    I would say the circuit has been short cycling.

    I would say the circuit has been short cycling.
  2. . Then you will need to pull the refrigerant and...

    .
    Then you will need to pull the refrigerant and pressure test.
    Measuring your subcool would have indicated low refrigerant.

    Gibbo
  3. It's the software locking the capacity from...

    It's the software locking the capacity from increasing it will reduce the capacity to raise the SST but if still a problem shuts down circuit.

    Gibbo
  4. The compressor won't load up as its see low...

    The compressor won't load up as its see low saturated suction temperature so compressor unloads and will stop.
    You either have a low refrigerant problem or EXV isn't opening properly but most likely...
  5. Replies
    4
    Views
    1,299

    You haven't mentioned any alarms so am assuming...

    You haven't mentioned any alarms so am assuming there are none. What is the control mode you are trying to run the chiller. If the control is saying on any mode such as
    Local On, BMS Rem, or CNN...
  6. Replies
    3
    Views
    1,153

    Heater is energised when circuit compressors are...

    Heater is energised when circuit compressors are off and standing Saturated Discharge temp goes nelow 17c it will go go off at 25c or when compressor starts.
    Heaters can be tested through quick...
  7. Replies
    10
    Views
    1,556

    The compressor protection relay has all the...

    The compressor protection relay has all the compressor safeties and monitors the crankcase heater current.
    Wouldn't think 1 fan down would trip the HP switch
  8. Replies
    10
    Views
    1,556

    Apologies . That should be T117 not T152. B...

    Apologies . That should be T117 not T152. B circuit low cooler suction temperature.
  9. Replies
    10
    Views
    1,556

    T051 is A lead compressor trip no feedback from...

    T051 is A lead compressor trip no feedback from protection relay most likely a crankcase heater failure.
    T152 B circuit is low suction cooler temperature most likely short of refrigerant.
    A152 is...
  10. Pretty sure there are various sites around the US...

    Pretty sure there are various sites around the US from Manhatton harbour to some of the large Tech company sites like Facebook and Google out west that use cool water from the depths.
  11. Is the 52F annually .

    Is the 52F annually .
  12. The coloured HSIO along with a new PSIO and...

    The coloured HSIO along with
    a new PSIO and Software upgrade for it all to work.
    Gibbo
  13. Replies
    18
    Views
    2,975

    There are 3 versions Phase 2 and 3 are the Pro...

    There are 3 versions Phase 2 and 3 are the Pro Dialog versions.
  14. Replies
    18
    Views
    2,975

    go to Carrier site eto.carrier.com/lit.asp

    go to Carrier site
    eto.carrier.com/lit.asp
  15. Replies
    30
    Views
    8,929

    Every manufacturer of these types of coils have...

    Every manufacturer of these types of coils have had issues with leaking coils some down to the manufacturer process and some by not following the maintenance manual regarding cleaning and washing...
  16. Replies
    30
    Views
    8,929

    The highest e coat for coastal and industrial...

    The highest e coat for coastal and industrial areas personally i would order e coated no matter where they are.
    Google Novation coils they do a nice book on the various coatings and areas for them...
  17. Replies
    13
    Views
    2,183

    pretty sure the retrofit kit for CT's etc will...

    pretty sure the retrofit kit for CT's etc will require new compressor protection boards which in turn will need software downloads done by Carrier Service.
    Your problem could be software related as...
  18. Replies
    17
    Views
    11,059

    The user access password which you have will...

    The user access password which you have will still work in user config only, its only the access to service and factory configs that is restricted and requires Carrier approved access via their...
  19. Replies
    15
    Views
    34,094

    The 3 digit passwords are on French made Carrier...

    The 3 digit passwords are on French made Carrier chillers.
  20. Replies
    15
    Views
    34,094

    If the password 2222 works then 3333 should work...

    If the password 2222 works then 3333 should work if not its been changed.
  21. Replies
    15
    Views
    34,094

    You would need to contact Carrier for the QR code...

    You would need to contact Carrier for the QR code which only lasts a few days then locks you out.
    The basic password should still work.
  22. Replies
    3
    Views
    1,503

    Sounds like the screen has frozen try powering it...

    Sounds like the screen has frozen try powering it off then back on.
    Gibbo
  23. Replies
    3
    Views
    1,349

    You will need to contact Carrier Service who will...

    You will need to contact Carrier Service who will send a technician to download the software and configure. Due to the age of the chiller there may be other issues need addressing.
    Gibbo
  24. Replies
    18
    Views
    2,975

    The Pro Dialog chiller 30GX / HXC is made in...

    The Pro Dialog chiller 30GX / HXC is made in France but sold throughout Africa, Europe, Middle East, Far East, Australia and New Zealand.so if its in India then most likely its French made chiller....
  25. Replies
    18
    Views
    2,975

    Depends on what info he wants the fundementals...

    Depends on what info he wants the fundementals are all the same. He hasn't mentioned where he is
    Gibbo
  26. Replies
    18
    Views
    2,975

    Google Carrier 30GX User Guide you will find this...

    Google Carrier 30GX User Guide you will find this is for French made chillers. As previously mentioned normally only issued to Carrier Techs. This is for a phase 2 Pro Dialog version there are 3...
  27. Thread: Carrier EEV

    by Gibbo
    Replies
    17
    Views
    3,864

    Yes 30 series

    Yes 30 series
  28. Thread: Carrier EEV

    by Gibbo
    Replies
    17
    Views
    3,864

    Exv board powers the valve and yes it powers open...

