    alright...so i went back at the end of my day...

    alright...so i went back at the end of my day yesterday.
    removed thermostat wires, jumpered R&W
    system turns on, goes thru its safety check, calibration where inducer ramps up so both low & high...
  2. Replies
    12
    Views
    1,985

    a little bit of information when i went back. ...

    a little bit of information when i went back.

    I disconnected the 2-stage thermostat and flipped the dip switch for a single stage thermostat. Jumped R&W.

    hooked up a manometer to the "+" hose...
  3. Replies
    12
    Views
    1,985

    gas is ON, the hot water tank is working. i...

    gas is ON, the hot water tank is working. i tested 7-8"wc on the input side of the valve. i have 0"wc on the output side of the valve when energized. i inspected the orfices when i installed the 2nd...
  4. Replies
    12
    Views
    1,985

    great idea, I swung by between calls and tested...

    great idea, I swung by between calls and tested that. It did pull in for the full 4 sec.
  5. Replies
    12
    Views
    1,985

    Lennox SLP98UH - not firing

    SLP98UH135XV60D-07

    replaced pressure switch (checked venting, drain, hoses, ports)

    jumper R&W, furnace goes thru its safety check, pre-purge, ignitor glows for 20 seconds, gas valve gets...
  6. Replies
    31
    Views
    4,666

    Good luck mikey, don't get discouraged. Try...

    Good luck mikey, don't get discouraged. Try everything once. Ask questions if you get lost. I spent a few years with journeyman, but i never learned as much as i did till i was on my own. Now i'm the...
  7. When you stop caring about the homeowner, thats...

    When you stop caring about the homeowner, thats when people get hurt.
  8. The test is simple, there always areas of the...

    The test is simple, there always areas of the heat exchangers you can't visually inspect. I've used this method dozens of times and it always works. You always take the blower wheel out and set it to...
  9. He posted on here and said that the flame was...

    He posted on here and said that the flame was rolling under the burner and was dancing around. Doesn't that sound like a plugged lung in the heat exchanger, meybe carboned up?

    I haven't seen...
  10. Replies
    7
    Views
    2,678

    Well, my fathers company has just picked up the...

    Well, my fathers company has just picked up the Maytag line of furnaces/AC. We were all impressed with it and i'm excited to start working with it.

    Has anybody else worked with the Maytag line?...
  11. Replies
    5
    Views
    3,285

    I'll check into it, we are a large retrofit...

    I'll check into it, we are a large retrofit company so we are using old duct work, but we always upgrade the size of the return air. The only thing i could think of is customers putting furniture in...
  12. Replies
    5
    Views
    3,285

    Has anybody else been seeing alot of problems...

    Has anybody else been seeing alot of problems with the Carrier MVP blower motors? Were doing alot of warranty work just for the motor quitting. I had 2 more on Sunday, 2 in one day. We are up to...