Search:

Type: Posts; User: thepresence

Search: Search took 0.01 seconds.

  1. Replies
    7
    Views
    837

    The iHarmony zoning control board is controlling...

    The iHarmony zoning control board is controlling all the equipment. Supply air target temperature is a set point in the parameters for the zoning control. It compares the value from the supply air...
  2. Replies
    7
    Views
    837

    Yes, I figured out it was cycling the heat to...

    Yes, I figured out it was cycling the heat to keep the supply air target temperature.
  3. Unfortunately yes. We have about 15 Excel classic...

    Unfortunately yes. We have about 15 Excel classic controllers still running here. It makes my job as an HVAC tech difficult because no one here can understand the programming notes. Thanks for your...
  4. Trying to understand Honeywell Excel Classic Programming Notes

    Referring to the attached .pdf, can anyone understand this? This is programming information from a Honeywell Excel classic controller. I believe all the sequence of operation information in...
  5. Thanks everyone for your replies. I will...

    Thanks everyone for your replies. I will defiantly checked the amp draw when i open up the valves to see how it runs. The design drawings are probably here somewhere, it will take me some time to...
  6. Picture

    Here's a picture of 1. This one happens to be a glycol heat reclaim system.
  7. Circulation Pump outlet valves throttled?

    I work in a large long term care facility and I've noticed on a lot of our closed loop glycol/water heating and cooling systems, the hand valves are throttled back to various positions on the outlet...
  8. Replies
    11
    Views
    3,759

    You've probably got a short or the wire is...

    You've probably got a short or the wire is grounded on your electric heat control circuit. Ohm the wiring out to find the problem.
  9. Replies
    6
    Views
    2,069

    Sorry for the confusion and thanks for your...

    Sorry for the confusion and thanks for your patience. My email has been updated.
  10. Replies
    6
    Views
    2,069

    XP20036230A02 Thanks.

    XP20036230A02

    Thanks.
  11. Replies
    6
    Views
    2,069

    Lennox xp20 cop chart

    Anyone know if there is a COP chart for the Lennox xp20 for different ambient temperatures?
  12. Replies
    2
    Views
    861

    The only specs i've ever given when replacing one...

    The only specs i've ever given when replacing one is the size, i've never been asked for the pitch. I suppose if you need to spec a replacement to a precise airflow there would be a fan curve chart...
  13. The dye should specify how much you need. If...

    The dye should specify how much you need. If not, an ounce or 2 would be plenty. Won't need much if the total charge is that small.
  14. Replies
    10
    Views
    2,377

    Just a thought, if your blower motor runs on...

    Just a thought, if your blower motor runs on startup, is there possibly a open high limit or rollout switch?
  15. Replies
    20
    Views
    2,761

    The way i think about this, if the first burner...

    The way i think about this, if the first burner is going out but the 2-4 burbers stay on, the gasflow out of the orifice must not be flowing. If there is no obstruction then it must be a gas...
  16. Yes you are right. I have a XP20

    Yes you are right. I have a XP20
  17. Lennox SLP98 90k btu

    Lennox SLP98 90k btu
  18. No, i have no bypass damper. I could install a...

    No, i have no bypass damper. I could install a bypass damper and raise the airflow, but why would i have the waste of a bypass damper when the heating system is capable of modulation?
  19. Lennox Heat Pump Capacity Output Max Setting

    I have a Lennox iharmony zoning system installed my my house. The problem i'm having is when only 1 zone is calling and the heat pump is operating in heat mode, it makes a vibrating sound from the a...
  20. Replies
    7
    Views
    837

    SLP98 & iHarmony zone control problem

    I've got a brand new SLP98UH090XV36C-09 i installed in my house with an S30 thermostat and a iHarmony zone control with 3 zones. When the zone control is connected to the furnace, the burners will...
  21. Replies
    2
    Views
    1,335

    Thanks, that is what i didn't get, and now i...

    Thanks, that is what i didn't get, and now i understand.
  22. Replies
    2
    Views
    1,335

    Using Enthalpy Conversion Chart

    How does the Enthalpy Conversion chart work to convert Web Bulb temperatures to enthalpy? It seems very straight forward except the "tenths of a degree Fahrenheit" part. I don't understand this...
  23. Replies
    10
    Views
    3,165

    i agree with hvacker. You should do an initial...

    i agree with hvacker. You should do an initial evaluation of the equipment. If your taking over for someone who knew what they were doing, everything should be in pretty good shape. But if the...
  24. Replies
    14
    Views
    4,529

    Check temperature rise and go from there. If...

    Check temperature rise and go from there. If it's ok, your limit is probably bad. If it's too high verify there are no restrictions in the furnace and then increase the fan speed.
  25. Replies
    45
    Views
    14,778

    Can you confirm when the compressor(s) cut out...

    Can you confirm when the compressor(s) cut out that the voltage to the compressor terminals is still present? That will confirm whether you have a control cutting out or something internal in the...
  26. Replies
    3
    Views
    4,643

    Tommyz23: If it were an air to air, i would...

    Tommyz23: If it were an air to air, i would think the TXV is stuck closed and needs to be replaced.

    Bergy: I have never checked the flow rate through a loop. How would i do it? I'm not sure...
  27. Replies
    3
    Views
    4,643

    Geothermal Heat Pump Problem...

    Problem: Evap coil is icing up and not cooling space down to setpoint.
    Data:
    R410A 340 High Side 76.5 Low Side
    10.7 degrees F Subcooling
    78 degrees F EWT
    82.5 degrees F LWT
    SA - 64.6 degrees...
  28. Replies
    11
    Views
    8,670

    All the trane units i've worked on if it's a...

    All the trane units i've worked on if it's a trane thermostat then then any standard thermostat will not work without installing the extra thermostat board first. You should be able to jump it out...
  29. agreed.

    agreed.
  30. Replies
    26
    Views
    6,300

    If it's raining and there's an emergency...

    If it's raining and there's an emergency refrigeration/ac call i would. It's only water and i'm not made of sugar. But lightening, no way.
  31. Replies
    17
    Views
    7,663

    could it be a crack in the heat exchanger that's...

    could it be a crack in the heat exchanger that's only opening up after the furnace runs for awhile?
  32. Replies
    21
    Views
    6,820

    The lennox iComfort only needs wireless internet...

    The lennox iComfort only needs wireless internet access. No additional gateway. It should work with any equipment as far as system monitoring/adjustment goes. But i have not actually tried it.
  33. As long as the spec's match up, enclosed or open...

    As long as the spec's match up, enclosed or open motor does not matter.
  34. Replies
    5
    Views
    2,975

    nice ones.

    nice ones.
  35. Replies
    2
    Views
    2,563

    this is why i ask for no ice. gross!

    this is why i ask for no ice. gross!
  36. Replies
    17
    Views
    5,097

    at least once per year. I'm sure there's alot of...

    at least once per year. I'm sure there's alot of ice machines out there that don't ever get cleaned. I always ask for no ice now after i started fixing them.
  37. Replies
    10
    Views
    5,633

    This is the Ask Our Pro's forum, and only Pro...

    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here. Please apply to the AOPC today, thank you.
    ...
  38. Replies
    8
    Views
    2,735

    This is the Ask Our Pro's forum, and only Pro...

    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here. Please apply to the AOPC today, thank you.
    ...