    Exv board powers the valve and yes it powers open and close.
    What is the problem ?
    Gibbo
  29. Its the old electro mechanical controls. Think...

    Its the old electro mechanical controls.
    Think all of the wiring diagrams are for the flotronic controls.
    Being obsolete it will be hard to find a wiring diagram you could try the Montluel factory...
  30. Looking at your photograph its not a Flotronic...

    Looking at your photograph its not a Flotronic chiller but one of the earlier chillers.
  31. Go to Carrier website for Montluel products....

    Go to Carrier website for Montluel products.
    www.eto.carrier.com/lit.asp
    then scroll through products only it will open with all manuals and wiring diagrams most of which were Flotronic controls....
  32. Replies
    30
    Views
    8,929

    Depending on the location I would opt for the...

    Depending on the location I would opt for the highest coating possible. Have seen far too often where the location was not taken into consideration when deciding whether it was urban or marine add to...
  33. Replies
    5
    Views
    2,111

    Trying to pump down a microchannel circuit will...

    Trying to pump down a microchannel circuit will cause it to trip on HP.
    Gibbo
  34. Replies
    4
    Views
    2,286

    It maybe due to oil in the cooler causing the low...

    It maybe due to oil in the cooler causing the low discharge superheat which then forces the EXV to close.
    This is normally associated with low load short cycling it can also be due to refrigerant...
  35. Replies
    9
    Views
    3,614

    Yes you can try to open the EXV, where was the...

    Yes you can try to open the EXV, where was the chiller made there are several versions of the XA chiller made in France and the US all with different style controls.
  36. Replies
    9
    Views
    3,614

    Your HP problem is being caused by EXV not...

    Your HP problem is being caused by EXV not opening correctly. Micro channel coil chillers can't do pump down hence your high pressure. Check your EXV board and EXV. Most likely the board.
    Gibbo
  37. Replies
    15
    Views
    2,615

    In fact some of the pinhole leaks after a coil...

    In fact some of the pinhole leaks after a coil clean using coil cleaner would be so small and hard to pick up even using nitrogen.
    Here in the UK we would use a Tracer -Gas mixture 5% Hydrogen / 95%...
  38. Replies
    15
    Views
    2,615

    You should never ever use any coil cleaner on...

    You should never ever use any coil cleaner on micro channel coils otherwise they will all start to leak. Water only
    Gibbo
  39. Your chiller has alarmed and will shut it down to...

    Your chiller has alarmed and will shut it down to Local Off.
    Check in alarm history for recent alarms.
    Gibbo
  40. Replies
    17
    Views
    11,059

    The information I have is Network Service Tool...

    The information I have is Network Service Tool and Comfort View can be used. But any software downloads is done via Carrier ProView service tool which is a new program and you would need to register...
  41. Replies
    17
    Views
    11,059

    You need to connect your service tool to the...

    You need to connect your service tool to the touch pilot middle 3 pin socket underneath , the plug you remove you will need to connect to the same plug via a cable with a female 3 pin plug.
    All...
  42. Replies
    11
    Views
    14,551

    oil_sp1 is while running oil_sp2 = 15 secs...

    oil_sp1 is while running
    oil_sp2 = 15 secs after start is mainly used for low ambients below 2c
    oil_sp2 = 45 secs after start would be the normal oil pressure trip point on start up.
    Oil...
  43. Replies
    11
    Views
    14,551

    You need to look at oil pressure on start up. You...

    You need to look at oil pressure on start up. You mention sometimes it alarms late in the day so the alarm history shows different times of the day.
    Oil Pressure Alarm Trip conditions see below
    ...
  44. Thread: 30hxc

    by Gibbo
    Replies
    11
    Views
    2,654

    As mentioned previously the O ring can be...

    As mentioned previously the O ring can be replaced by sliding the motor casing back. Of course it begs the question what the condition of the other O rings on the compressor might be. But from...
  45. Did you press "Save" after each "Attach" can't...

    Did you press "Save" after each "Attach" can't think of any other reason at the minute why it didn't retain the settings will have a think over the weekend and get back to you before Monday.
    Gibbo
  46. Brett No problem glad it all worked out ok....

    Brett
    No problem glad it all worked out ok.
    Gibbo
  47. Brett Same procedure as you did for fans but now...

    Brett
    Same procedure as you did for fans but now set_drive =3 for variable pump. Remember to switch off fan vsd's while attaching pump vsd.
    Glad to help.

    Gibbo
  48. Apologies I was looking at a 30 RB, Look in ...

    Apologies I was looking at a 30 RB,
    Look in Maintenance / DRV_CTRL menu you will see the "attach" at the bottom. It's either set_drv = 1 for A or 2 for B
    All drives should be switched off except...
  49. Depends on number of circuits if only 1 circuit...

    Depends on number of circuits if only 1 circuit or 2 circuits if 2 then you will need to attach the drive to the correct circuit you should find this in service configuration. Your software is ok so...
  50. Think it's only the Danfoss VSD that requires the...

    Think it's only the Danfoss VSD that requires the attaching procedure.
    Schneider is just plug and play. Just verify the config is similar.

    Gibbo