Wow, what a rabbit hole that will be to dive into... you'll end up trying to convert the super-fast CAN network into something pokey for building controls, probably something like this CAN-BACnet...
Type: Posts; User: davem
Wow, what a rabbit hole that will be to dive into... you'll end up trying to convert the super-fast CAN network into something pokey for building controls, probably something like this CAN-BACnet...
And Wattstopper/Legrand very helpfully offered a migration path through a panel retrofit kit, but that was 10 years ago, so nobody sells it anymore.... oh well, time for a rip-and-replace retrofit.
My recent experience with their AX JACE offering showed only BACnet integrations - the field panels the JACE was talking to were BACnet-MS/TP, not the older CC Dataline stuff... I was hopeful that...
From the help file:
Number Of Points
The number of components which are resolved by the point query, and are being monitored.
Count
number of components used in evaluating the orOut and andOut...
I'll bet I know the answer already, but I thought I'd toss this out there to see what floats... I have a site with 12 Wattstopper LI panels, all connected with their legacy dataline cards to an...
Yes, I sure am - I'd recognize that controller anywhere. We purchased the first batch of them for our project when they were a Sysmik offering, but shortly after our initial deployment, Sysmik sold...
We used these about a dozen of these on a datacenter project in Virginia, and I LOVE them... like some offerings, they suffer from a mild form of bipolar disorder, with a Niagara side, and a Sedona...
Did you copy all the folders from the AX station to the N4 station? A migration won't necessarily grab everything in the file structure, and your programs are likely still sitting on the AX JACE in...
As those IO modules are not BACnet MS/TP devices, I believe that you will roach the network as soon as you connect the first IO module, and you won't be able to talk to anything.
Strange, my Software Center is showing only 4.10 and 4.13 as installable options... I never even grabbed 4.12 if/when it was available. Maybe try grabbing the newest version (if Software Center is...
Allow me to ask the dumb questions:
When you click on a single discovered new module, have you Winked it so you know which one to match it to? (Provided you have disconnected to terminals on the DOs...
Can you? I thought Supervisors (even laptops) could not be licensed to run any fieldbus drivers, and there's no IP router for PUP... it would be cool to be able to access a laptop's COM port from one...
You will need a copy of SoloPro, which AAM put into a USB-dongle-licensed arrangement several years ago. You will need to find a dealer willing to sell you an "end-user" version of the key (which...
861861
Just realized I should have included the manual, now that pdf's are allowed to be attached...
If you have the "Crest Modbus and BACnet Communication Instructions", chapter 7 "Unit Operation" describes how to set AV0 and AV1 for the various operating modes you may need (depending on what is...
I should have most of those for you (I've never heard of a GX3) - I received your email while on vacation, but now that I'm back, I'll dig up the old laptop that still has those manuals on it, and...
I have been doing research freezer monitoring (-80C) with ACI products - well suited to BAS systems, and they make low-temp freezer-specific sensors and matching transmitters, with NIST certs...
I haven't seen that document in over a decade, and while I'm usually pretty good at transferring everything from laptop to laptop over the years, this pdf is lost to the stream of time.
The...
The VykonPro>hvac>RollingAvg works well, with adjustable sample count and sample rate.
You can't delete the NiagaraNetwork points directly with the Program Service, but a point is essentially a slot of its parent. If you can configure the Program Service to display the parent(s) of the...
Ah - the original post asked about an option for the Distech input, so I thought you were working with the Distech software.
Since you are looking for a solution within AX, the generic solution is...
Unfortunately no... it's a screenshot of my Bitmoji version of myself... I wear a suit often enough in non-work situations to present myself that way, there's just less hair now... haven't used that...
In the definition of the point within Resources Configuration, the Programming Value fields (where you can, for instance, define its Units) has a Scale field. Set to .001, and the value should read...
You've got mail...
Striking out so far - the conversion happens in a proxy extension of a point that must be in a specific device type (Niagara device within a NiagaraNetwork, Bacnet device, etc. etc.)... can't seem to...
