  1. Replies
    4
    Views
    1,042

    Yes. The soft JACE and the Loytec was working...

    Yes. The soft JACE and the Loytec was working fine. We had 9 floors full of this controller, with some Trane and Distech mixed in that worked fine when we moved them to a JACE 8000. We ended up...
  2. Replies
    4
    Views
    1,042

    No. They are...

    No. They are local:|module://honeywellLonSpyder/XL10NextGenXML/MandatoryMicro.lnml

    We had 8 trunks of these and only this one is doing this. We were not the installing contractor.
  3. Replies
    4
    Views
    1,042

    Can't see LON devices, service pin error

    We are adding JACES where there used to be one Honeywell soft JACE. So far so good until.... We have came across one group of controllers that will not talk to our JACE. We have verified the domain...
  4. Replies
    7
    Views
    2,648

    The device is a Solidyne MNL-700-101 which I...

    The device is a Solidyne MNL-700-101 which I think is actually Invensys. I've just rebooted the JACE to see if that helps it take the nan value. Maybe something got a little confused during the quik...
  5. Replies
    7
    Views
    2,648

    I found it in the master SNVT table and it shows...

    I found it in the master SNVT table and it shows that the max 3.4028E+38 and the min value is the same but negative. It says NAN and out of range are invalid.
  6. Replies
    7
    Views
    2,648

    Thanks amigo. The SNVT type is CountIncF. I will...

    Thanks amigo. The SNVT type is CountIncF. I will look up the SNVT and try to find its null value.
  7. Replies
    7
    Views
    2,648

    LON nci set to null

    We recently took over a site that was setup using LNS and iLon servers. I had to manually override an nci for the chilled water valve. Now when I try to release the control back to the controller I...
  8. Replies
    7
    Views
    4,364

    Thanks klrogers. I'd been looking into this for a...

    Thanks klrogers. I'd been looking into this for a couple days and thought I would throw it out here. Looks like it's proxy points.
  9. Replies
    7
    Views
    4,364

    I am sharing the points across the Niagara...

    I am sharing the points across the Niagara network. That wasn't stated in my post. I can proxy bind from the Niagara network to the Lon Network. I was looking for a solution to hopefully keep the...
  10. Replies
    7
    Views
    4,364

    Flat LON bindings across multiple JACES

    I have a site with multiple JACE's and an AX server. If I need to take a nvo out of JACE 3 and bind it to an nvi on JACE 6 can it be done without using proxy bindings? In the past on a single JACE...
  11. Replies
    7
    Views
    2,126

    Sometimes I just WAAAAYYYYY over complicate...

    Sometimes I just WAAAAYYYYY over complicate things! Thanks again! :gah:
  12. Replies
    7
    Views
    2,126

    Any hints on how I can write to that bit? I've...

    Any hints on how I can write to that bit? I've tried Linkmark but it says that I can't link baja:boolean to Lonworks:boolean. I've tried adding a lon boolean point. Converting to status boolean. Any...
  13. Replies
    7
    Views
    2,126

    Thanks klrogers. I had been looking at the...

    Thanks klrogers. I had been looking at the property sheet of the device but I guess I've overlooked that point for the past 2 hours! Thanks for pointing me in the right direction. Hopefully now I...
  14. Replies
    7
    Views
    2,126

    Distech RTU-L controller

    I have a customer that has made a request to be able to toggle from the graphic to set the fan to run continuously when occupied or not. This is a configurable controller and that option is in the...
  15. Thread: Trane BCI-I

    by sycontrol
    Replies
    12
    Views
    3,441

    When you discover the points find the point in...

    When you discover the points find the point in the discovery window. Click the plus beside the point and you will see a lot more options under it. One of those options will be a boolean point...
  16. Replies
    3
    Views
    1,333

    381 thank you very much. I have to use the iLON....

