  1. Replies
    20
    Views
    6,557

    I also think you have a pressure switch related...

    I also think you have a pressure switch related issue. Some manufacturers want to be sure the switch opens when the unit cycles off so as to avoid the possibilty of a welded switch reporting the...
  2. Replies
    30
    Views
    6,527

    Totally forgot about an automatic expansion...

    Totally forgot about an automatic expansion valve. I think his problem is solved!
  3. Replies
    30
    Views
    6,527

    I think you would be able to use the suction line...

    I think you would be able to use the suction line coming out of the box if you attach the temperature control sensing bulb to it in much the same way as one would an expansion valve bulb. You would...
  4. Replies
    30
    Views
    6,527

    Would it be possible to use a liquid line...

    Would it be possible to use a liquid line solenoid before the expansion valve with a temperature (or pressure)control in series with the coil?
  5. Replies
    29
    Views
    7,207

    It does not become virgin unless it is reclaimed...

    It does not become virgin unless it is reclaimed (as opposed to recovered or recycled), and it is not technically reclaimed unless it has been tested for and reaches a purity standard known as ARI...
  6. Replies
    8
    Views
    8,288

    Glad to help. Happy New Year!

    Glad to help. Happy New Year!
  7. Replies
    8
    Views
    8,288

    You will need something called a charging...

    You will need something called a charging cylinder (sometimes referred toas a dial a charge). It's a calibrated container that allows you to accurately weigh the charge in. And yes, you do add 2oz....
  8. Replies
    22
    Views
    36,799

    ditto

    ditto
  9. Replies
    11
    Views
    2,919

    A standing vacuum test is the last confirmation...

    A standing vacuum test is the last confirmation that your system is leak - free, but the ability to hold a vacuum does not guarantee your system is tight. It makes sense when you think of it this...
  10. When I read "compressor saver" I thought of those...

    When I read "compressor saver" I thought of those little square black time delays that were so easy to sell before the advent of digital stats.
  11. Replies
    39
    Views
    14,676

    On a very hot day, the utility company may be...

    On a very hot day, the utility company may be dropping supply voltage (although they will never admit it). I've seen as little as 196 volts feeding a 208 circuit. If you drop voltage, amperage must...
  12. Replies
    21
    Views
    2,748

    Did you get your EPA Certification through NYCT?

    Did you get your EPA Certification through NYCT?
  13. Replies
    11
    Views
    6,670

    Outdoor coil temperature is relevant because that...

    Outdoor coil temperature is relevant because that is how the heat removed from the conditioned area is released to ambient air.
  14. Replies
    26
    Views
    5,649

    I don't know your husband's age, but this is a...

    I don't know your husband's age, but this is a young man's work. Their is plenty of lifting, climbing, kneeling, and bodily contortion involved. After a number of years, the little nagging injuries...
  15. Replies
    32
    Views
    10,529

    The ability of the unit to hold a vacuum does not...

    The ability of the unit to hold a vacuum does not guarantee that the unit is tight. Consider that even under a perfect vacuum (30" hg, 0 psia) the greatest pressure differential between inside the...
  16. Replies
    9
    Views
    1,653

    Also used to prevent liquid migration to the...

    Also used to prevent liquid migration to the compressor in an off cycle.
  17. Replies
    6
    Views
    1,921

    Often use a heat gun but be careful; they can...

    Often use a heat gun but be careful; they can remove paint.
  18. It's also a real quick way to determine which of...

    It's also a real quick way to determine which of the unmarked breakers feeds it:whistle:
  19. Replies
    4
    Views
    3,168

    I agree Pro. But I actually held the check and...

    I agree Pro. But I actually held the check and felt it chattering.
  20. Replies
    4
    Views
    3,168

    Thanks Gas. It is a split with the compressor...

    Thanks Gas. It is a split with the compressor under the car body and the evap in the interior (passenger compartment) "attic". Also, it is a spring loaded check. Condensing temp was low, but I...
  21. Replies
    4
    Views
    3,168

    Discharge check valve chattering

    Greetings all. I have been asked for advice concerning an intermittent discharge check valve chatter on a subway car air conditioner. It is a Carrier Open Drive 10 ton R- 22 unit with a typical...
  22. Replies
    56
    Views
    12,316

    was a bit of an a hole...

    when I ws a kid. Sent to a no cool (resi) for my first call. Find no 24v to contactor, trace it back to stat. As I'm removing the cover, H/O proudly states that it's only a year old & he did it...
  23. Don't be so rough on yourself. We've all seen...

    Don't be so rough on yourself. We've all seen this and did exactly what you did even though the little voice was telling us it might let the smoke come out of the transformer
    :gah:
    :cheers:
  24. Replies
    4
    Views
    1,388

    It was marketed under a few names. Mine...

    It was marketed under a few names. Mine specifically by GE. It's about 25 years old; still my "OLD RELIABLE". I have never tried it on HFCs because there was no such thing as HFC refrigerant when...
  25. Replies
    33
    Views
    21,949

    Two points to consider: Even if you were to...

    Two points to consider:
    Even if you were to attain a 500 micron vacuum, that does not mean you are absolutely leak free. The greatest pressure differential between inside your system and the...
  26. Replies
    14
    Views
    4,287

    What are you going to pull a vacuum on? The...

    What are you going to pull a vacuum on? The system should already be charged and there is no field installed lineset.
  27. Solenoid closed most likely, but were the txv...

