Search:

Type: Posts; User: DaveCR

Page 1 of 15 1 2 3 4

Search: Search took 0.01 seconds.

  1. Replies
    7
    Views
    1,799

    Is the blower compartment down stream of the...

    Is the blower compartment down stream of the cooling coil? If so, the upper humidity limit of 90% will be exceeded.

    Is the controller very close to the blower motor and/or is there a motor speed...
  2. Of the items you listed, not all of them are...

    Of the items you listed, not all of them are 'told' what to do by the controller. Some are inputs that 'tell' the controller what is going on in the world outside of the controller.

    DP sensor,...
  3. Replies
    1
    Views
    695

    I used the Honeywell TR20 series a while back...

    I used the Honeywell TR20 series a while back without any issues.
  4. Thread: AAM BBC-SD

    by DaveCR
    Replies
    11
    Views
    3,027

    The display can't read an SD card greater than...

    The display can't read an SD card greater than 2GB...
  5. Replies
    4
    Views
    736

    6 = +15Vdc 5 = Common (to comm and power) 4 =...

    6 = +15Vdc
    5 = Common (to comm and power)
    4 = +15Vdc
    3 = Common (to comm and power)
    2 = Rx/Tx -
    1 = Rx/Tx+
  6. Replies
    5
    Views
    1,888

    If the RTUs have a small display in them, the...

    If the RTUs have a small display in them, the procedures in this manual should be of help. You can also use a York branded MAP gateway.

    https://cgproducts.johnsoncontrols.com/met_pdf/12011998.pdf
  7. If the N31 has a LAN card then it's pretty easy....

    If the N31 has a LAN card then it's pretty easy.
    Use Site Builder to create a site with an ethernet connection.
    Open Project Builder, add an N31 Controller, edit the name to match the one you want...
  8. Replies
    8
    Views
    1,613

    JCI has been using those designations for at...

    JCI has been using those designations for at least 35 years. Why change something that works for them and causes their competition some grief.
  9. Replies
    3
    Views
    1,316

    This question has been asked here a couple of...

    This question has been asked here a couple of times in the past with no responses. It appears that York made no attempt to add integration capabilities to this product line or if they did, the...
  10. Replies
    22
    Views
    5,057

    JCI sells a PCV1626 without the airflow sensor....

    JCI sells a PCV1626 without the airflow sensor. There are canned commercial zoning files for the PCVs and PCG that work pretty well out of the box.
  11. Replies
    1
    Views
    3,629

    BCI-I is the way to go IF the unit supports it....

    BCI-I is the way to go IF the unit supports it. In other words, not all Intellipacs can be converted to BACnet communications. Give your local Trane rep the serial number and they will tell you if...
  12. Replies
    5
    Views
    830

    No. The vast majority of our controls customers...

    No. The vast majority of our controls customers have mechanical service contracts with the company. The labor to install the updates is charged off to the service agreement.
  13. Replies
    5
    Views
    830

    Usually five year SMAs.

    Usually five year SMAs.
  14. Replies
    16
    Views
    5,689

    A Viconics 8600 series room controller with some...

    A Viconics 8600 series room controller with some custom Lua programming might do the trick.
  15. Thread: Happy New Year

    by DaveCR
    Replies
    8
    Views
    919

    Happy New Year

    The title says it all.

    Good fortune to you all in 2019.
  16. Thread: Ground loops

    by DaveCR
    Replies
    35
    Views
    3,926

    Change it; the shield should be grounded at only...

    Change it; the shield should be grounded at only one point. If the transceivers are three wire capable (they have a common) then upgrade the wire as well.
    Other things to consider that generate...
  17. Replies
    1
    Views
    770

    Radwell may give you a few bucks for it.

    Radwell may give you a few bucks for it.
  18. Replies
    16
    Views
    3,863

    Ain't that the truth.

    Ain't that the truth.
  19. Replies
    5
    Views
    748

    Thanks FG and kp. Merry Christmas to you and...

    Thanks FG and kp. Merry Christmas to you and yours.
  20. Replies
    4
    Views
    1,116

    Many ways to skin a cat in AX or N4. Here's some...

    Many ways to skin a cat in AX or N4. Here's some logic that will do what you want; it enforces a two degree spread. (two states shown, only one logic group required per set point pairing) If you...
  21. Replies
    4
    Views
    1,603

    This ^^^^^ Put an email address in your...

    This ^^^^^

    Put an email address in your profile so I, and maybe others, can send you some pertinent info. on AX and N4.
  22. Replies
    1
    Views
    644

    That is my understanding of how it works. FWIW,...

    That is my understanding of how it works. FWIW, JCI uses different part numbers for initial purchase SMAs vs renewal SMAs; pricing is the same.
  23. Replies
    19
    Views
    3,153

    Good to know. To the OP, TU is more expensive...

    Good to know.

    To the OP, TU is more expensive than Rover....
  24. Replies
    19
    Views
    3,153

    I've heard horror stories of $4k; ultimately it...

    I've heard horror stories of $4k; ultimately it will be up to your friendly Trane dealer.
  25. The fix was to upgrade the firmware from 5.3 to...

