  1. After I posted this forum I was thinking about...

    After I posted this forum I was thinking about this and based on this check method it's simply saying this......

    The heat pump adds 110 degrees of heat to any outdoor ambient temp and transfers it...
  2. I don't really remember my return temp. I did...

    I don't really remember my return temp. I did check it and I believe I was getting 106 at return and 66 or so at the supply.
  3. "Hot Gas Method" for heat pump check/charging in the winter

    I read somewhere you could check heat pump charge (ballpark) by the following...

    Discharge line temp + OA (Outdoor Ambient) = 110 + OA (+- 5 degrees)

    I did a quick check on this and on a 54...
  4. Replies
    2
    Views
    281

    So I just contacted Goss to get more info. ...

    So I just contacted Goss to get more info.

    BA-3 = 1/4" to 1/2"
    BA-4 = 1/2" - 1"
    BA-5 = 1" - 1.5"

    BA-10a = .5 - 1" (The tech told me this torch swirls the flame and it has a stainless steel...
  5. Replies
    2
    Views
    281

    Goss v.s. Turbo (Tip sizes)

    I'm having confusion between tip sizes. I've been using mainly air acetylene brazing. Someone gave me a GOSS AA-1 with a BA-3 tip. It seems the tip is large enough to do the 7/8 liquid but it...
  6. What is the difference between a two stage and...

    What is the difference between a two stage and single stage pump?
  7. Replies
    11
    Views
    1,312

    Vacuum pump CFM, does it matter?

    I was talking to someone that the CFM really relates to how fast it pumps the system down. Most technicians choose higher CFM pumps so that it trims the time they are with each customer. I'm...
  8. I think I'm going to pass on it. I need a good...

    I think I'm going to pass on it. I need a good pump that I know works, not something I'm going to have to tinker with. The price looks tempting, but I"m going to let it pass.
  9. Replies
    0
    Views
    209

    Goss Air/Acetylene

    I just picked myself up an Acetylene "B" tank. It came with a Goss regulator and Goss AA-1 Handle (screw in type) and BA-3 Tip. I believe BA-3 is going to be too small for HVAC linesets. I was...
  10. Possible Broken Robinair Cooltech Vacuum Pump

    I saw this at a pawn shop around my area. The shop originally wanted 125, but we noticed the oil was overfilled and when we drained and turned the unit on it only pulled down 640 microns on my...
  11. Replies
    13
    Views
    1,653

    I do know about the "thermal paste" situation. I...

    I do know about the "thermal paste" situation. I remember many technicians using wet rags for heat controll. Is there a chart or guidelines regarding tips and pipe diameters? Are tips...
  12. Replies
    13
    Views
    1,653

    Thanks, What is the difference between the B...

    Thanks,

    What is the difference between the B tank and MC tank? Also I do see a lot of videos of people brazing with just straight acetylene. What type of tips do beginners typically get? What's...
  13. Replies
    13
    Views
    1,653

    Begenners Brazing kit

    Just want to get some opnions on what type of brazing set is good and types of gasses.

    I see some people use just straight acetylene v.s. oxy-acetylene. I was reading that it's better because...
  14. Replies
    7
    Views
    847

    Assuming the leak is in the coil, the tech was...

    Assuming the leak is in the coil, the tech was indicating they have to order the coil from trane, and they may not have it. He was indicated it would be better to replace the whole system (quoted me...
  15. Replies
    7
    Views
    847

    The air handler is a Trane that is from 2005, but...

    The air handler is a Trane that is from 2005, but the outside heat pump and coil is from 1998. I couldn't get a model number from the coil. The outdoor heatpump is a XE 1000 3.5 ton. Yes the rust...
  16. Replies
    7
    Views
    847

    System Leak

    So I turned my A/C on (for the first time). I was getting coil freezing (evap). I knew because when I took the cover off from the unit the entire coil was a block of ice. I defrosted it and...
  17. Replies
    5
    Views
    1,038

    I identified the high/low side. The service...

    I identified the high/low side. The service ports are there. I opened up the high and I can see the needle right in front. But on the low (either the needle is not there or it's too deep. I can't...
  18. Replies
    5
    Views
    1,038

    Can't find Schrader valve stem

    I have a set of gauges. I went to take the cover off my condenser unit and put the high side on. My gauge registered. I took the cap off the low side and didn't see any Schrader valve stem. I put...
  19. What type of Thermometers do you guys use when doing superheat calc.

    You know when you are taking the temp of the suction line and indoor/outdoor dry bulb temp. Are non-contact therm ok? I was looking at these.
    ...
  20. That's good to know. The furnace is a different...

    That's good to know. The furnace is a different matter.

    It's a Lennox G12. It was made in 75. Everytime I get someone to come to my house they want to replace it with a furnace that matches up...
  21. Thanks this is very informative. Why would the...

    Thanks this is very informative.

    Why would the evap coil be .5 tons oversized. Is this normal?
  22. What is the tonnage and Sheer for a Lennox HS26-261-1P condenser unit?

