If you look at the schedule object, navigate to the scheduled items in the navigation mode. Make sure that the occupied command which is I believe bd227 in the UNT controller is there. If so, then...
Type: Posts; User: Froz'ninWpg
If you look at the schedule object, navigate to the scheduled items in the navigation mode. Make sure that the occupied command which is I believe bd227 in the UNT controller is there. If so, then...
Just because you swapped the sensor does not mean the wiring is not bad from the controller to the sensor. If it works in commissioning mode and not in the jace you have a jace issue.
Silly question but did you ohm out the sensor from the wiring at the controller to confirm there are no issues with wiring. This line of controllers is pretty bullet proof to use. Next question, if...
Ended up changing out the PC with Win7-32 bit pro version. No more problems and never did find out what was causing this.
It must be selected as exp 4di4do, it is on the bottom of the selection drop down.
If you selected the xp as xp 4di 4do then you will also need an XT module. If you open up the module for this you will see a configuration for the module in which you need to set an N2 address. IF...
When you selected the second module how dud you select it? The first module would be selected as the xp 6a12ao and the second module must be selected as exp......
If not you are adding another...
Hello, I am working on a Metasys system with GGT graphics. The issue is one XP machine will not display the graphics, just a plain greay/white screen. If I restart Metasys I might get one GGT...
We have an issue that is similar, we lose connectivity to the device every few days as out IT dept does maintenance. A firewall reload for instance causes about a 5 minute outage to that device. I...
Are these on a managed network or are they on a private network? If they are managed check with IT to see if there is something being done with firewall maintenance or some other reload or testing...
Hi All, I am looking for info on this device part# R7425A1017. It is an old Honeywell SCR and cannot find literature online or by contacting Honeywell. It was connected to old H'well controls...
Yes it is.
I worked there for 8 years as a Systems Rep, DDC tech. It is a great place to learn and take it for what it is. JCI is a large multi-national company that looks out for its shareholders before...
In MSEA, you can use LCT/Interlock/Global etc. to write to an analogue input as long as it is not on a DX-9100 controller. There are a couple of ways to do it. The most simple is to put the input...
Hello, we have these two integrated together and under the ADX I can see the Pegasys Server and it's points. However, I cannot add extensions to the individual point in order to trend or alarm...
Hello, I have a customer with several sites with Reliable Mach-1 controls with at least one site with a Mach-Global controller. All devices have network enabled communications that he is able to...
Hi, we have over 350 of these in one of our buildings. We used Johnson VMA controllers, the N2 type, and left the pneumatics in place. We were able to control both the mixing of the hot and cold...
Try this out from Greystone,
http://greystoneenergy.com/webcura/files/247807_gt_ares_spec.pdf
JCI will sell to a building owner and this is part of the SCT tools which would include the database/offline programming tools for the MSEA, HVACpro, GX-9100 and of course the CCT Tools.
Looking to integrate the two systems on an LAN as we wish to see all of the devices on the Edwards Quick Start Panel.
Has anyone done this or have guidance other then using a fieldserver box?
...
Hi, if you do not have the DX key for the editing of paramaters in the DX you can use a small jumper or set of needle nose pliers. The "key" essentially jumps the top and bottom pins of the plug...
It must be brought in through an NAE and a Bacnet integration and the NAE will discover the points.
Hi Integrator, check to ensure that IT has not blocked anything. Is the ADS behind a firewall? We have had the same issues but found that IT had to make modifications to all ports for each PC being...
JCI is stopping production of all N2 devices from that era of controllers. They apparently are replacing them with an FEC that will communicate on the N2.
Role the dice on this one. The UNT is...
Is there any chance it got added into a schedule?
Then map the hours into a graphic or a user view. Right click on the hours and you should be able to reset from there.
If not, check to see if you have the rights to do this.
Is the runtime calculation being done in an FEC or through the totalization block in the BI?
Right click on the hours, select reset.
Hi all, we have many out buildings where we cannot get a fibre connection and will need a dedicated leased line (phone). I have a requirement to install FEC's to monitor equipment and need to get...
One other thing to check since this is being monitored via a head end device. Check to see if the AO for the cooling valve is under local control. Also, have a look to see if there is possibly some...
The sequence should be on the O&M manuals that were left onsite when JCI or the mechanical contractor left onsite.
You can always contact JCI for a copy of them, they are worth their weight in...
Depends on the sequence of operations, I noticed the OA-T is around the freezing mark which would typically have disabled cooling and enabled heating. This means that the only way to get the supply...
Just by looking at the screenshot it looks like the heating valve is passing. 51 off the coolnig coil and 61 or so off the heating coil. Looks like the issue is here.
If the output is not defined in the UNT is will not work.
You need to write the Supervisory Schedule to ADI78 which is the scheduled point in the VMA. If the occupancy button is pushed it will override the Occ Mode in the VMA.
Don't forget that this is...
Since you don't have avything left to lose with this device has you tried the reset button located on the panel?
This will reset the device back to factory defaults.
After that, using the steps...
Found the issue, when I replaced the controller I found that water had gotten into the cabinet and onto the back of the circuit board. The corrosion and damage to the board is what did it.
SCT is the offline database generation tool. It also is the only tool that can backup and restore databases.
If there is an ADX onsite I would hope that the SCT is loaded on it. You can check by...
If you have performed a backup of the database from SCT and saved at an earlier date of course you can. You restore the old database in SCT and find the missing graphic.
The issue with this being...
I had a UNT110-1 go offline from my NAE and when I went onsite to investigate I found out the UNT thinks it is a fume hood controller. I was able to communicate to it with HVACpro software Ver 8.08B...
The enable alarms in the UNT would have nothing to do with this issue. Can you command the point from the front end? Are you writing to the point at an appropriate level?
Not familiar enough with the FX-60 but with Metasys you need to define the analogue input as an analogue output with the address reflecting AI-6.
The other thing to do is to put the AI out of...
Also, try the last 4 digits of the company phone number.
Yes it is possible. You need the tools from the disk for NAE configuration tool, Update tool, the images as well as pretty much a complete SCT load on a machine.
The steps for flashing it are the...
Is the shutdown status on? Are the tuning paramaters in all of the loops properly defined, ie. prop bands and integrals?
If you like, send me the program email is in my profile and I am at my...
Silly question but is the fan status on? Are all of your input/outputs reading correctly? Is the fan system occupied? Does the system work if you plug into it with HVACPro from you computer and...
Yes it is.
Happy New Year.
You would use a sideloop for PI control with reset to BO Sequencer.
Athens, Greece? Loved it there and was hoping to go back for my upcoming wedding in June but due to the economic turmoil over there we are hesitating.
Do you have the Metasys.ini file setup to...
Check the uploaded doc.