01-19-2012, 10:45 AM #1
Hello experts in order to replace the oil sump sensor is necessary remove all the refrigerant of the unit ?????
could you please advise
thanks in advance
01-19-2012, 12:21 PM #2
remove the refrigerant does not require
01-20-2012, 10:34 AM #3
- Mar 2007
- Thailand
- 35
01-20-2012, 06:13 PM #4
- Dec 2010
- georgia
- 69
If your machine has isolation valves, You can transfer refrigerent to the condenser to change this sensor.
01-20-2012, 06:27 PM #5
Why don't they put that thing in a well?
Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
01-21-2012, 01:49 PM #6
- Jun 2010
- northwest connecticut
- 55
You can put the charge in the condensor with an isolation valve on the dicharge of the compressor and liquid lines, you should have flow through the cooler while you are doing this also.{ to keep from freezing a tube. Drain the oil and good to go, also make sure the oil heater is disconnected before oil is drained. Good luck!
01-21-2012, 02:12 PM #7
we decide with the owner remove complete charge of refrigerant also change the oil put new sensor and filters and again put the unit on service.
thanks all for the support opinions and thoughs
regars
oscar
06-19-2012, 09:19 PM #8
Oil sump temp sensor shows code 267. Fail sensor. -40*f.
When I compare my resistance and voltage drop readings against the Carrier manual it tells me all is good. I've measured at the sensor and at the pic 2 panel. Reset the alarm. A few hours later the alarm comes back. Anyone have this experience?ENJOY THE RIDE
06-20-2012, 07:19 PM #9
- Jul 2008
- LOS ANGELES
- 24
pump the charge over to about 1/2 psi and drain the oil level below the sensor and be PDQ