Results 1 to 9 of 9
03-31-2006, 09:31 PM #1
- Apr 2003
- 43
Is there a set amount of KW back up electric strip heat per ton of Heat Pump? Is 15 KW strip heat enough for a 3 ton heat pump? (5 KW per ton)
03-31-2006, 09:33 PM #2
Grumpy Old Man
- Apr 2003
- 6,383
03-31-2006, 11:40 PM #3
There's a possibilty that's right.... could be way off too.
Go with the above answer."If you call that hard work, a koalas life would look heroic."
VETO PRO PAC, The Official Tool Bag of HVAC-Talk.com
Testo... you guys rule!
04-01-2006, 05:59 AM #4
- Apr 2006
- 143
plenty...be sure and check available power at panel... 15k is a lot of amp draw w/heatpump
04-01-2006, 08:04 AM #5
Do a load cal, and find out if thats enough to heat your house without the heat pump.
You might need 17 kw without the HP running.
04-01-2006, 08:32 AM #6
Professional Member*
- Nov 2004
- SW FL
- 5,249
General Explantion of Electric Heat Strip Sizing
Generally,Originally posted by jrcase
kW needed =
Total Heat Load - the reduced Heat Pump capacity at dsign temp ( 0'F to 35'F) depending on North or South U.S.
3 Ton ... ~36,000 BTUh Total
_______.. ~36,000 BTUh at 47'F
_______.. ~20,000 BTUh at 17'F
_______.. ~14,000 BTUh at 10'F ( ??)
For example, IF heating load for 2,000 S.F. residence is 50,000 BTUh at 10'F design temperature, a heat strip would need to provide 36,000 BTUh (50K -14K)
or 10kW ( 1 kw = 3,412 BTUh)
If your winter design temperature is 30'F (several Southern U.S. states), the heat pump would provide
~28,000 BTUh and residence may only need 37,000 BTUh
total heating capacity. Therefore, a 5 kW ( 17,000 BTU) heat strip would be MORE THAN sufficient to meet the 9,000 BTUh demand.
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".
04-01-2006, 08:41 AM #7
Size the strip to carry the full load, incase the OD unit goes out when its near design, if your design is below 30.
04-01-2006, 04:03 PM #8
- Apr 2003
- 43
Thanks a million for all the replies. One more question. Do the heat strips only come in 5K increments? (5KW, 10KW, 15KW, ect.)Say I only need 7.5 KW, do I have to step up to 10KW or can I get 7.5KW?
04-01-2006, 04:09 PM #9
Grumpy Old Man
- Apr 2003
- 6,383
Check with your distributor for each manufactures available options:Originally posted by jrcase
5, 7.5 and 10 nominal KW models available with lug terminals
5, 7.5, 10, 15, 20, 25 and 30 nominal KW models available
with Circuit Breakers