    Thermostat / Heat Pump Challenge

    Hi,

    I'm a licensed contractor, , Ive installed around 15 Gas packs
    Now I'm installing a package heat pump and running into problems with wiring the thermostat for a york 2.5 ton Heat pump system with Heat Kit

    Ive got it wired up to a honeywell 3000 series thermostat, Using the 2H/1C config.

    Could you guys check my work for the thermostat wiring, Im not getting a response on the heat cycle, fan comes on fine.

    On the thermostat I jumpered E and AUX and connected it to W2 on the unit
    I wired B on the thermostat to C on the unit (per the schematic)
    From the unit to the thermostat G to G , O to O, Y to Y, R to R
    On the thermostat I left L and C open.

    Below are all the pertinent schematics

    so did I cross my wires? What correction do I need to make?

    TIA,

    Warhorse








  2. #2
    Join Date
    Sep 2002
    Location
    The Alamo
    Posts
    3,025
    Jumper w1 w2 on the unit and see what happens.
    Read, read, read!

  3. #3
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    B on t-stat to C on what unit.


    you're fixing to let the magic smoke out of something
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  4. #4
    Join Date
    Sep 2002
    Location
    The Alamo
    Posts
    3,025
    Quote Originally Posted by dandyme View Post
    B on t-stat to C on what unit.


    you're fixing to let the magic smoke out of something
    Good one.

    I am so used to Trane's C being B.....

    LOL!
    Read, read, read!

  5. #5
    C on what unit?

    On the heat pumps terminals

    Heat pump = Unit

    I'd like to keep the magic smoke inside there please.

    jumper w1 and w2

    will this work?

  6. #6
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,613
    B on stat to C on unit is dead short when you call for heat.

    I would agree that jumping W1 to W2 will get your electric heat on.