My comment on low heat output was directed at when the coil had frosted up. After a defrost, I get 85 degrees when the outside temp is 30ish. Tomorrow I will check to see if there is...
Type: Posts; User: decarguy
CircusEnvy,
My comment on low heat output was directed at when the coil had frosted up. After a defrost, I get 85 degrees when the outside temp is 30ish. Tomorrow I will check to see if there is...
beenthere,
it does not go into defrost, just keeps running with very little heat output eventually backup heat kicks in, when I force defrost it completes the defrost. air filter is brand...
You are right, he no diagnostician and he did put s t-stat instead of a sensor on the coil.
Thanks you for taking time to write but no one has really answered my question. What, other than the...
1. This guy comes as highly rated as anyone in the area so I might get someone else just as "good".
2. Even this guy can wire up a board. He does HP installs.
3. I did not ask you to fix...
Dogboy,
How could Freon charge effect defrost cycling on a demand based system? As far as I can tell the system compares air temp to coil temp and starts a cycle when the difference reaches a...
Coleman/Evcon FRHS0361CD 15 SEER/ 9 HSPF heat pump installed in 2001. System has demand defrost. I am located in central Pa where nighttime temps are usually in the 20s but we get down to around 10...