    notice the potential problem? lol

    brand new rtu i encountered recently. the company i work for didn't install this. the remedy for lack of heat was a breeze to diagnose. the idiots who installed & set this thing up r known residential scum/crooks/hacks but i didn't even know they did commercial. they def had no concept on how to set up an economizer. while there i found a few things i wrote up including the pic ... how long into cooling season do u think it will take for a big $ repair? Name:  uploadfromtaptalk1326567510816.jpg
Views: 1037
Size:  59.0 KB

  2. #2
    Join Date
    Jan 2012
    Location
    British Columbia
    Posts
    76
    Oh my ,,,, I guess it will be OK if the compressor never runs for more than a couple hours , ....total........Ever!

  3. #3
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    4th straight day over 80 degree; there'll be a loud noise, then no cooling.

    if od coil gets dirty, it won't take 80 degrees


    hell, just disconnect the od fans and let's find out
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547

  5. #5
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Quote Originally Posted by madblack View Post
    Oh my ,,,, I guess it will be OK if the compressor never runs for more than a couple hours , ....total........Ever!
    Red compressors don't run as hot as black ones....
    Technical incompetence is NOT a sales tool....

  6. #6
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    I'm thinking on my next visit there will be armaflex on that discharge line. lol

  7. #7
    Join Date
    Feb 2010
    Location
    Ontario Canada
    Posts
    1,341
    Talk them into letting you rewire it properly, should not be too hard....
    Never give up; Never surrender!

  8. #8
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    i wrote my invoice explaining everything that stood out that's wrong & it got quoted w/ pics to go with it. its a month old so i wouldn't b surprised the install company gets called back .. there were some other serious code violations that were in that quote.

  9. #9
    Join Date
    Dec 2004
    Location
    maple ridge, bc
    Posts
    107
    Seriously now, it seems to me that most guys are either too lazy to set up economizers or too lazy to read the manual. Sigh.

  10. #10
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Quote Originally Posted by deerwhistle View Post
    Seriously now, it seems to me that most guys are either too lazy to set up economizers or too lazy to read the manual. Sigh.
    the service call was in relation to that. I've come to the conclusion a long time ago many ppl don't understand an economizer & even more don't respect the minimum % the balancing company sets them to

  11. #11
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    947

    Don't

    you know? That's to keep the electricity in the wires warm. That way it flows better.
    GO NAVY, BEAT ARMY!

    A DECADE OF DOMINANCE! +2

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event