    Solenoid closed most likely, but were the txv strainers checked? If one clogs, they both will. Since the system is recovered, open the solenoid and remove the "guts" (diaphragm, plunger etc). Put...
  28. Replies
    23
    Views
    6,069

    If you experienced multple failures and they have...

    If you experienced multple failures and they have all been electrical, an acid condition likely exists. At the very least, an acid test should have been performed in order to prevent condemning the...
  29. Replies
    17
    Views
    4,770

    Dirty evaporator would also make it hard to open...

    Dirty evaporator would also make it hard to open a cover.
  30. Typically, the tanks are rated for 50 & 30...

    Typically, the tanks are rated for 50 & 30 pounds, so they can (legally) hold 40 & 24 pounds respectively.
  31. Replies
    32
    Views
    7,451

    Is the house very warm inside? Is there a panel...

    Is the house very warm inside? Is there a panel open on the air handler? At 80 psig on the low side, you would have a coil temp of close to 50 degrees.
    You specified that the a-coil is clean; how...
  32. Replies
    27
    Views
    23,421

    You can try switching legs of the compressor...

    You can try switching legs of the compressor (reversing the motor rotation). Sometimes, if you are persistent enough, this will free it. You can also try reversing the rotation and energizing the...
  33. Thread: EPA

    by jaypslugger
    Replies
    11
    Views
    3,481

    Try www.hvac-pro.org. They have a practice...

    Try www.hvac-pro.org.

    They have a practice Universal Exam. I refer my students to it. It's not absolutely great, but it gives you an idea what to expect. Good luck!
  34. Replies
    14
    Views
    3,770

    Excuse my rusty-ness. To my recollection, Ice -...

    Excuse my rusty-ness. To my recollection, Ice - o -matic machines go into harvest based on low pressure. At a cooler outdoor ambient, pressure would be lowered in a shorter amount of time, which...
  35. Replies
    18
    Views
    12,351

    If you tried tightening the packing nut without...

    If you tried tightening the packing nut without success, and you don't have or can't find the proper (graphite) o-ring, a piece of teflon "rope" wrapped around the stem, then tightened in place by...
  36. Replies
    44
    Views
    31,936

    I change it after every use, while the oil is...

    I change it after every use, while the oil is still warm. There was a reason for this, but I honestly don't remember what it is.
  37. Replies
    40
    Views
    7,848

    Are you sure it's a leak and not moisture in the...

    Are you sure it's a leak and not moisture in the system? Time is not an indicator of sufficient vacuum. After you reach 600 microns, isolate and turn the pump off, then watch the pressure rise. If...
  38. Have you checked the belt tension and/or pulley...

    Have you checked the belt tension and/or pulley adjustment?

    Also, if it is an air over motor, is it located in an area where the is poor air circulation?
  39. edit - Called Robinair. Tanks can be used,...

    edit -

    Called Robinair. Tanks can be used, but a risk of overfilling exists. It will be necessary to weigh theses tanks as they're being filled.
  40. Question about Robinair 17800B recovery machine

    My company just purchased 50 lb recovery tanks to use with the Robinair 17800B . The new tanks do not have a shraeder valve (in addition to the liquid and vapor valve connections) to attach a hose...
  41. Replies
    3
    Views
    1,104

    Thanks. This looks like the way to go. ...

    Thanks. This looks like the way to go. Hopefully one of the parts houses around here has them.:yes:
  42. Replies
    3
    Views
    1,104

    compressor terminals wasted

    Went on a call today and found compressor terminals on r & s fried away with just roundish posts left (no flat area for clip to connect to). I replaced the connectors on the end of the wires and re...
  43. Replies
    62
    Views
    9,635

    Was repairing a 10 ton unit for a subway car with...

    Was repairing a 10 ton unit for a subway car with an ignorant supervisor breathing down my neck. Told him the unit was going to need an Illudium K-234 Vacuum modulator. He wouldn't admit that he...
  44. Replies
    78
    Views
    20,825

    Are you sure the guy's even around? Maybe he had...

    Are you sure the guy's even around? Maybe he had some kind of extenuating circumstance (death in family, hospitalized etc...) and hasn't been able to respond to your calls. I know it's a longshot...
  45. Thread: Goodman

    by jaypslugger
    Replies
    74
    Views
    14,141

    I felt the same as most with regard to Goodman...

    I felt the same as most with regard to Goodman equipment until we lost the Condensing unit three days before closing on the house we just sold. I was looking for the cheapest possible replacement...
  46. Replies
    22
    Views
    4,062

    You know that oil goodman uses in its shipping...

    You know that oil goodman uses in its shipping pallette that smells like refrigerant oil? I refused to accept units 3 times before I realized that all goodmans ship with that oil. But I've been...
  47. Replies
    41
    Views
    6,287

    Did it always do this? If so, your service...

    Did it always do this? If so, your service capacity may be on the low side so that when the compressor reverses, the additional amp draw is taxing the panel. Does it happen all the time, or only...
  48. Re: Okay.

    Finally the voice of reason is heard above the din. This is the only response that was both correct and a reasonable solution what is going to be a common problem.
  49. Replies
    65
    Views
    157,732

    Did anyone perform an acid test on this unit? If...

    Did anyone perform an acid test on this unit? If acidity is not determined, then you are being misled by your technician. The pinholes are probably a result of environmental circumstances rather...
  50. Replies
    13
    Views
    13,545

    Very well "spoken". And absolutely correct.

    Very well "spoken". And absolutely correct.
Results 1 to 50 of 86