The CR18 compressor pumps about 10,800 btuh @ +25 SST. The Bristol would pump about 14,400 btuh @ +25 SST.
Here's a formula (it'll get you close) that you can use when trying to determine the...
It's a solid core drier so that helped.
Add 15% to the rated capacity of the Unit Freezer for it's medium temp capacity.
4700 x 1.15 = 5405 btuh @+20 sst 10TD.
It looks like a Sporlan TXV so check/change the power head to a KT43SC.
...
To answer your question.
Find a Copeland:
M6GP-H064-CAA-177 115V
or a
M6GP-H064-CAA-272 115V
It's rated for R404A/R448A/R449A/R407C
(Note: change the TXV power head if using R404A)
All we're doing here is matching a unit cooler to a condensing unit. The optimum unit cooler for this Copeland unit is the Heatcraft 10,400 btuh unit. Heatcraft does make a 12,000 and 13,000 2 fan...
The FFAP-015Z pumps 11,500 btuhs at +25 SST at a 90 ambient, R404A. The optimal evap to use would be the Heatcraft ADT104 or LSC104. When you looked it up online you mistakenly chose the BTUH at a...
Sounds like you might have a pressurized crank.
Here's an old thread started by basser (Copeland Engineer) that might help.
https://hvac-talk.com/vbb/showthread.php?58023-Pressurized-Crankcase
As I stated, it's probably a Heatcraft or Russell evaporator. There will be a part number on the motor.
Similar to:
Heatcraft:253?????
Russell: 082?????
Your supply house will probably have...
That I know of, Koldpak does not make evaporators. It's probably a Heatcraft or Russell. You can purchase them cheaper at a local wholesaler who sells one of these brands.
What is the compressor number?
As you guys determine your BTUH's remember to adjust the freezer evaporator BTUH for a cooler application.
The Trenton evaporators TPLP422L are rated for 22,000 btuh at a -20 SST, 10TD. At a +20...
I like to keep the evaporator TD around 8.5 to 9 for a -10F box. Using a 7500 would put the TD around 6.9 which will get even lower at a higher ambient.
5170 BTUH @ -20 SST @ 90 AMB
7160 BTUH @ -10 SST @ 90 AMB
Optimum Unit Freezer would be the 6500
Double AA port Sporlan Valve
What is the condensing unit your using? Heatcraft and others use this compressor in several units increasing the btuh capacity by condenser size.
6500
Hey, it's not nice to question the Sporlan gurus!:beat:
Sporlan Bulletin 10-11
"For a complete explanation of when an
externally equalized valve should be used,
refer to “equalization method,” Bulletin
10-9. Valves supplied with an external...
This is not equipment for a walk in freezer, it's a cooler. It doesn't even have an insulted floor which a freezer normally has.
Whoever designed it used an electric defrost evaporator so it...
The CKSA-094AB Krack is an Air Defrost evaporator rated at 9400 BTUH 10F TD. It does not have defrost heaters. The amp draw for the two motors is 4.2. The KOH013H2A pumps 9300 BTUH @ +25 SST @ a 95...
Look on the name plate of the motor. Copeland usually shows their part number.
Example: 050-0264-01 or sometimes the 050- is not shown.
The model number of the condensing unit would be helpful.
The HDT0500M6CF and the HMA450BA are matched for about a 35F box.
The TD across the evaporator is .96 at a 95 ambient. That's about a 87% RH.
The electric defrost model would be a HME390BA which...
This is easy if the existing evaporator was matched properly to the condensing unit. We just need the model number of the evap.
The size you show looks to be a coil for a fractional HP unit, Copeland, Tecumseh or maybe a Danfoss. Why not pick an OEM condenser coil from one of these brands and use it. It might be a few...
All is good. Thanks!:)
Nope, it's all about BTUH requirements and picking a unit that matches those requirements at a given SST.
An extended medium temperature compressor has a SST (Evap Range) of -25F to +25F. So it can be used in freezer or cooler application. Of course the BTUH capacity will drop the lower the SST.
That's a 3/4 HP unit pumping about 7500 btuh's. It's undersized for an 8 x 10 x 7.6 cooler. The long pull down time, freezing up and needing defrosts is a result of an undersized unit.
There's no reason for a defrost timer on a cooler unless it's undersized or running temperatures around 32F. I design for a 16 hour run time which gives an 8 hour off cycle defrost. An 8 x 10 35F...
10,500 btuh @ +15F SST @ 110F CT
Since you experimenting, just pick a rating and go for it. If it doesn't work, change something.
The Boyard compressor you have is a rotary type. I cant find the performance charts on it.
The comparable Tecumseh model, RKA5518EX, will pump 6630 btuh @ -5F SST @ 110CT using R22.
We need the compressor number!
If you could post the compressor model, new evaporator model and the refrigerant I could determine the new evap TD the system is now maintaining. If it's too high then more moisture will be removed...
I've got a lot of old catalogs but I don't see that evap.
If the box is around an 8 x 8 x 8 size then we can assume the evap is around 8700 btuh as Techman stated.
Match it to a 1HP (9000 btuh)...
Someone called me about this exact equipment last week. If it was you give me a call back tomorrow and we'll discuss the application.
Hmmm..........add a TXV and it possible could work. Have you ever done this Bill?
Interesting thought. Are you thinking at the inlet to the evap?
It's a 2 fan, 4fpi, 7800 btuh @ 10 TD, air defrost; if my memory is correct.
Use:
L-3/4 R134a
L-1/2 R22
L-1 R404a
arnie,
It's very common to design reach in equipment at a 15 to 20 TD. That way we can get more btuh capacity when there are limits on the size of an evap that will fit the box.
Ice,
Actually I used the condensing unit capacity for a: F3AD-A151-CFV which uses the CR18 compressor and includes 5 F subcooling. I never use A/C ratings for commercial refrigeration.
You got it BBeerme, they don't approve squat.
http://www.hvacrinfo.com/cope_ae_bulletins/TAE1282.PDF
Here's a paragraph from Copelands AE bulletin.
http://www.hvacrinfo.com/cope_ae_bulletins/TAE1260.PDF
"There are different opinions in the industry on oil
sump temperatures. The viscosity of...
It's a 3 fan ceiling mounted reach in evap rated at 6100 btuh @10 TD.
Matched with a CR18KQ (R22) pumping 10800 btuh @ +20 SST @ 90 ambient it would be designed for a 38F box with a 17.7 TD.
The only difference between the "K2E" and the "K2" is the oil. The "K2E" has POE oil.
If the system has R12 then you will have oil return problems.
Check out this Tecumseh website. Andy wrote a great pipe sizing program
http://boxload.tecumseh.com
The "K" bodies are used in dental offices but have a slightly different model number (the fourth character is 4, KAT4) because the crankcase doesn't have a passageway to the head. (keeps the oil...
There's no problem with applying a coating to walk-in evaps. One can even order the evap from the factory with a coating, it just takes 3-4 weeks to get it. If you want to coat an evap in the field...
What's your question KHR?
You need to check the wrist pins. If you don't see any evidence of heat such as nasty burnt oil then the rod could have busted due to a liquid slug.
If you want to buy parts check out...