Looks like our replies crossed... I need this functionality in a generic Niagara point, not in a BACnet point or any other specific driver-created proxy point. I won't be using BACnet, since the...
I like the ability to generate a custom lookup table within an NRIO input, but is there an object or process that would allow a similar table to be constructed for use in a generic Niagara point? I...
I haven't touched any of the Solidyne stuff, so I don't know about its Sedona functionality. I imagine that it should work just fine with whatever Sedona tool you have at your disposal (Sedona...
1) We've had some of the earliest easyIO controllers (the 30p) in service for over 12 years, so their longevity doesn't seem to be an issue (the myriad electrical issues in this thread are news to me...
If this Veris device works like their other devices, if you can't change the DevID through the Niagara Delta-Device-ID function, you can always discover the device ID as a writable point, then set it...
In my experience with these LCD's, you do not connect to the LCD MMI with Workbench - it is not a controller with points that can be accessed. You configure an easyIO controller to serve points to...
When connecting to the easyIO controller that is serving up points to the LCD, you would use "admin" with a blank password.
When using the touchscreen of the LCD to log into it, the high level...
That's a new one on me - I've never seen flow used as a control variable for chiller staging, but there's all sorts of sequences out there...
I've had the most success in staging chillers based on...
Or you will simply get tired of the squishy sound, and resign yourself to your fate. Don't worry - it will only be a few more years before Niagara changes their platform again, then we can all start...
Thank you!! I'd reached out to one of the mods, who gave me a couple ideas to try, but once I saw this thread, I thought I'd jump in... many thanks for your patience in dealing with this!
I'm in the same boat - I see my profile used a now-defunct email address, but updating my email address still didn't help. So, I tried reapplying using the link, and after three tries (I'm...
Encouraging to hear there might be an alternate wiring method - according to what I saw in Kaiterra's literature, the standard Sensedge is powered through a connector on the outside bottom, but their...
It would have to be cheap - it's only expected to last 5-7 years... that would be a tough pill to swallow every few years for an installation of any quantity.
My biggest issue with this unit is the...
We've successfully used Senva current switches (which they claim are ideal for EMC's) on fan-powered VAV's with small ECM fan motors, but some certainly benefitted from a multiple wrap...
I realize the custom solution in this thread was baked out a few years ago, but this still sounds like a good application for the module at vykonPro>history>PeakTracker. Just feed it your totalized...
Open a browser to its default IP address (which you will likely change to put it on your network) and configure away - addressing, input/output types and ranges, BACnet device ID or Modbus ID, etc....
One recent "gotcha" on the Maxline driver - a service customer of mine had migrated their DX-9100 off of N2 (and put the logic into a new BACnet controller), but did not disable the DX-9100 on their...
+1 on the gc5 iSMA stuff - the iSMA-B-XX-X-IP modules configure without special software; universal inputs support 12 different types of thermistors/RTD's, 0-10V, 0-20mA (albeit with a resistor, but...
Or kitControl>Math>Reset.
There are several of us AAM gurus on this board that will have various vintages of documents available. A decent introduction to AAM and how their network works is available in the first couple...
For PCT routing to work, the BACnet/IP port must be enabled (can't tell you how many times I forget to do that when I don't otherwise have any BACnet/IP devices on my project), and set to use the...
You may likely have to put some sort of "periodic write" function in the proxy versions of your outputs to ensure that the Spyder sees a "fresh" command - there is a heartbeat setting within the...
Here's what I use to meet various trim-and-respond types of sequences (please pardon the zeroes, since this is from an offline copy of the logic) - depending on the type of setpoint (pressure,...
Perhaps some of those checkboxes that are available in the user's config? I don't know if disabling the Hx Workbench views would prevent visibility of some of the elements you are seeing, but it's...
Kodaro makes this driver in both N4 and AX versions - download the driver, put it on your JACE, and it will run fully-functional for 2 hours. Need it for longer? Pay for it, or reboot your JACE to...