    awesome guys... thanks for all the input. I'll post back tomorrow after they get here and do what you recommended - or as much of it as I can get them to

  2. #28
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    5,098
    Post Likes
    It might improve air delivery performance to the furthermost rooms by reducing the main trunk after the closer branch runs.

    In a Reducing Trunk System the main trunk run is reduced in size usually after each one or two branch takeoffs.

    These multiple size reductions make it possible to maintain a constant ft/min velocity & static pressure in the trunk even though the total air volume is reduced as each branch is supplied.

    This type of system takes a little more material to build and requires more labor to fabricate and install. Another major concern is that there are more joints to air-seal with mastic.

    However, those trunk reductions ‘regain’ the velocity & static pressure needed for the remaining branch runs & supply air diffusers.

    The same reduction principles apply to the round duct branch runs - where they are split into two outlet runs, etc.

    IMO, genduct gave you good advice; Using a main trunk would be the better way to go, with shorter runs of flex duct, if you have to use flex, stretch it tight & use supports a max of 5 feet apart to keep it straight as possible.
    Last edited by udarrell; 01-17-2012 at 06:55 PM. Reason: Typo...

  3. #29
    Join Date
    Jan 2012
    Posts
    13
    Post Likes
    The contractor come by and fixed the crushed flex ducts to the problem rooms... but as we all suspected it helped a bit but did not fix the temp balancing issue completely.

    They do not want to build a new trunk, plenum, or redo any of the existing ducts. - I think this is fine since they agreed to do the balancing dampers.

    They were not prepared with the balancing dampers... so they will be coming back a week from this Friday to install 3 16" dampers on master branch & each branch for the 2 main areas.

    Can you guys give me tips on how to use the balancing dampers to get rooms balanced?... since these guys are definitely not AC guys.