    Considering R22 AC myself

    Vince,

    A Trane dealer says when the R22 outdoor condensor (compressor) wears out (No R22 units after 2010), he does NOT recommend indoor coil (evaporator) be flushed & reused with R410a condensor. A commercial HVAC tech said it's ok (maybe depends on indoor coil type???). 3rdgenhvac's remarks (410 higher pressure etc) is one more reason I am leaning towards a Trane R22 (1.5 or 2 ton XB13). The Copeland website says 2 million scrolls sold. I'm sure they are good (quiet too). But, it reinforces R410a hasn't been around as long, like cde72's comments about "R410a questionable history of reliability". I hope to have a system with NO leaks and not need recharge (impossible?). Do you really plan to be in your condo 15 years from now?

  2. #28
    Join Date
    Mar 2006
    Location
    South Jersey
    Posts
    86
    Good question XV, I'm rehabbing the entire place so I figure I'll be there for the next 5 years or so. I would hate to use the 410A and then have some problems with the lines which are imbedded in the walls and ceilings. I do think the installers I have talked to will do an adequate job flushing the lines, but the pressure (psi) difference between the 2 refrigerants does have me concerned. The American Standard guy feels I should stick with the R22, Carrier and Trane feel that there should be no problem changing to 410A. All of the new equipment is labor and parts warranted for 10 years, if something happens to those lines it's all on me and getting those things replaced is going to be big buckeroos.

  3. #29
    Join Date
    Mar 2006
    Location
    fla
    Posts
    33
    Well there are a couple of items up for discussion here. before we get into those though, either one you go with if installed by some one who knows what they are doing will give satisfactory service for 10+ years with no more than routine maint.
    Having said that, is there a drop in replacement for 22, yes, is it more expensive, also yes but has only been out for a few months and reg. 22 is still bieng imported so that is to be expected. nu22 is suppose to be a/an exact drop in replacement so no oil equiptment issues.
    410a is a newer refrigerant, is more enviornmentaly friendly than reg 22 and does operate at higher pressures. can you re use the 22 line set if flushed. mfg say yes is pressure diff and issue.. no the same soft copper is pulled through (if new) for 22 and 410a installs dont know the burst pres of 3/8 copper but probably 2000 or so psi more than you'll ever put on it. coils must be matched to the outdoor unit irreguardless so no issue there
    410a and poe oil is a more efficient refrigerant and has a bit higher heat tranfer ratio and poe is a very good lubricant it does have a very high affinity for water though. what does this mean if a system is installed and checked correctly, nothing as its a sealed system. if you got a leak however, it would be almost impossible to get all the water out.(not impossible but a long, expensive process, with many filter driers and a lot of vacuume) 410a also has a critical temp of 165. meaning it seperates its componets at that temp. they seem to recombine ok in the condensor, but what the long term effects are no one knows. 22 on the other hand has a critical temp of about 225, so no worries there. and once again if installed correctly should last more than long enough to get to gen 4 frfrigerants and seers. so go with who you like, either will give good service

  4. #30
    Join Date
    Aug 2002
    Posts
    1,642
    I got a question for anyone that has information about the supposed drop-in replacements for R-22..

    Are any of the supposed drop-in replacements recommended by any manufacturer or compressor manufacturer?

    Are any of the supposed drop-in replacements allowed to be sold yet in the US with approval from the EPA?

    Are the supposed drop-in replacements a mix that leaks at the same rate that they can be topped off in case of a small leak or a shrader valve leak? Or must they be totally recovered and recharged from a vacuum?

    What is the affect of the sensible and latent capacities if a drop-in is used in place of R-22? If differant what percentage of loss/gain on the sensible and latent capacities?

    Do you know of any manufacturer that is currently working on a unit that is designed around the drop-in replacement or has one out on the market yet in the US?

    Not trying to knock a drop-in but every drop-in that I have researched in the past had serious capacity issues or were two differant mixes which if a small leak happened would require total refrigerant recovery and recharge.. Any information you have I will surely listen..

    Thanks
    J

  5. #31
    Join Date
    Feb 2006
    Posts
    302

    R22 Drop In

    On page 1, tostaos says:

    There are HFC refrigerants to replace R-22 in any application. (NU-22 from ICOR is one) You will not have a problem with availability of refrigerant for a system you buy today.


    If I remember reading the manufacturer website right, supposedly there were no capacity issues.

    ICOR International NU-22

    HOWEVER, that is their claim and I'm just a homeowner.


  6. #32
    Join Date
    Feb 2006
    Posts
    302

    R22 Linesets Not For 410a Per This Link

    Vince,

    If you want to read more about your question about R22 linesets and whether to re-use with 410a, check out this thread. I stumbled on it while searching on HSPF.

    The R22 / 410a lineset part starts on page 2 of the thread:

    http://hvac-talk.com/vbb/showthread.php?threadid=70906


  7. #33
    Join Date
    Mar 2006
    Location
    South Jersey
    Posts
    86
    Thanks XV. I see you posted at 4:49 AM. Don't you go to sleep?

  8. #34
    Join Date
    Feb 2006
    Posts
    302
    Vince - I put in a contract for a system on Thursday and was working up a detailed post for the HVAC Talk pros' opinions in case I needed to request a change on Friday before the contractor orders the equip. I might ask on Monday about the XL15i upgrade cost. But, even if I don't, I still think I'll be happy. The NATE website says 100% of the techs at the contractor's company are NATE certified.

  9. #35
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,579


    It is not absolutely necessary to replace the lineset when replacing a 22 system with 410A. However,it is necessary to ensure that the lineset is correctly sized for 410A and is clear of most of the oil from the previous system.

    For details on the differences between 22 and 410 read the following article.

    http://www.bacharach-training.com/norm/410.htm

    Norm

  10. #36
    Join Date
    Apr 2006
    Posts
    2
    go with the r22 cause 41oa must be blazed.and i bet you there is many fitting in wall that will not last long at all if 410a is use.

  11. #37
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,579
    Originally posted by tomsinex
    go with the r22 cause 41oa must be blazed.and i bet you there is many fitting in wall that will not last long at all if 410a is use.
    Say what! Nobody should have been using soft solder on any system in the first place.

  12. #38
    Join Date
    Apr 2006
    Posts
    2

    Hmm

    all the guys around here do it,me i blaze everything

  13. #39
    Join Date
    Oct 2003
    Location
    Valdosta Ga
    Posts
    847

    Wink

    Most new 3ton 13seer units on up you will need you to change to a increase in line size.
    chicken the sky is falling don't worry about stocking up on r-22 gas you will not never use.
    Retro fit r-12 systems has showed us something will go in there and work better.

Page 3 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event