Likes
    no advice given here he would need to be a tech to do or even know what I said besides checking if he has fuel in the tank if its lp we never received that answer.

  17. #17
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,103
    Post Likes
    we can't help giving advice. W are very sympathetic.

  18. #18
    Join Date
    Feb 2010
    Location
    Ohio
    Posts
    573
    Post Likes
    He's in a tech-to-tech forum.

  19. #19
    Join Date
    Oct 2005
    Posts
    12
    Post Likes
    had a keeprite gas unit that would get to the point of lighting the pilot then main valve opened and a good flame would be there then die back. Sometimes it would burn for a few seconds or few minutes... found out the gas company had a bad meter/reg and it was choking off the supply. The guy was way out in the country.

  20. #20
    Join Date
    Jan 2012
    Posts
    2
    Post Likes
    Thread Starter
    Thanks guys! I am sorry for not updating sooner! I am not just a home owner trying to do it myself. Markvilleman put me on the right track. I went back and checked the honywell board and it was bad. Changed board heat fired and everyon was happy! Now A/C season has started early down here in Memphis TN and I am loving it! Not much of a winter here so I am well rested. Thanks for the advice guys and Ill check back in sooner so I am not labeled a diy.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •