    Is there a set amount of KW back up electric strip heat per ton of Heat Pump? Is 15 KW strip heat enough for a 3 ton heat pump? (5 KW per ton)

  2. #2

  3. #3
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,385
    There's a possibilty that's right.... could be way off too.

    Go with the above answer.
    "If you call that hard work, a koala’s life would look heroic."

    VETO PRO PAC, The Official Tool Bag of HVAC-Talk.com

    Testo... you guys rule!

  4. #4
    Join Date
    Apr 2006
    Posts
    143
    plenty...be sure and check available power at panel... 15k is a lot of amp draw w/heatpump

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,184
    Do a load cal, and find out if thats enough to heat your house without the heat pump.

    You might need 17 kw without the HP running.
    Contractor locator map

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,255

    General Explantion of Electric Heat Strip Sizing

    Originally posted by jrcase
    Is there a set amount of KW back up electric strip heat per ton of Heat Pump? Is 15 KW strip heat enough for a 3 ton heat pump? (5 KW per ton)
    Generally,
    kW needed =
    Total Heat Load - the reduced Heat Pump capacity at dsign temp ( 0'F to 35'F) depending on North or South U.S.

    3 Ton ... ~36,000 BTUh Total
    _______.. ~36,000 BTUh at 47'F
    _______.. ~20,000 BTUh at 17'F
    _______.. ~14,000 BTUh at 10'F ( ??)

    For example, IF heating load for 2,000 S.F. residence is 50,000 BTUh at 10'F design temperature, a heat strip would need to provide 36,000 BTUh (50K -14K)
    or 10kW ( 1 kw = 3,412 BTUh)

    If your winter design temperature is 30'F (several Southern U.S. states), the heat pump would provide
    ~28,000 BTUh and residence may only need 37,000 BTUh
    total heating capacity. Therefore, a 5 kW ( 17,000 BTU) heat strip would be MORE THAN sufficient to meet the 9,000 BTUh demand.

    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,184
    Size the strip to carry the full load, incase the OD unit goes out when its near design, if your design is below 30.

    Contractor locator map

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Apr 2003
    Posts
    43
    Thanks a million for all the replies. One more question. Do the heat strips only come in 5K increments? (5KW, 10KW, 15KW, ect.)Say I only need 7.5 KW, do I have to step up to 10KW or can I get 7.5KW?

  9. #9
    Originally posted by jrcase
    Say I only need 7.5 KW, do I have to step up to 10KW or can I get 7.5KW?
    Check with your distributor for each manufactures available options:

    5, 7.5 and 10 nominal KW models available with lug terminals

    5, 7.5, 10, 15, 20, 25 and 30 nominal KW models available
    with Circuit Breakers