    ISM parameters need to be configured and can be...

    ISM parameters need to be configured and can be done through ICVC. Time to find the manual.
  2. Thread: Connection Trane

    by nyrb
    Replies
    5
    Views
    8,287

    RTAC uses older Adaptaview screen and uses BCI2-C...

    RTAC uses older Adaptaview screen and uses BCI2-C interface, RTAF uses UC800 and has a different bacnet interface. At least that’s my understanding.
  3. Thread: Connection Trane

    by nyrb
    Replies
    5
    Views
    8,287

    Bacnet card to BAS. ...

    Bacnet card to BAS.

    https://www.trane.com/Resources/Partners/1ce8996a-a162-4101-b862-09bda7d80984/documents/RF-SVN02C-GB_0820.pdf

    This is the older version, a newer card is available now but...
  4. Replies
    6
    Views
    10,484

    15 PSI Suction is 15 degree saturated evaporator...

    15 PSI Suction is 15 degree saturated evaporator temperature, 44 degree leaving water minus 15 degree SST means you have 29 degrees of approach. 1st thing that comes to mind is fouled tubes.
  5. Replies
    2
    Views
    3,825

    That Sporlan / Trane EXV is obsolete I believe,...

    That Sporlan / Trane EXV is obsolete I believe, if it's just the plug that has melted you could wire it direct for the time being.
  6. When ordering the new MBB you should have...

    When ordering the new MBB you should have communicated the software version you had in order for RCD to send it out pre-programmed.
  7. Thread: CGAM Chiller

    by nyrb
    Replies
    6
    Views
    4,605

    The last time I had that issue the EXV was not...

    The last time I had that issue the EXV was not responding properly to command, I believe my 4 pin connection on top of the valve was not making proper contact.
  8. Replies
    21
    Views
    15,840

    Those fuses are fast blow, my coworker had very...

    Those fuses are fast blow, my coworker had very similar issues on the same chiller, power issues were the cause. Single phasing, brownouts and when the generator runs were noted to cause inexplicable...
  9. Replies
    6
    Views
    2,218

    Google is your best friend. ...

    Google is your best friend.

    http://img.ebmpapst.com/products/manuals/S3G500AE3301-BA-ENG.pdf
  10. Replies
    6
    Views
    2,218

    Likely the condenser fan motor is an ECM motor...

    Likely the condenser fan motor is an ECM motor that receives an enable signal as well as an analog input for speed control. ECM motors usually have nothing other than fuses on the power feed.
  11. Replies
    3
    Views
    1,323

    I don’t believe PCO5 controllers are backwards...

    I don’t believe PCO5 controllers are backwards compatible, I think all the controllers need to be replaced with PCO5’s.
  12. Replies
    2
    Views
    403

    Assuming the charge will fit in the condenser and...

    Assuming the charge will fit in the condenser and your valves hold… you should be able to utilize the pump down option with the liquid line closed then recover remaining refrigerant. Is there a...
  13. Thread: 23xl transducers

    by nyrb
    Replies
    2
    Views
    322

    Page 63. ...

    Page 63.

    https://www.carrier.co.th/m/23xl-3ss.pdf
  14. Replies
    3
    Views
    1,587

    More than likely a dead spot in your guide vane...

    More than likely a dead spot in your guide vane feedback potentiometer.
  15. Thread: PEH063 Oil loss

    by nyrb
    Replies
    13
    Views
    1,513

    The one and only time I ever lost oil that fast...

    The one and only time I ever lost oil that fast was due to a failed low speed motor seal allowing oil to blow into motor cavity. Evidence was seen at motor cooling drain line schraeder valve. Usually...
  16. Replies
    12
    Views
    2,046

    Leaks are definitely more difficult to find but...

    Leaks are definitely more difficult to find but the purge system gives plenty of information based on pump out time to determine if a potential leak even exists. Typically leaks on low pressure...
  17. Thread: YLAA

    by nyrb
    Replies
    9
    Views
    1,265

    Water or Glycol?

    Water or Glycol?
  18. Replies
    12
    Views
    1,060

    Have you verified your pressure transducers are...

    Have you verified your pressure transducers are accurate?
  19. Replies
    10
    Views
    860

    I have a few McQuays that run 24/7/365 for the...

    I have a few McQuays that run 24/7/365 for the most part also in cold climate. When crap happens which it always does, the tower bypass valve is usually a big help. The biggest issue I have with...
  20. Replies
    4
    Views
    1,423

    Sounds like your TXV bulb lost its charge to me.

    Sounds like your TXV bulb lost its charge to me.
  21. Replies
    11
    Views
    2,798

    I went to that link initially and this was my...

    I went to that link initially and this was my view. Do you actually get the manual?
  22. Replies
    11
    Views
    2,798

    I found this in my files, unfortunately it’s part...

    I found this in my files, unfortunately it’s part of a massive file that is too large to share, hope this helps.
  23. Replies
    13
    Views
    1,759

    It primarily comes down to maintaining a positive...

    It primarily comes down to maintaining a positive pressure at the highest point in a building’s piping to expel air and prevent a vacuum condition drawing air into the system. Every 2.3 feet of...
  24. Replies
    23
    Views
    18,729

    The link below may help you with understanding...

    The link below may help you with understanding the operation of the pilot and main TXV operation. I myself am leaning towards your main valve sticking intermittently. They used to rebuild or replace...
  25. Thread: GPM

    by nyrb
    Replies
    7
    Views
    1,467

    To get 900 tons of cooling you would have to...

    To get 900 tons of cooling you would have to reject at least 1125 tons of heat (probably more) with an 18 F temperature rise. Your current temperature rise of 4F at 900 GPM equates to 150 tons of...
  26. Thread: GPM

    by nyrb
    Replies
    7
    Views
    1,467

    18 degree temperature rise at 900GPM equates to...

