    York rtu intermittent ign driving me insane. HELP

    Older York rtu Md# d6cg060n07946ecc

    This unit will not light off! Started out with induce running,then ignition was sparking and I could smell gas at exhaust. So I replaced ign control thought the spark was weak. No go. Then I threw a gas valve in. No go. I cleaned the sparking contact point and made sure burner had a good ground. Pulled burner out and made sure pilot tube was clear. I blew through everything and felt it coming out pilot holes. I can see it sparking on the pilot tube and smell gas SO WHAT THE HELL. The last thing I did before it got dark was check inlet pressure at the gas valve. Without running it was 6.0. I know the other york rtu next to it had an inlet pressure of 8.0 not running and that runs fine. These rtu's have gas reg's before the gas valve. Tomorrow I want to see what the inlet drops to when trying to fire?????Maybe its dropping below 4.0 And Im getting 26volts at pv on the gasvalve so its not voltage issue. My next replacement part will be the reg. Dam this is getting crazy. Alot of part changing. Thats not how to do it. If you have a suggestion please let me know.
    Thx Bill

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    When you say pilot tube do you mean the crossover tube? Did you check the orifice? Pilot outlet pressure should equal inlet pressure. Are you sure the pilot is not lighting? Maybe it lights but there is no flame rectifiction. Could be a draft issue or HX issue also
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Feb 2011
    Location
    Fogelsville, Pa.
    Posts
    137
    Post Likes
    Thread Starter
    Quote Originally Posted by 2sac View Post
    When you say pilot tube do you mean the crossover tube? Did you check the orifice? Pilot outlet pressure should equal inlet pressure. Are you sure the pilot is not lighting? Maybe it lights but there is no flame rectifiction. Could be a draft issue or HX issue also
    Yea crossover tube and orfice are clear. Pilot def not lighting. Could be hx Ill have to check tomorrow. So if inlet pressure is 6.0 the pilot pressure should be 6.0??

  4. #4
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    645
    Post Likes
    Cut 1/2" off both ends of your spark plug wire I've had these spark but not hot enough due to resistancein the wire plus you should check or replace the pilot assy./spark assy.

  5. #5
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    135
    Post Likes
    Sounds like you have the exact same problem I have been having with the York im working on. If you are using LP gas then you should have 11" at the pilot outlet on the gas valve. Other guys have suggested the burner plate at the exhaust collector box, and the plate that is above the inducer fan could be rotted out. I inspected mine today and they were kinda rough but not rotted out enough to allow excess airflow across the hx. Damn you York haha

  6. #6
    Join Date
    Feb 2011
    Location
    Fogelsville, Pa.
    Posts
    137
    Post Likes
    Thread Starter
    Quote Originally Posted by controldude View Post
    Cut 1/2" off both ends of your spark plug wire I've had these spark but not hot enough due to resistancein the wire plus you should check or replace the pilot assy./spark assy.
    Oh yes that was replaced too.

  7. #7
    Join Date
    Feb 2011
    Location
    Fogelsville, Pa.
    Posts
    137
    Post Likes
    Thread Starter
    Ok. Hx looks fine and so does the collector box. When trying to run, the inlet pressure is almost 5.0 natural gas.
    I looked in there with a mirror and it looks like every once in a while the crossover tubing will lite a little bit near the spark but it will not cross over? I again cleaned out pilot tube and crossover. No luck. Maybe the cross over holes are to small? I'd hate to ream them out. Any other suggestions? New pilot assembly?

  8. #8
    Join Date
    Jul 2008
    Location
    Mid Michigan
    Posts
    321
    Post Likes
    Have you taken out the cross over tube and blown it out?

    You could have a spider web or something else blocking it causing your

    problem.
    Waddya mean don't thaw out the frig with a knive?

  9. #9
    Join Date
    Mar 2007
    Location
    Orange County NY
    Posts
    218
    Post Likes
    Quote Originally Posted by knewguy View Post
    Have you taken out the cross over tube and blown it out?

    You could have a spider web or something else blocking it causing your

    problem.
    I agree this is a common problem on the York RTU's. Sometimes I have to use a piece of wire to clean them out because air, or N2 pressure won't dislodge the spider eggsacks.

