    motor condition in centrifugal chiller

    Hello guys new question related to a motor on centrifugal chillers
    YORK is open drive motor so no question about MEGG the motor
    TRANE low pressure R-123 is a semi-hermetic motor whats the best condition to perform motor MEGGER ??? according to your experience
    CARRIER & MC Quays 134a is semi-hermetic motor whats the best condition to perform motor MEGGER???? according to your experience.
    if you guys have any chart or manual that explain how is the best method to MEGG the motor and under what condition ,i will appreciate your Help.

    Regards

  2. #2
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Why wouldn't you test an open drive Y motor with a megger? It has windings with insulation that can deteriorate the same as any other motor.

    As far as T, C, and M chillers... I don't know of any special procedures for any of them, other than checking from phase to phase in addition to phase to ground. Don't meg any of them in a deep vacuum. Don't use a megger with a solid state starter or vfd connected. Megger readings don't do a whole lot of good without a history. I think T has a chart in the blue service guide?

    As far as a go/no-go rule of thumb for standard motors, I've always used 1 megohm per 1kv + 1 megohm.
    Don't pick the fly crap out of the pepper.

  3. #3
    Join Date
    Sep 2011
    Location
    BAJA AND CALIFORNIA
    Posts
    101
    Post Likes
    Thread Starter
    Rob you right that we need to check all the motors of the chillers , my question is around to the fact of york is open chiller compresor and motor are separate so the motors are under ambient condition , now trane R-123 OR 11 are low pressure and normally with refrigerant the units stoped are in vaccum my question is according to your experience we have to increase the pressure to 0 or 1 psi and then apply the megger or is no problem to megg the motor if the units are in vaccum but with the load of refrigerant???
    Now on the R-134a C,M, or any other centrifugal with positive pressure you can megg the motor of the unit under pressure condition??
    Do you have the blue service book for share??

    regards

    oscar

  4. #4
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    The reason they say not to meg a motor in a vacuum is because in a deep vacuum, there is no atmospheric insulation between the phases and from phase to ground. Arcing can occur inside the motor. Even in a low pressure machine that's in a vacuum when it's sitting idle, the refrigerant is the atmosphere that helps to insulate the phases from one another and ground.

    The chart is in CTV-SG-1 and CTV-SB-61. My copy of it is not much good and is mostly illegible.
    Don't pick the fly crap out of the pepper.

  5. #5
    Join Date
    Sep 2011
    Location
    BAJA AND CALIFORNIA
    Posts
    101
    Post Likes
    Thread Starter
    K ROB i will be on tampa next february , if you have time we can meet and buy you lunch do you work for a company or you do yourself??? may be you can give me some advices and recommendations in a chiller side , we have tranes ,mcquay,yorks and carrier under our responsability most of all are screw or centrifugals

    thanks again for your support

  6. #6
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Going to a class or something around here? Tampa's pretty cool, you'll enjoy it. I am always for doing lunch and talking shop with other folks in the business. Glad I could be of assistance, Oscar.
    Don't pick the fly crap out of the pepper.

  7. #7
    Join Date
    Sep 2011
    Location
    BAJA AND CALIFORNIA
    Posts
    101
    Post Likes
    Thread Starter
    yes i will teach some succes cases whit new water treatment technology that we apply on chillers and boilers for eliminate in certain porcentage the usage of chemicals we install the technology on chill water plants with centrifugal chillers,boilers and heat exchangers, now we make an aplication in a petrochemical plant under extreme conditions and power plants. please see below
    www.scaleblaster.com
    also i got home in tampa bay , i travel to florida every 30 to 60 days my partner on energy bussines live there i live near to san diego on border city we got office usa side and mexico side www.esschillwater.com

  8. #8
    Join Date
    Mar 2007
    Posts
    96
    Post Likes
    Quote Originally Posted by Tech Rob View Post
    The reason they say not to meg a motor in a vacuum is because in a deep vacuum, there is no atmospheric insulation between the phases and from phase to ground. Arcing can occur inside the motor. Even in a low pressure machine that's in a vacuum when it's sitting idle, the refrigerant is the atmosphere that helps to insulate the phases from one another and ground.

