We have been using vBox for M-Tools with XP OS. I had a Win7 32 bit machine I used to use and still can but it is getting long in the tooth. Our tech who does some buildings with a lot of VMA 1420's...
Type: Posts; User: billcontrols
We have been using vBox for M-Tools with XP OS. I had a Win7 32 bit machine I used to use and still can but it is getting long in the tooth. Our tech who does some buildings with a lot of VMA 1420's...
You can't change the branding that I know of. But the FX packages will let you use them the same as the M4. If you can get the packages from your supply chain. If you have both it is not hard to...
I have not done anything with Sedona, but from what I have seen, it may also have an Enable/Disable on the controller side.
What do the tuning policies and poll scheduler look like?
And If you look at the point property sheet what does the Proxy look like.
And try a force read and force write on the proxy.
You need...
One possible solution may be a Debounce filter. Contact must be open or closed for a specified length of time before the input shows the switch. An induced trip likely does not last very long. A...
Did you program the PCA? It sounds like the PCX is having an issue with the PCA on the SA bus. Maybe the Boot and Main code are different in the 2 devices? I guess I'd unplug the FC bus and plug in...
I have done this in the past. I think the local controller has to be Mac 4 on the MSTP. I recall not finding a place to change that. But I may be wrong. And the NAE can be a MSTP to IP router. All...
I typically use the layer method grputtick described.
"Is that right? Old."
Hey not that old...
I have OLD JCI N2 ASC's running for over 25 years. The keep running and do just what I expect them to. Not saying they are not obsolete, but we can still...
On the old stuff I have VAVLF, you configure the unused I/O by Launching the Wizard on the specific hardware points you want to use right from the Niagara wizard view of the device. I also remember...
The old stat must not have activated G on a call for heat. The furnace or heater must run the fan when W is activated on the old stat.
So try just disconnecting the G wire. I am guessing this is...
Ord would be "slot:" (remove the quotation marks)
text %.% or %displayName% or many other possibilities.
I have also seen schedules that hit the tuning reset at a non-critical time (unoccupied) so tuning starts fresh each morning or each Monday morning, depending on the length of time it takes for the...
S2sam and SteveS4 probably know the most about what you are trying to do as anybody. This would include people who work for JCI. System91 was developed in Europe 30 years ago. Most of those guys have...
I always seem to miss something...
In the License Manager on the FX80 and FX Workbench, you should see 2 licenses, the FacExp.license, and Johnson.license.
Using a different brand workbench the driver would not be licensed on the...
"If I recall shouldn’t the BACnet over IP devices automatically appear under the BACnet
Folder"
No you have to discover and add them like any other device. Or Manually add them.
Hardware tests...
Are you able to "ping" both devices with your laptop plugged into a hub/switch connecting these two devices (Test the connection to the NICs)?
Can you pull the LAN2 cable from the...
Here in the northeast many buildings do not have cooling. Without cooling the dewpoint can be assumed to be equal inside and out. In this case, we often run units for several hours at night to pull...
Try with %displayName%, note the upper case N.
The slot: reference works when you use the graphic as a view in the Device. This has been the way to do it since AX. I also use the string writable...
The JACE programming is more like the System program you can do in the Programing Folder. The program objects are dragged in from the Kit Control pallet onto a wire sheet view. The wire sheet can be...
I just wonder what they are saying with the Rose? Am I supposed to get this for my romantic interest? Or is the Portable PC supposed to be my romantic interest? Or I just do not understand anything...
What Cagey said.
At least this one had Windows programming tools. There other thread today hac a DC9100 which only had DOS tools. Both are dead products. (Though I can work on a DX-9100 if the...
DC-9100. Replace this. There is no fix. There is no access to the program. It will save you time and money to just replace with something new.
It has lived about 25 years longer than any that I...
This will do it using the wire sheet.
Edit adding formula in text.
(inA * (inC / 100)) + (inB * ((100-inC) / 100)) as 'out'
846589
You could try this link on the NYS OGS purchasing system.
https://online.ogs.ny.gov/purchase/prices/7720123150PL_NewEnglandMechanical.xlsx
I have nothing to do with this, I just know this stuff...
You can try doing Boot by itself. Then Main. And try a different connection. Options are Map tool, Ethernet Router, or Bluetooth BTCVT. I had a few FX-PCV that came back from our construction site....
Do the RS485 to RS232 converters show any life? (The exposed circuit boards.)
The local port should be 19200 baud and there should be some response with a terminal interface.
The technical...
Unless it is a virtual point using the Point Tags. Then you may need to run a "Join".
I was hoping there was an answer for this out there. I have also generated a new program from time to time in 10.4 only to realize later I need it at 10.2. In the case of the upgrade you did, have...
Once you set it to N2 you leave it in N2. The CCT will need to connect with MAP tool plugged into the SA port for the controller you want to do CCT on. If there is another controller you want to...
MAP tool or BTCVT plugged into SA bus port. I dont think the BRTRP will work on the SA Bus, but someone else more knowledgeable will confirm this.
As far as the EF CT is concerned...
RIBXLCF
RIBXLCA
RIBXLCRF
RIBXLCRA
These will separate the voltages. We've been using them for years.
I have seen it too. Righ and Down near the edge but not at the edge.
Do this and precharge your bladder to the static fill pressure set on the fill valve or fill pump or whatever sets the fill pressure you want ( I would expect about 95.) The pressure reading at the...
What JCI Man said...
( I was going to answer, but the phone rang. Then...)
The MS-HAMMER-01 is a branch only product. The branch can sell it to you but they may not. (They won't sell to us.)
The FX-PCSLEDGE-3 is the Facility Explorer equivalent and will work on both MS...
OK my brother has a Ski Condo in rental and he uses it some weeks. He has 4 or 5 old T87 2 wire that operate valves, I think. He wants to upgrade to WIFI stats. I do Commercial BMS systems so lack...
You should check the diagram that is provided in the unit. It will be on the cover at the electrical end. There is a Controls by others diagram for ECM motors that is just enough different to make...
An important alarm class and an important alarm console for important alarms. All those default alarm class alarms help on the GUI and also log when something happens. Very useful but may not be...
This is what I use most.
https://www.amazon.com/dp/B00009V2QT/ref=redir_mobile_desktop?_encoding=UTF8&%2AVersion%2A=1&%2Aentries%2A=0
Zero and 9 volt 2 position tester.
Single point most of...
Just gave the video a 1 min look over.
Nice exercise. But not the way I would do it. (Is there a single proper way?)
It will work this way, but you can condense all those states into 1 output...
Or your head will have made a big enough hole in the wall you can fit your whole body through and you can escape!
I am guessing the UI will be better if you can login to the NAE on the Ethernet. But without some infor like user , password, and IP address that will be difficult.
Check to see if the COM port has changed?
Or, In the windows Blue tooth devices settings remove the BTCVT and re pair like new. Then Check the COM port and try it.
The import with the JCI point manager is done using the CAF file. I had trouble the first time due to importing the PRN. The AX workbench imposed some rules on the PRN file and some of the points did...
Here you go.
First take pressure switch 1 & 2 out of the picture. Connect terminal 2 to compressor 1 contactor and terminal 8 to compressor 2 contactor.
Now change the jumper 1 to 4 so it...
The DCM was not a Bad controller. In fact most controllers today can not match the capabilities of some parts of their specification. BUT...
They are obsolete. By almost 30 years. Time to remove...
When the gauge was plugged in you could see the pressure move up and down as you moved your hand in to adjust the calibration screw.
Also explaining to the school nurse why you have hypodermic...
I originally used a piece of telephone wire 24 or 26 solid. Strip each end about 1/2" with enough insulation left to span pin 1 to 4, Then coil the bare end around the small Honeywell stat wrench....