    381 thank you very much. I have to use the iLON. This is a customer requirement and they won't give, I've tried before. I actually don't even have access to the iLON, we just provide and install...
  17. Replies
    3
    Views
    1,333

    Loytec LS-33300CB

    I have a new building with 3 floors. If I have one panel where all my LON home runs come back to can I use the LS-33300CB to allow the devices on each floor to communicate with each other?

    I...
  18. Replies
    32
    Views
    10,168

    Matrix. Not disagreeing with what you said. ...

    Matrix. Not disagreeing with what you said. Just trying to understand.

    So if I put one controller and connect it to two JACE all would be OK?
  19. That's the same symptoms I had. I was like half...

    That's the same symptoms I had. I was like half the program was running but other parts were not. A brief power glitch will sometimes cause the controller not to reboot at all or not properly. I...
  20. What capacity are you at with the program size? ...

    What capacity are you at with the program size? I have had this happen with controllers that were at or pushing max recommended capacity. If you are much over 85% capacity then that is most likely...
  21. Replies
    6
    Views
    2,976

    I'm not much on the mechanical side but most...

    I'm not much on the mechanical side but most Trane units have a set of contacts where you can cycle it thru test mode. All the compressors will fire, fans on and heat if it's set up. You have to...
  22. Replies
    6
    Views
    2,976

    Depends on the type of unit and how Trane has it...

    Depends on the type of unit and how Trane has it setup. Looks as though Type A is space temp control. Make sure your occ and unocc setpoints are in the correct order. Looks like Type B is doing...
  23. Replies
    32
    Views
    10,168

    Hooking the FX 60 to the device probably wasn't...

    Hooking the FX 60 to the device probably wasn't the best of ideas. LON can only have one managing device. In this case it was the NAE. If you did a replace on the controllers on the FX 70 now it is...
  24. Replies
    32
    Views
    10,168

    Authentication key is under lon netmgmt. Right...

    Authentication key is under lon netmgmt. Right click the lon network and select properties. Expand Lon Netmgmt. Authenticate should be set to false. Authentication key on mine is all FF FF FF FF...
  25. Replies
    14
    Views
    4,060

    What's the busy time in your JACE? What type of...

    What's the busy time in your JACE? What type of bindings did you setup Normal, Reliable, Critical (that's from memory may have left some out). Reliable and Critical will have a lot more traffic. Is...
  26. Replies
    3
    Views
    1,030

    I had a similar issue. I ended up using open...

    I had a similar issue. I ended up using open relay. It uses the IP address of the JACE to authenticate on the mail server so you don't need a user name or password. Works great and no password...
  27. Replies
    5
    Views
    2,504

    You also have to taggle the out of service points...

    You also have to taggle the out of service points for the particular points you want to control via the BAS.

    From the Trane Document:

    You can define the amount of control that the BAS system...
  28. Replies
    12
    Views
    9,935

    If you have a JAR file loaded on a JACE that is...

    If you have a JAR file loaded on a JACE that is not in the modules folder of that installation then the software manager will tell you that it is not available locally. If you are 100% certain that...
  29. Replies
    14
    Views
    4,060

    If there are any LON bindings that would be a...

    If there are any LON bindings that would be a good thing to know. Not sure how to find that out in an NAE but you would look at the LON network wire sheet of a JACE. Do not recommission any of the...
  30. Replies
    3
    Views
    1,209

    there is an example on the JCI whatspossible...

    there is an example on the JCI whatspossible website of using these. I think Greg Wilmer posted it.
  31. Replies
    16
    Views
    4,216

    Awesome. Thanks!

    Awesome. Thanks!
  32. Replies
    16
    Views
    4,216

    AWESOME! I will say after talking to 3...

    AWESOME!

    I will say after talking to 3 different schneider electric folks in different states and two 888 numbers later.....I still have no one that can or will help me. Software would be GREAT!...
  33. Replies
    16
    Views
    4,216

    While our service tech was there I had him look...