    The chart is in CTV-SG-1 and CTV-SB-61. My copy of it is not much good and is mostly illegible.

    Motor is to be megged with the stator at ambient temperature after 24 hours of idle standby.

    Meg Phase to Phase with remaining Phase connected to Ground.

    Meg Phase to Ground with remaining Phases connected to Ground.

  9. #9
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by w~p View Post
    ...Meg Phase to Phase with remaining Phase connected to Ground.

    Meg Phase to Ground with remaining Phases connected to Ground.
    nope.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  10. #10
    Join Date
    Oct 2011
    Location
    La.
    Posts
    323
    Post Likes
    In the IOM manuals the manufactures tell how to meg their motors and the limits that are allowed. Sometimes we need to read. See any York OM manual around page 58.

  11. #11
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    x2


    Quote Originally Posted by jayguy View Post
    nope.
    true knowledge exists in knowing that you know nothing.

  12. #12
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by w~p View Post
    Motor is to be megged with the stator at ambient temperature after 24 hours of idle standby.

    Meg Phase to Phase with remaining Phase connected to Ground.

    Meg Phase to Ground with remaining Phases connected to Ground.
    Where did this instruction come from?

  13. #13
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    Something of far greater importance than a simple "Megger" reading is called a "Polarization Index". What with the windings of most centrifigal motors being bathed in both refrigerant and oil mixture a "PI" test can and will give a far better deternination of good/bad than any simple "Meg" reading. The megger voltage is applied, the first reading is taken, then for 10 minutes with the megger still connected a second reading is taken.

    In summary, if the insulation system is clean and dry, the insulation resistance will increase with time( a smaller current). An insulation system that is contaminated with water, oil or is weak will show little if any increase with time.

    James G. Biddle (now AVO Corp. of Dallas, TX) publishes the following table for the Dielectric Absorption Ratio (Polarization Index)

    Condition 10:1 Min Ratio

    Dangerous < 1
    Poor <1.5
    Questionable 1.5-2.0
    Fair 2-3
    Good 3-4
    Excellent > 4

    I have given the ratios for the 10/1 min. test. A 60sec/30 sec. test is also made and the corresponding values arefrom top to bottom) <1.1, 1.1-1.25, 1.25-1.4, 1.4-1.6 and > 1.6. Many technicians prefer the shorter test times especially if they have a hand crank test set.

    Some References

    "A Stitch In Time..." by James G. Biddle pub. 21-P8
    Insulation Testing by D-C Methods by James G. Biddle pub. 22t1a-1975
    Principles of Dielectric Engineering, by Andrew Blanck, Rutherford Research Products Comapany
    The Characteristics of Insulation Resistance by Sydney Evershed, presented to Institute of Electrical Engineers, London, 27 Nov., 1913
    Ain't "None" of us as smart as "All" of us..

  14. #14
    Join Date
    Sep 2011
    Location
    BAJA AND CALIFORNIA
    Posts
    101
    Post Likes
    Thread Starter
    thanks Richard very good and understandable explanation also thanks for the literature reference
    regards
    oscar

  15. #15
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    451
    Post Likes
    some intersting reading.
    Attachment 238911

  16. #16
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    thanks for posting Richard...i was getting tired of having this same conversation...that and the myth of not megging a motor in a vacuum...there is a huge difference between megging a motor in a vacuum versus applying line voltage to a motor in a vacuum. i use the PI method (1 minute / 10 minute). a 6 lead compressor can take about an hour so i have to plan for it!
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  17. #17
    Join Date
    Jan 2008
    Location
    pritzberg
    Posts
    4,641
    Post Likes
    Quote Originally Posted by supertek65 View Post
    x2
    Quote Originally Posted by jayguy View Post
    nope.
    gotta love the open section
    \m/
    original member of the racoon brotherhood

  18. #18
    Join Date
    Mar 2007
    Posts
    96
    Post Likes
    Quote Originally Posted by klove View Post
    Where did this instruction come from?
    It is from Fluke.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •