Results 1 to 13 of 18
    Sep 2011
    BAJA AND CALIFORNIA
    motor condition in centrifugal chiller
    Hello guys new question related to a motor on centrifugal chillers
    YORK is open drive motor so no question about MEGG the motor
    TRANE low pressure R-123 is a semi-hermetic motor whats the best condition to perform motor MEGGER ??? according to your experience
    CARRIER & MC Quays 134a is semi-hermetic motor whats the best condition to perform motor MEGGER???? according to your experience.
    if you guys have any chart or manual that explain how is the best method to MEGG the motor and under what condition ,i will appreciate your Help.
    Regards
    Why wouldn't you test an open drive Y motor with a megger? It has windings with insulation that can deteriorate the same as any other motor.
    As far as T, C, and M chillers... I don't know of any special procedures for any of them, other than checking from phase to phase in addition to phase to ground. Don't meg any of them in a deep vacuum. Don't use a megger with a solid state starter or vfd connected. Megger readings don't do a whole lot of good without a history. I think T has a chart in the blue service guide?
    As far as a go/no-go rule of thumb for standard motors, I've always used 1 megohm per 1kv + 1 megohm.
    The key to happiness is lower expectations.
    Don't pick the fly crap out of the pepper.
    Sep 2011
    BAJA AND CALIFORNIA
    Rob you right that we need to check all the motors of the chillers , my question is around to the fact of york is open chiller compresor and motor are separate so the motors are under ambient condition , now trane R-123 OR 11 are low pressure and normally with refrigerant the units stoped are in vaccum my question is according to your experience we have to increase the pressure to 0 or 1 psi and then apply the megger or is no problem to megg the motor if the units are in vaccum but with the load of refrigerant???
    Now on the R-134a C,M, or any other centrifugal with positive pressure you can megg the motor of the unit under pressure condition??
    Do you have the blue service book for share??
    regards
    oscar
    The reason they say not to meg a motor in a vacuum is because in a deep vacuum, there is no atmospheric insulation between the phases and from phase to ground. Arcing can occur inside the motor. Even in a low pressure machine that's in a vacuum when it's sitting idle, the refrigerant is the atmosphere that helps to insulate the phases from one another and ground.
    The chart is in CTV-SG-1 and CTV-SB-61. My copy of it is not much good and is mostly illegible.
    Sep 2011
    BAJA AND CALIFORNIA
    K ROB i will be on tampa next february , if you have time we can meet and buy you lunch do you work for a company or you do yourself??? may be you can give me some advices and recommendations in a chiller side , we have tranes ,mcquay,yorks and carrier under our responsability most of all are screw or centrifugals
    thanks again for your support
    Going to a class or something around here? Tampa's pretty cool, you'll enjoy it. I am always for doing lunch and talking shop with other folks in the business. Glad I could be of assistance, Oscar.
    Sep 2011
    BAJA AND CALIFORNIA
    yes i will teach some succes cases whit new water treatment technology that we apply on chillers and boilers for eliminate in certain porcentage the usage of chemicals we install the technology on chill water plants with centrifugal chillers,boilers and heat exchangers, now we make an aplication in a petrochemical plant under extreme conditions and power plants. please see below
    www.scaleblaster.com
    also i got home in tampa bay , i travel to florida every 30 to 60 days my partner on energy bussines live there i live near to san diego on border city we got office usa side and mexico side www.esschillwater.com
    Quote Originally Posted by Tech Rob View Post
    Motor is to be megged with the stator at ambient temperature after 24 hours of idle standby.
    Meg Phase to Phase with remaining Phase connected to Ground.
    Meg Phase to Ground with remaining Phases connected to Ground.
    Quote Originally Posted by w~p View Post
    ...Meg Phase to Phase with remaining Phase connected to Ground.
    nope.
    Oct 2011
    La.
    In the IOM manuals the manufactures tell how to meg their motors and the limits that are allowed. Sometimes we need to read. See any York OM manual around page 58.
    x2
    Quote Originally Posted by jayguy View Post
    nope.
    true knowledge exists in knowing that you know nothing.
    Dec 2008
    Dixiana, AL
    Where did this instruction come from?
    Aug 2000
    Austell, Ga.
    Something of far greater importance than a simple "Megger" reading is called a "Polarization Index". What with the windings of most centrifigal motors being bathed in both refrigerant and oil mixture a "PI" test can and will give a far better deternination of good/bad than any simple "Meg" reading. The megger voltage is applied, the first reading is taken, then for 10 minutes with the megger still connected a second reading is taken.
    In summary, if the insulation system is clean and dry, the insulation resistance will increase with time( a smaller current). An insulation system that is contaminated with water, oil or is weak will show little if any increase with time.
    James G. Biddle (now AVO Corp. of Dallas, TX) publishes the following table for the Dielectric Absorption Ratio (Polarization Index)
    Condition 10:1 Min Ratio
    Dangerous < 1
    Poor <1.5
    Questionable 1.5-2.0
    Fair 2-3
    Good 3-4
    Excellent > 4
    I have given the ratios for the 10/1 min. test. A 60sec/30 sec. test is also made and the corresponding values arefrom top to bottom) <1.1, 1.1-1.25, 1.25-1.4, 1.4-1.6 and > 1.6. Many technicians prefer the shorter test times especially if they have a hand crank test set.
    Some References
    "A Stitch In Time..." by James G. Biddle pub. 21-P8
    Insulation Testing by D-C Methods by James G. Biddle pub. 22t1a-1975
    Principles of Dielectric Engineering, by Andrew Blanck, Rutherford Research Products Comapany
    The Characteristics of Insulation Resistance by Sydney Evershed, presented to Institute of Electrical Engineers, London, 27 Nov., 1913
    Ain't "None" of us as smart as "All" of us..