    The fix was to upgrade the firmware from 5.3 to 6.x.
  26. Replies
    19
    Views
    3,153

    The software is called Rover. It is not cheap.

    The software is called Rover. It is not cheap.
  27. JCI had an issue with short duration, power...

    JCI had an issue with short duration, power outages locking up programmable controllers. It was fixed 4-5 years ago.
  28. Replies
    13
    Views
    5,004

    Having those addresses in use dealt me a fit one...

    Having those addresses in use dealt me a fit one time.
    https://hvac-talk.com/vbb/showthread.php?1842311
  29. With a few blocks and totalizer extensions,...

    With a few blocks and totalizer extensions, create a pulse train as input for the SlidingWindowDemand block.

    Steam demand/totalizer --> Convert to kWh --> Greater Than to reset steam totalizer...
  30. Replies
    67
    Views
    18,997

    Here's one by Honeywell....

    Here's one by Honeywell.
    http://s3.supplyhouse.com/product_category_files/10020-brochure.pdf
  31. Replies
    11
    Views
    3,678

    As orion suggested, use two. We have the remote...

    As orion suggested, use two. We have the remote dp reset the set point of the pump dp. If the network goes down, the pump maintains the last valid set point.
  32. Replies
    30
    Views
    29,402

    Ya know, that's basically what the JCI tech rep...

    Ya know, that's basically what the JCI tech rep that ended up on site said. After a couple of attempts, he was as befuddled as we were.
  33. Replies
    30
    Views
    29,402

    We recently had one that wouldn't respond to the...

    We recently had one that wouldn't respond to the default password. It took about six resets before it actually reset.
  34. Replies
    9
    Views
    1,389

    Not really controls related, but handy to figure...

    Not really controls related, but handy to figure out if the process you're trying to control has any chance of actually working.

    Q = 1.08 x CFM x delta T (Imperial units)

    Q = U x A x delta T...
  35. Replies
    7
    Views
    4,674

    Considering the field device trunk is landed on...

    Considering the field device trunk is landed on the isolated COMM3 port, I'd say COMM3.
    The comm cards in the Intellipaks may have a COMM4 option.
  36. Replies
    4
    Views
    971

    Switch high means the CO triac will control 24V...

    Switch high means the CO triac will control 24V Hot. Switch low means the triac will control 24V Common. The only difference is in the external wiring; the CO is a stand alone triac when use for...
  37. Replies
    7
    Views
    5,433

    We had issues with CCN (RTUs and VAVs, no...

    We had issues with CCN (RTUs and VAVs, no chillers) and 4.3; problems went away with 4.4 upgrade.
  38. Replies
    8
    Views
    4,115

    "When this actuator is used with a DDC...

    "When this actuator is used with a DDC controller, it is important to program the controller's output to provide a minimum control span of 4.5 to 11.5 Vdc, to assure full travel to each end of the...
  39. Configurable Output (0-10Vdc or triac) hardware...

    Configurable Output (0-10Vdc or triac) hardware point.
  40. Replies
    10
    Views
    1,471

    Wait a minute. TCP/IP = TC/I ; the protocols...

    Wait a minute. TCP/IP = TC/I ; the protocols cancel. :grin2:
  41. After mucking around trying to write to the UPC,...

    After mucking around trying to write to the UPC, we ended up changing the condensing unit configuration to follow a 4-20mA signal for staging and hardwired the input to the AHU controller.
  42. I don't know about the OA sensors, but the room...

    I don't know about the OA sensors, but the room and duct sensors are not thermistors.
  43. Replies
    5
    Views
    3,262

    This ^^^

    This ^^^
  44. Replies
    9
    Views
    2,193

    Contrary to what JCI instructors say, PCT/CCT is...

    Contrary to what JCI instructors say, PCT/CCT is all about the green triangles.
  45. Replies
    9
    Views
    2,193

    Yes, Johnson has canned routines that can be...

    Yes,
    Johnson has canned routines that can be downloaded that are called Commercial Zoning Application.
  46. Replies
    3
    Views
    1,212

    Thanks, bolt You mention using a jace, which...

    Thanks, bolt

    You mention using a jace, which KMC offers, but I don't see any drivers listed for their proprietary protocol.
    How is the Web Portal interface once it's configured by Total Control?...
  47. Replies
    3
    Views
    1,212

    KMC front end recommendation

    I have a customer that has tired of WinControl and would like something less clumsy to use. For example, they have several NiagaraAX systems and like that user interface.
    Their system is comprised...
  48. Replies
    76
    Views
    12,319

    Take a look at the OP's profile. Joined on the...

    Take a look at the OP's profile. Joined on the 4th, made one post and hasn't been back since. Obviously not interested in the discussion or is possibly following the discussion under a different name.
  49. Replies
    8
    Views
    2,673

    14.4 (4.4) wizards were released last month.

    14.4 (4.4) wizards were released last month.
  50. Replies
    8
    Views
    2,673

    JCI uses rebadged Distech products for their Lon...

    JCI uses rebadged Distech products for their Lon offerings.
    The LX wizards are available for N4 as a download off of the Connected Community site. Maybe the jar files are part of that package.(?)
Results 1 to 50 of 733
Page 1 of 15 1 2 3 4