    While our service tech was there I had him look at the lights. The yellow (rx) light was blinking rapidly like it was getting data. The green Tx light was blinking like once a second or maybe...
  34. Replies
    16
    Views
    4,216

    PEM 1 Controller

    I am supposed to look at a PEM 1 controller tomorrow. I know it has an ASD bus but is this proprietary to Invensys? Is there any software that I can use to look at the controller?

    It seems this...
  35. Replies
    7
    Views
    1,660

    You see the entire network using Rover? Go to the...

    You see the entire network using Rover? Go to the Lon Utilities Manager in the JACE. Set the command to Identify and set the SubCommand to Service Pin and press Execute. Go to any lon controller...
  36. Replies
    11
    Views
    6,400

    Yellow means the device is down. Orange meas the...

    Yellow means the device is down. Orange meas the device or point is in a fault condition. Either way you are not communicating with the units/points that are in this color. If they "blink" in and...
  37. Replies
    11
    Views
    6,400

    I would have a look at the bacnet device manager....

    I would have a look at the bacnet device manager. See if the problem units are in yellow which could indicate a communication issue. Also, sometimes a JACE reboot will clear up some things,...
  38. Replies
    11
    Views
    2,126

    While I agree 100% that it is TAB's function to...

    While I agree 100% that it is TAB's function to enter this data into the boxes, I am stuck doing this most of the time for TAB. Last job I sat for two days and opened boxes to max/min flow and input...
  39. Replies
    11
    Views
    2,126

    I see that point scrool. So if the balancer...

    I see that point scrool. So if the balancer tells me the box is flowing 300 cfm and the box is reporting 210 cfm how do I know what value to make the gain?
  40. Replies
    11
    Views
    2,126

    They do show up. The has to be a point somewhere...

    They do show up. The has to be a point somewhere to enter the actual flow readings from a flow hood so the box can calibrate itself and adjust the K factor. So if the box is reporting 340 cfm and...
  41. Replies
    11
    Views
    2,126

    I looked for it on trane website but didn't see...

    I looked for it on trane website but didn't see it.
  42. Replies
    11
    Views
    2,126

    UC 400 VAV Balancing in Niagara

    I've got some new Trane VAV boxes with the UC 400 controller in them. I've got the Tracer TU Balancing guide but I don't have Tracer TU. I've found most of the points that TU talks about but I...
  43. Replies
    22
    Views
    7,060

    Very nice. I've tried sketch up, GIMP and...

    Very nice. I've tried sketch up, GIMP and Blender. I struggle, bad just to make a straight line lol.
  44. Replies
    3
    Views
    1,272

    I do not think slot 8 is a writable slot in a...

    I do not think slot 8 is a writable slot in a JACE. If you look at any writable point in the FX 60 you will notice that slot 8 does not have the 2 arrows pointing down at the end of the slot.
  45. Replies
    13
    Views
    4,358

    Rover 7.1 did allow me to change the discovery...

    Rover 7.1 did allow me to change the discovery domain and I found all the devices. I was able to set the change the limits on the cooling min/max value to allow the cooling setpoint to change.
    ...
  46. Replies
    5
    Views
    2,171

    That's the part that's got me confused. The flow...

    That's the part that's got me confused. The flow setpoint is 400 cfm. The flow sensor is reading 0 cfm. The damper is closed and the damper output from the controller is calling for 0% damper. ...
  47. Replies
    5
    Views
    2,171

    I found this on this site as well. Maybe my...

    I found this on this site as well. Maybe my issues is similar, but there are about 60 other VV550's working fine.
    ...
  48. Look at the Facility Explorer group...

    Look at the Facility Explorer group
  49. Replies
    5
    Views
    2,171

    Trane VV550 Damper issue

    I'm working with some Trane VV550's and I've got 2 that have me scratching me head. It seems the damper will not open. The have an flow setpoint, duct in temp across the network seems fine. There...
  50. if you look at the whatspossible jci website...

    if you look at the whatspossible jci website there is a lot discussion about this topic. Seem if you have custom modules in a pre PCT 10 caf file they won't be in the caf file when you open it with...