What wire size, and heat strip size should be used.
I have a Goodman aepf183016 and an hkr 15 cb heat strip. I am wondering what size of wire to run to the Unit. The distance of the wire is about 15 feet. I live in Nebraska if that matters. He mentioned maybe using 4 gauge or 6 gauge Romex.
Another question is the heat strip he sold me being 15 kw isn’t listed on the unit. I hope I can trust his judgement but is this normal to use a larger heat strip? The guy who I purchased it though said to run the unit on a low fan speed. Is this ok, or should I downsize to the smaller 10KW heat strip.
Installer is coming Saturday and I would like to make sure everything is the proper size. Any knowledge would be great.
Thanks
-
01-10-2012, 08:06 AM #2
Professional Member*
- Join Date
- Apr 2001
- Location
- MINN
- Posts
- 932
#6ga wire should be ok. but I would leave that up to the electrician on site.
As for blower speed it needs to be set after instulation to acheive proper temp rise.
-
01-10-2012, 08:29 AM #3
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,748
-
01-10-2012, 09:35 AM #4
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
01-10-2012, 10:23 AM #5
aepf air handler
10 kw is cfm this furnace does, proper wire size for a 60 amp circuit is #4 copper, current code
Total Energy Management, inc
-
01-10-2012, 01:47 PM #6
Regular Guest
- Join Date
- Jan 2012
- Posts
- 8
Is #4 a four gauge wire? Should I purchase a new heat strip before he installs it? What would happen if he did install the 15 kw on a low speed. I'm stlil confused why he sent a larger kw than what the heat pump has listed. Do I need to change the circuit breaker they sent me if I downsize to a 10 kw heat strip. I forgot to mention do I need a wire that runs from the exterior unit?
Thanks for all the answers.
-
01-10-2012, 01:57 PM #7
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
01-10-2012, 02:08 PM #8
You really need to hire an experienced professional to spec out your system and install it.
Your DIY project is going to cost lots more in the long run.How tall are you Private???!!!!
-
01-10-2012, 02:29 PM #9
I would seriously consider redoing the power to both the indoor and outdoor units according to current code.
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
01-10-2012, 02:37 PM #10
Regular Guest
- Join Date
- Jan 2012
- Posts
- 8
I think they all are professionals. I got worried when I read the 15 kw wasn’t on the side of the unit. It stated only up to a 10kw. Any advice where I can order a 10 online and get it by Saturday? Gunnery this isn’t a DIY project. A professional picked out the equipment for me. An experienced person is going to install it. I’m not sure about some people though. I’ve heard so many different things from different companies. Not sure what to trust. One guy said 4 gauge wires, another said 6. I’m just trying to see what other people recommend.
-
01-10-2012, 02:51 PM #11
You can't go wrong using a larger wire size. It's a little more in materials, but will carry more current with less line losses and less voltage droop. But you really should be following the National Electric Code.
A real rpofessional would be getting materials frmo a local supply house. A simpel google search can find a dozen online sources for components, some may or may not fit in your air handler. IF you're ordering online, you have to really know what you need.
Heat strips should have and normally would have been ordered with the air handler.
-
01-10-2012, 05:00 PM #12
A real professional doesn't spec the equipment and leave it up to the homeowner to buy...
Sounds like you're dealing with a moonlighter or someone very inexperienced...How tall are you Private???!!!!
-
01-10-2012, 05:52 PM #13
Regular Guest
- Join Date
- Jan 2012
- Posts
- 8
Yea i'm starting to have second thoughts on using him. He quoted $$$& to $$$$ to install everything. I assume thats an ok price?