    I believe the unit its about 5 years old or so. The model is HS26-261-1P. The evaporator coil is C22-31-TXV-2. I believe they were both replaced at the same time.
  23. Replies
    9
    Views
    798

    So what is the correct method.

    So what is the correct method.
  24. Replies
    9
    Views
    798

    Picking the right CFM for your A/C

    I had a contractor come to the house. I have an old house built in 1974. The ductwork is not the top design. It's a small house roughly 1400 sq ft. One of the major problem is the upstairs is not...
  25. Is it possible to calculate the CFM of a blower motor?

    I have a old furnace. The blower motor had been changed. I can see the RPM of the motor but I also think it depends on the size and diameter of the cage portion. Is there a formula for caluclating...
  26. So what your saying if I went and put in a system...

    So what your saying if I went and put in a system according to the "Bonnet Capacity" (i.e. 65600BTU Output system) it would be oversized. The people that have came into my house for estimates are...
  27. Why does my old 1975 Lennox G12D2 that I'm about to replace show a AFUE of 80%??????

    It'a a 1975 Lennox G12D2. It's really old and I'm getting it replaced. The unit shows an input BTU of 82K and an output BTU or named "bonnet capacity" of 65600. This makes not sense. I believe...
  28. If a home a/c system is missing 1 - 3 ounces of refridgerant is this noticable?

    I have a 1,200 sqft home. I have a Lennox system. I'm not sure of the ton but the furnace is 65K BTU and it's a r-22 system. It's not cooling that well that is the system is taking a very long...
  29. Not every homeowner fits that budget you just...

    Not every homeowner fits that budget you just stated. I don't pay for bottled water. I don't have cable TV. My company pays for my Cel phone. I don't drive a $30,000 car nor do I have a dog. I'm...
  30. No one started talking about human value until...

    No one started talking about human value until you. What make you think Iím an Engineer are you assuming. I never said I was I simply gave an instance if someone was one. In all fields the person...
  31. So this experience represents all situations. Is...

    So this experience represents all situations. Is that what you are implying. An Engineer takes several years of FORMAL schooling particularly at a major college and/or university. If you've ever...
  32. This seems like a better answer rather then...

    This seems like a better answer rather then attacking my spelling or stating one experience to represent all experiences.
  33. Well let's take it this way. What would happen...

    Well let's take it this way. What would happen if a company or companies started to make HVAC systems that can be fully serviced by the homeowner. Considering you need a license to purchase...
  34. Why don't HVAC people like DIY homeowners?

    I understand the amount of lisensing that is required and training to understand and fully repair an HVAC system. But one thing I notice is that a lot of HVAC people (not including those here) don't...
  35. Replies
    9
    Views
    732

    What is considered a reasonable setpoint. ...

    What is considered a reasonable setpoint. Considering if it's 90 or so outside we keep our system on 80. If we set it lower it will take a while longer to cool. But what is a typical cycle lenth...
  36. Replies
    9
    Views
    732

    Is system working properly

    What are some simple things a homeowner can look at with their A/C system this summer to determine if it has the appropriate charge and working properly.

    Ex:

    1. Pipes that run from condensor...
  37. Is it normal to have a supply line run through a return (wall cavity)

    I was taking off my return register and notice the supply line that runs upstairs from the basement runs through the return to get there. This is is how the system had been set up since the house...
  38. Replies
    1
    Views
    478

    Dampening Return registers

    Essentially this is the thing. I have a return register upstairs on the 1st floor and one on the second. The one on the 1st floor has great suction. So much that I can put a plastic storage box...
  39. Replies
    6
    Views
    1,396

    Thanks guys I looked carefully today when I...

    Thanks guys

    I looked carefully today when I went home. I noticed there is in fact a seperate wall cavity shaft that runs from the return to the 2nd floor. It appears though sheet metal wasen't...
  40. Replies
    6
    Views
    1,396

    The house was built in 74. The Condenser unit is...

    The house was built in 74. The Condenser unit is a Lennox made in 93. When it was installed a new evaporator coil was changed as well. However, the air handler and furnace (all as one unit) is the...
  41. Replies
    6
    Views
    1,396

    Warmer Upstairs then downstairs

    I was told by several people this is normal. However I want to do something about it so at least it's better upstairs. I was analyzing my ducting in my house. It's essentially a 1,200 sq ft home. It...
  42. Replies
    8
    Views
    1,010

    What would happen if the system that is choosen...

    What would happen if the system that is choosen has a higher BTU then what the house needs. Lets say it's like 5 to 6K higher BTU then what is needed. People say you will waist electricity. But if...
  43. Replies
    8
    Views
    1,010

    Calculating BTUs for furnace upgrade

    I have a 1,296 SF home built in 1974. The home contains the original gas furnace with standing pilot with output capacity of 65,600 BTU. I had some people come down to my house on getting a price...
  44. Replies
    4
    Views
    958

    Ok here is the deal I recently moved in a...

    Ok here is the deal

    I recently moved in a house build in 74. The furnace is gas and there is an outdoor condensor for AC. The AC has been upgraded including the replacement of the condensor coil,...
Results 1 to 44 of 44
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event