    18 degree temperature rise at 900GPM equates to 675 Tons of heat rejection, this would only get you 540 tons of cooling based on a 1.25 heat rejection factor on the chilled side. The numbers you gave...
  27. Replies
    3
    Views
    2,086

    https://cgproducts.johnsoncontrols.com/yorkdoc/160...

    https://cgproducts.johnsoncontrols.com/yorkdoc/160.75-rp1.pdf

    Hope this helps.
  28. Replies
    8
    Views
    3,216

    Explain the pLan failure a little more. Is this...

    Explain the pLan failure a little more. Is this an error message generated by windows on the touchscreen during boot up?
  29. Thread: RTAC 275, 2014

    by nyrb
    Replies
    3
    Views
    1,830

    Seems like we’ve been here before......

    Seems like we’ve been here before...
    https://hvac-talk.com/vbb/showthread.php?2218250-Trane-RTAC-275-will-not-start
  30. Replies
    22
    Views
    3,731

    Call a refrigeration mechanic!!

    Call a refrigeration mechanic!!
  31. Replies
    22
    Views
    3,731

    Faulty cable or a faulty component, you have to...

    Faulty cable or a faulty component, you have to figure that part out yourself.
  32. Replies
    22
    Views
    3,731

    Divide and conquer is the best answer I can give...

    Divide and conquer is the best answer I can give you!! Obviously something is faulty on that string of components.
  33. Replies
    22
    Views
    3,731

    Disconnect 4 wire cable leaving panel to all...

    Disconnect 4 wire cable leaving panel to all field sensors / devices. See if panel mounted LLID’s are talking then. One bad cable or sensor can mess up everything. Familiarity is key and...
  34. Replies
    22
    Views
    3,731

    https://hvac-talk.com/vbb/showthread.php?1157541-R...

    https://hvac-talk.com/vbb/showthread.php?1157541-RTAC-excessive-comm-loss

    If you know how to use Techview, now would be the time. If not time to call someone familiar the system. Link above is for...
  35. Replies
    22
    Views
    3,731

    What is the exact message that comes up? If the...

    What is the exact message that comes up? If the entering / leaving sensors are reading wrong it can give an alarm that points You towards flow but can actually be the sensors. With just the pump...
  36. Replies
    11
    Views
    2,971

    I don’t have anything to help but this guys an...

    I don’t have anything to help but this guys an expert LOL!!!
  37. Replies
    1
    Views
    853

    Saturated refrigerant temperature - Leaving water...

    Saturated refrigerant temperature - Leaving water temperature = approach
    Liquid line temperature provides you with subcooled refrigerant temperature below saturation.
    To measure you need an...
  38. Replies
    10
    Views
    3,204

    Assuming this is the Multistack chiller from your...

    Assuming this is the Multistack chiller from your other post.... the E-stop should be a digital input to the chiller control system which should disable all running compressors immediately. The...
  39. Replies
    7
    Views
    6,435

    http://www.pretempco.com/html/products.html...

    http://www.pretempco.com/html/products.html
    These are what York uses from factory. Just have to know what DP is supposed to be. I usually install 20 or 40 paid as replacements.
  40. Replies
    12
    Views
    6,020

    Unless you’re the only one that ever touched it...

    Unless you’re the only one that ever touched it and know otherwise, I would wonder if someone else has recovered the charge into a used cylinder that had some oil in it and unintentionally...
  41. Replies
    9
    Views
    1,721

    Being a new chiller you should have all design...

    Being a new chiller you should have all design information readily available from the manufacturer. Most chillers today are designed for very low approach temperatures of 0.5 to 1.0 C but there are...
  42. Replies
    9
    Views
    1,721

    I think what you need to know is what “Approach”...

    I think what you need to know is what “Approach” means. It is the difference between leaving water temperature and saturated refrigerant temperature. 6.7C - 5.5C =1.2C. This is a common measurement...
  43. Replies
    42
    Views
    13,647

    The equalizing pipe in my picture was an after...

    The equalizing pipe in my picture was an after thought installed the 1st summer of operation after issues arose with flooding basins. Then nobody thought about winter operation until it froze 3 years...
  44. Replies
    42
    Views
    13,647

    Balancing flow is my 1st concern. Secondly if the...

    Balancing flow is my 1st concern. Secondly if the equalizing line is physically below the towers as shown I expect it will eventually become a huge pocket for debris to collect and difficult to clear...
  45. Thread: part numbers

    by nyrb
    Replies
    10
    Views
    1,620

    Google is your best friend.

    Google is your best friend.
  46. Replies
    1
    Views
    2,685

    Hope this helps.

    Hope this helps.
  47. Replies
    4
    Views
    2,024

    Some Customers Make Me Laugh

    What some customers are willing to do kills me. We told them at time of installation to add a Dry Cooler for winter operation. They said nope, -17F the last couple nights might have convinced them...
  48. Replies
    4
    Views
    1,482

    A pilot operated solenoid valve utilizes water...

    A pilot operated solenoid valve utilizes water pressure to open the main port of the valve, chances are if it used to work and no longer does the valve is gummed up internally.

    In regards to a...
  49. Thread: CW valve ID tag

    by nyrb
    Replies
    2
    Views
    1,071

    https://estore.industrialcontrolsonline.com/Custom...

    https://estore.industrialcontrolsonline.com/Customer/incodi/specpages/valves.pdf
  50. Replies
    9
    Views
    5,049

    Unfortunately RichardL is no longer amongst us...

    Unfortunately RichardL is no longer amongst us I’m sorry to say, his insightful responses are greatly missed by many of us here on this forum.