Search:

Type: Posts; User: chilledcool

Page 1 of 6 1 2 3 4

Search: Search took 0.02 seconds.

  1. Replies
    10
    Views
    8,942

    It was the compressor. Readings were way to...

    It was the compressor. Readings were way to close. The relay was bad which is probably what did in the compressor. New compressor and drier all is working well.
  2. Replies
    10
    Views
    8,942

    According to Tecumseh spec sheet RLA 4 amps, LRA...

    According to Tecumseh spec sheet RLA 4 amps, LRA 31.
    Start relay was found to be bad, all start components were replaced including run cap.
    C-S = 2.3
    C-R = 1.9
    R-S = 4.1
  3. Replies
    10
    Views
    8,942

    Problems with potential relay

    Walk in cooler, Tecumseh compressor AKA9442EXD, R-22.

    Customer calls walk in cooler warm compressor hot. I check unit and find the potential relay contacts not opening and further inspection find...
  4. Replies
    6
    Views
    1,731

    Have not had the water tested, but we have very...

    Have not had the water tested, but we have very hard water here in Florida.
    The ice machine gets a lot of scale build up. I have been looking at filters, some are one cartridge and say they can...
  5. Replies
    6
    Views
    1,731

    Ice machine water filtering.

    I'd like to get an idea of what water filter most of you are using for ice machines.
    Some of these filtering systems are quite pricey.
    I am currently looking into installing one on a Hoshi...
  6. Replies
    2
    Views
    1,158

    Thanks 24, I appreciate the input.

    Thanks 24, I appreciate the input.
  7. Replies
    2
    Views
    1,158

    Scotsman Flaker

    I have a Scotsman Flaker, M# AFE400A-1B, S# 0407132 0016338, that I have to replace the gear motor bearing on. I have not worked on one of these yet so I was looking for a heads up on what I may...
  8. Replies
    14
    Views
    3,645

    Thanks for all the replies. I'm going to replace...

    Thanks for all the replies. I'm going to replace the cap tube again and use the 032 drier instead of the copper one. Hopefully this will last for several years. I hope.
  9. Replies
    14
    Views
    3,645

    Cap tubes and POE just not a good mix. I'm going...

    Cap tubes and POE just not a good mix. I'm going to have to fix this again, I just hope it's not every seven months.
    I wonder if I'm better off putting a regular filter drier in rather then the...
  10. Replies
    14
    Views
    3,645

    True TDD-4 restriction again!!

    Seven months ago had a TDD-4 keg cooler with cap tube restriction. Opened system, blew out with nitrogen, changed compressor oil, factory cap tube (.046 x 10') and factory filter drier, vacuumed down...
  11. Replies
    47
    Views
    9,557

    It is wired correctly. What is the best temp...

    It is wired correctly. What is the best temp setting for defrost termination?
    Is 50 degrees about right?
  12. Replies
    47
    Views
    9,557

    You did get it right. Thank you. 1-...

    You did get it right. Thank you.
    1- possibility, the defrost is set for twice a day every twelve hours. I told the owner I was going to put another one or two defrosts in there. Do I need 4?...
  13. Replies
    47
    Views
    9,557

    First let me say thank you to all of you that...

    First let me say thank you to all of you that shared your knowledge and experience in helping me out with this freezer. This was a great learning experience. Things are looking much better.
    When I...
  14. Replies
    47
    Views
    9,557

    A damaged reed would cause the high suction...

    A damaged reed would cause the high suction pressure I'm seeing?
  15. Replies
    47
    Views
    9,557

    To many hands in this thing previously. Have to...

    To many hands in this thing previously. Have to check the obvious first. If it were running on one cylinder would I still pull 5.6 amps?
    Don't want to change a pump and then find out I have a TXV...
  16. Replies
    47
    Views
    9,557

    Today 21 degrees and hopefully still dropping. ...

    Today 21 degrees and hopefully still dropping.





    No I did not test it this way. I will do it tomorrow. Just to make sure i do it right this time. Run unit, jump LPC, close suction valve,...
  17. Replies
    47
    Views
    9,557

    When I pumped it down the pressure climbed to 8...

    When I pumped it down the pressure climbed to 8 and held there so I figured it was just some residual refrigerant. I did not pump into a deep vacuum, shut it off as soon as it hit zero. I'm leaning...
  18. Replies
    47
    Views
    9,557

    I spoke with the owner and apparently he had a...

    I spoke with the owner and apparently he had a few guys out there before me. The last guy he said was there for 15 minutes and said he added refrigerant. I looked the system over again and checked...
  19. Replies
    47
    Views
    9,557

    Thanks for the replies. I'm downloading the...

    Thanks for the replies. I'm downloading the performance calculator as I type.

    Powell out of your four options I like number four. I'll bring an extra large hammer.
  20. Replies
    47
    Views
    9,557

    It has a receiver. Your suggesting from the...

    It has a receiver. Your suggesting from the pressures that the valves may be damaged and the refrigerant is bypassing? Best way to prove this out I guess would be powell's suggestion of a pumpdown....
  21. Replies
    47
    Views
    9,557

    Box is small , 6 x 6 or 6 x 8. Box is in good...

    Box is small , 6 x 6 or 6 x 8. Box is in good shape, Its fiber glass inside and out. I did not get the amp draw I will get that tomorrow. Condensing unit is on roof of box and no disconnect so hard...
  22. Replies
    47
    Views
    9,557

    My thoughts today exactly.

    My thoughts today exactly.
  23. Replies
    47
    Views
    9,557

    Now Now calm down. Some of your questions are...

    Now Now calm down. Some of your questions are answered in my first post. As far as the site glass goes I am not concentrating on it, I made a comment about it so I could get some constructive...
  24. Replies
    47
    Views
    9,557

    My initial thought was that I am still low on...

    My initial thought was that I am still low on refrigerant and that my high side was a little low and my low side a little high. I figured the low side was high because of the box temp.
    If a freezer...
  25. Replies
    47
    Views
    9,557

    Walk in freezer not making temp

    Had a call for a walk in freezer not dropping below 30 degrees. Last call late this afternoon so not much time to hang around and watch the unit. I will be returning tomorrow to spend more time on...
  26. Replies
    91
    Views
    12,857

    Poll: I got a headache just looking at this monster.

    I got a headache just looking at this monster.
  27. Replies
    91
    Views
    12,857

    Poll: Not much of a refer guy. But my first question...

    Not much of a refer guy. But my first question would be depending on how thick the ice on the suction line is, are you actually taking the temp of the line or of the ice build up? The saturation temp...
  28. Replies
    34
    Views
    4,316

    So how did this work out? Did the larger return...

    So how did this work out?
    Did the larger return help your problem and increase air flow? You should have noticed a considerable amount of increased air flow out of your supply registers.
  29. Replies
    34
    Views
    4,316

    If you only have the one return mentioned and it...

    If you only have the one return mentioned and it truly has only an 8 inch duct attached to it, that is a big problem, the return is way undersized.
    Upon initial start up, this small of a return...
  30. Replies
    28
    Views
    2,968

    Supposedly it is the same, but I am not sure. I...

    Supposedly it is the same, but I am not sure. I am going to try one to see if it is the real thing.
  31. Replies
    28
    Views
    2,968

    The Mars Bar has a new name... Snickers Almond...

    The Mars Bar has a new name... Snickers Almond Bar.

    http://www.oldtimecandy.com/mars-bar.htm
  32. Replies
    20
    Views
    3,053

    I live in Florida also. My homeowners insurance...

    I live in Florida also. My homeowners insurance has risen a total of 500 percent in the last two years. The insurance companies have gone crazy. People are trying to move out of the state but the...
  33. Replies
    21
    Views
    3,107

    The builder mentioned a dirty filter. But did he...

    The builder mentioned a dirty filter. But did he change it? Depending on how bad the filter is could have a great impact on the cooling capacity of the system. If not enough air passing through the...
  34. Replies
    5
    Views
    2,305

    I would do as Yota suggested pull the charge,...

    I would do as Yota suggested pull the charge, evacuate and weigh in the proper amount of refrigerant per the dataplate. The last table I did only held 9 Oz of refrigerant.
    Also unplug the compressor...
  35. Replies
    3
    Views
    1,270

    I believe that is a 10 Seer unit. But I would...

    I believe that is a 10 Seer unit. But I would wait til one of the trane guys respond to be sure.
  36. I'll have to agree here. I'm sure there was some...

    I'll have to agree here. I'm sure there was some sort of return through the ceiling at one time and through the years they were covered up.
  37. Replies
    12
    Views
    4,917

    At least they left a vacuum and a broom down...

    At least they left a vacuum and a broom down there so you could tidy up before you left.
    Remember a good tech always leaves the place looking better then when they arrived..
  38. Replies
    3
    Views
    1,780

    Ice-O-Matic Parts?

    Anyone know where to get parts for Ice-O-matic ice machines. I am in the Tampa Bay area, Florida. No one in this area seems to carry the line that I can find.
    I just sent an e-mail to Ice-O-matic to...
  39. Replies
    88
    Views
    11,684

    43 here. Florida West Coast. Actually had to put...

    43 here. Florida West Coast. Actually had to put the heat on.
    Stay warm.
  40. Replies
    10
    Views
    1,435

    This tester is the best for testing the lights....

    This tester is the best for testing the lights. It actually works. I have been using it now for several years and it sure has saved a lot of time, no more pulling one bulb at a time to see which one...
  41. Replies
    15
    Views
    4,104

    I'll tell. For a dummy, Ice's posts sure make a...

    I'll tell. For a dummy, Ice's posts sure make a lot of sense.
    How he does it, I don't know. Could be the eighth wonder of the world.
  42. Replies
    15
    Views
    4,104

    Thanks for the replies. My main concern was...

    Thanks for the replies.
    My main concern was component match up since it looked like the TXV was replaced at one time. Ice and the Fridge confirmed that the match up is correct.
  43. Replies
    15
    Views
    4,104

    I am working on a walk in cooler that has a...

    I am working on a walk in cooler that has a restriction in the drier but I want to make sure the components in the system match up correctly since I have to open it up. The expansion valve looks like...
  44. Replies
    39
    Views
    8,670

    To install ductwork and to do it properly so...

    To install ductwork and to do it properly so there are no leaks for many years to come is a highly labor intensive job. You can have it done quickly for less money, but if you want it done correctly...
  45. Replies
    16
    Views
    3,506

    I do not work outside in the rain. I have this...

    I do not work outside in the rain. I have this phobia when it comes to water and electricity. Besides who knows what has been done to a unit from a previous service company.
  46. Replies
    9
    Views
    3,223

    Owner did not think the machine was working...

    Owner did not think the machine was working properly since there was no ice after a busy weekend, plus the fact that they emptied the remaining ice for a Sunday fishing trip.
    After cleaning the...
  47. Replies
    9
    Views
    3,223

    The ice looks good it is very clear.

    The ice looks good it is very clear.
  48. Replies
    9
    Views
    3,223

    Looking for some advice on the following. Friend...

    Looking for some advice on the following.
    Friend owns a bar and he does not think his ice machine (Hoshizaki KM-1300SAF) was working properly and asked me to look at it. It was a 93* day and the...
  49. Replies
    5
    Views
    1,745

    Check that coil to see if any thing was sucked up...

    Check that coil to see if any thing was sucked up in it and blocking it. TD of 30* points to low air flow. Need more info from you to get a better idea of what is going on with the system. Pressure...
  50. Replies
    10
    Views
    2,409

    Stamped registers usually have less free space...

    Stamped registers usually have less free space (to much restriction), the louvered ones will open up the register more.
    Some of the stamped I have seen in place run the air to much to the ceiling...
Results 1 to 50 of 254