goodman 90+ intermit. locking out
have a 6yr. old goodman 90+ locking out [1 flash ]
m# gms90904cxs s#0409798428 cleaned sensor and
replaced glow coil. the 1 flash on the panel is kind of vague,
anyone come across this?
-
01-15-2012, 09:01 PM #2
One flash is a lockout due to an excessive number of ignition retries. The possible causes are:
Failure to establish flame.
• the cause may be no gas to burners, front cover pressure switch stuck open, bad igniter or igniter alignment, improper orifices, or coated/oxidized or improperly connected flame sensor.
or
Loss of flame after establishment.
• the cause may be interrupted gas supply, lazy burner flames (improper gas pressure or restriction in flue and/or combustion air piping), front cover pressure switch opening, or improper induced draft blower performance.
It is just going to take researching each one to see if you can find the culprit.Instead of learning the tricks of the trade, learn the trade.
-
01-15-2012, 09:10 PM #3
Professional Member
- Join Date
- Jan 2012
- Location
- Ashland Ky
- Posts
- 19
If it cant estabish a flame it may also be to no or a weak ground connection.
-
01-15-2012, 09:49 PM #4
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,975
May be dirty burners and the flame not crossing over all the way.
Beware of advice given by some guy on the Internet.
-
01-15-2012, 10:23 PM #5
New Guest
- Join Date
- Jan 2010
- Posts
- 1
It is gas valve.
-
01-15-2012, 10:29 PM #6
Professional Member
- Join Date
- Dec 2011
- Location
- bedford ind
- Posts
- 1,080
if it is propane, check for burp tube blockage
-
01-16-2012, 09:05 PM #7
Professional Member
- Join Date
- Apr 2009
- Location
- massachusetts
- Posts
- 44
ended up putting one of the large white-rogers universal glow coils in
and so far so good.
-
01-16-2012, 09:58 PM #8
Professional Member
- Join Date
- Jan 2010
- Location
- over here
- Posts
- 458
Are the drain tubes on the same side as the collector trap? If they arent the furnace acts irratic and can throw different codes. see it all the time on new installs. just a thought.
-
01-17-2012, 10:10 AM #9
Professional Member
- Join Date
- Jun 2000
- Location
- N. W., IN
- Posts
- 1,016
at 6 years it's likely time for a trap cleaning too.
-
01-17-2012, 10:03 PM #10
Professional Member
- Join Date
- Apr 2009
- Location
- massachusetts
- Posts
- 44
jinxed myself, came back in tonite.
will try all these suggestions tomorrow.
-
01-18-2012, 06:18 AM #11
Professional Member*
- Join Date
- Sep 2004
- Posts
- 115
Just posted about the same code. I had bad connections on gas valve. These things are always causing problems.
Check everything twice. I've had to add a second flame sensor to keep some of the goodman equipment running.
-
01-18-2012, 08:54 PM #12
Professional Member
- Join Date
- Jul 2009
- Location
- Northern area between Alantic and Pacific
- Posts
- 106
Check your gas pressure,burners,flame sensor,ground circuit,circuit board.....
-
01-18-2012, 10:34 PM #13
Regular Guest
- Join Date
- Jul 2010
- Posts
- 19
Good point for people not to familiar with amana/goodman. Also check to see if the fitting in the exhaust 90 (off the I.D. Motor) is plugged. Is the furnace sloped properly? OHM out the pressure switch to see if the contacts are dirty.
If the ignitor was working before I don't think you've found the problem yet (could be wrong). Other then dirty burners (which you can see) there's not too much else from there.
Dale