Page 2 of 6 FirstFirst 123456 LastLast
Results 14 to 26 of 67
    Connecticut
    Quote Originally Posted by CraziFuzzy View Post
    Something to think about is that there is a LOT of variables in a chiller plant. To truly optimize the whole plant, you must know how all those variables will affect the system. (Things like Chiller efficiency over it's load range, and how this changes with condenser water temperature. The electrical use for the Cooling Tower fans over their range, etc).
    I agree 100%. I think I am going to leave the condenser water alone for now. I will be putting VFD's on the towers and condenser water pumps. The thing that just kills me is they had a plate and frame for free cooling in the winter and they ripped it out! Now they are complaining about having to run the chillers all the time.
    yeah, pretty smart move.
  3. Likes oldhweller liked this post
  4. #16
    Aug 2009
    Jurupa Valley, CA
    Quote Originally Posted by The Reaper View Post
    Yeah, the biggest change in chillers over the last 10-15 years has been the capability to run with much lower condenser temps. With the older chillers, as you've already eluded to, there really isn't much you can do for optimization, aside from resting on the chilled water supply temp based on zone demand (the goal should be for the most open chilled water valve in the facility to be near 100% open).
    The old chillers can't handle the newer methods for increased efficiency, like lower cond temps, variable primary flows, etc.
  5. #17
    Jun 2012
    Portland. Oregon
    ClimaCheck Performance Analyzer
    Have any of you heard of the ClimaCheck Analyzer? This tool is by far the most advanced tool for you to get all the information you want regarding optimization of a chiller. Take a look at this
    Advertising Link Removed
    Last edited by Chris_Worthington; 06-17-2012 at 12:24 PM. Reason: Advertising Link Removed
  6. #18
    Greater Seattle Area
    looks more like an ad for your company.
  7. #19
    http://www.efftec.com/efftrack/maxim...efficiency.php
    Dont know if it's any good,but they have good articles about chiller operation.
  8. #20
    There are two I have limited experience with, Optimum Energy and the CPECS from Smardt/Kiltech.
    They are both Tridium based, the Optimum Energy one the last I heard requires a annual fee to continue operating. I have heard figures as high as $20k a year. I also believe they will not show you any of their code.
    The CPECS one is also a Tridium based application, it runs on a softjace and uses Kiltechs controllers (I/O Boards) integrated to the softjace through Modbus TCP to chillers and 485 to the VFD's. The one I worked on they gave me full admin access and there is not an ongoing annual fee I am aware of.
    I'm sure there are many others out there. It's really about understanding all of the efficiency curves of your equipment and using the code to determine the sweet spot to be operating in at a given time based on load profile and outside conditions.
  9. #21
    San Diego, CA
    Quote Originally Posted by controlgeek View Post
    Wow, they act like it's rocket science... I can send you a station done in the 3.0.99 days, where all the logic was done in the JACE, using standard kitcontrol blocks. It did not look pretty, and didn't work all that well either. I think they wised up and packaged it all in a module. Still, I take it all with a grain of salt. If it sounds too good to be true, it usually is.
  10. #22
    Jan 2013
    Advertising not happening here....
    One and only warning given
    Last edited by Chris_Worthington; 01-07-2013 at 09:57 PM. Reason: Advertising not happening here.... One and only warning given
  11. #23
    Mount Airy, MD
    Quote Originally Posted by tekEddie View Post
  12. Likes oldhweller liked this post
  13. #24
    Dec 2008
    Digo,
    Could you send me the station you mentioned, I'm currently trying to play kitcontrol in the JACE.
    Quote Originally Posted by digo View Post
  14. #25
    Southern California
    Armstrong Pumps has a central plant optimization controller. I think that it is BACNet based. I have seen it in action once.
  15. #26
    May 2013
    Cool Hi Digo
    Hi Digo,
    Appreciate if you could share the station that you made a while ago ,may be i can have a better understanding and tweak the same .
    Thanks in advance