  10. #10
    Join Date
    Feb 2011
    Location
    Fogelsville, Pa.
    Posts
    137
    Post Likes
    Thread Starter
    Yea already ran wire threw. Blew out with air.

  11. #11
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Quote Originally Posted by jackpiner View Post
    I agree this is a common problem on the York RTU's. Sometimes I have to use a piece of wire to clean them out because air, or N2 pressure won't dislodge the spider eggsacks.
    Just had one that did the same thing. Make sure your flame sensors are positioned correctly. I had that issue also. It would light the pilot but then go out with no flame sense. The rod was in the flame but not enough of it. Moved it a little and it has been fine for week now.


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  12. #12
    Join Date
    Dec 2011
    Location
    Asheville, N.C.
    Posts
    103
    Post Likes
    What was the reading from the controller to the PV? Corroded or broken wire maybe? Sorry. I just noticed you had correct voltage at pv.
    Last edited by mikeybow; 01-19-2012 at 09:13 PM. Reason: 26 volts at pv

  13. #13
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    I serviced a Dork unit a few years ago that would light if I was on site but not when I left. I went back every day for a week. Checked gas pressures, voltages, everything I could think of. After changing the gas valve and the pilot head/ignitor/sensor it STILL would not light consistently. I finally noticed the pilot flame was barely encompassing the sensor. I bent the flame deflector down a little to direct the flame onto the sensor.
    That fixed it.
    The angle of the deflector was the same on the old and new parts. I hate it when a new part doesn't work properly!

  14. #14
    Join Date
    Sep 2002
    Posts
    17,037
    Post Likes
    I had a 5 ton York where the orifice that is pressed fit into the crossover tube was loose,would not light! replaced ok!

  15. #15
    Join Date
    Dec 2011
    Location
    Southern Oklahoma
    Posts
    55
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    Just had one that did the same thing. Make sure your flame sensors are positioned correctly. I had that issue also. It would light the pilot but then go out with no flame sense. The rod was in the flame but not enough of it. Moved it a little and it has been fine for week now.


    Sent from my iPhone 4s
    using Tapatalk
    I'm wondering if these flame sensors can vibrate/rotate within the ceramic??
    I went on an old york rtu on monday and the flame sensor wasn't even close to the flame.

  16. #16
    Join Date
    Feb 2011
    Location
    Fogelsville, Pa.
    Posts
    137
    Post Likes
    Thread Starter
    Quote Originally Posted by coolperfect View Post
    I had a 5 ton York where the orifice that is pressed fit into the crossover tube was loose,would not light! replaced ok!
    Yea this orfice is loose, I can pull it right out. I just can't see it being that. It's worth a try though.

  17. #17
    Join Date
    Feb 2011
    Location
    Fogelsville, Pa.
    Posts
    137
    Post Likes
    Thread Starter
    Quote Originally Posted by qwerty hvac View Post
    Just had one that did the same thing. Make sure your flame sensors are positioned correctly. I had that issue also. It would light the pilot but then go out with no flame sense. The rod was in the flame but not enough of it. Moved it a little and it has been fine for week now.


    Sent from my iPhone 4s
    using Tapatalk
    If the pilot does light its only neat the spark. The flame sensor is at the other end of the crossover tube. The flame hasn't made it there yet.

  18. #18
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by billymons View Post
    If the pilot does light its only neat the spark. The flame sensor is at the other end of the crossover tube. The flame hasn't made it there yet.
    If you are telling us your inlet gas pressure when trying to light is bellow 5 inches wc you inlet pressure is too low.

  19. #19
    Join Date
    Feb 2011
    Location
    Fogelsville, Pa.
    Posts
    137
    Post Likes
    Thread Starter
    Quote Originally Posted by second opinion View Post
    If you are telling us your inlet gas pressure when trying to light is bellow 5 inches wc you inlet pressure is too low.
    Yea I always thought I should have 7 inches but the gas valve says min 4 inches???

  20. #20
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    You will lose 1 inch going through the valve and that would give you a minimum of three on your manifold side. If the unit next to it has 8'' then it should be no problem bringing this unit up and your problems will more than likely go away.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •