  1. Replies
    3
    Views
    535

    Your going to need TU to connect to the AFD3...

    Your going to need TU to connect to the AFD3 board. There is a procedure on how to do this.Last time i had this problem the DSP board was my issue.
  2. Thread: Trane ch 530

    by manny238
    Replies
    29
    Views
    1,093

    So you have to enable the relay for the VFD...

    So you have to enable the relay for the VFD you’re working on ( run command ) while in binding mode and then you enter the 0-10 VDC signal you want in the speed analog llid for the same circuit. The...
  3. Thread: Trane ch 530

    by manny238
    Replies
    29
    Views
    1,093

    You need to find the relay board for the...

    You need to find the relay board for the condenser fan motors you’re working on ( you need to move your screen down). You will see where you can energize all your relays. Just click on each output. ...
  4. Replies
    17
    Views
    1,040

    Sounds like your evap is oil logged

    Sounds like your evap is oil logged
  5. Replies
    22
    Views
    9,483

    I’ve had some where the piston was worn and...

    I’ve had some where the piston was worn and didn’t seat against the valve body anymore. I was getting random low superheat and loss of charge alarms. I ended replacing the complete EXV assembly, took...
  6. Replies
    21
    Views
    15,840

    How old are your machines? Check your plug...

    How old are your machines? Check your plug connections at each fan motor.


    Sent from my iPhone using Tapatalk
  7. Replies
    3
    Views
    860

    Make sure your EXV and liquid level sensor are...

    Make sure your EXV and liquid level sensor are binded to the correct circuit.


    Sent from my iPhone using Tapatalk
  8. Replies
    5
    Views
    1,208

    30HXC EXV oil in it??

    Lmao


    Sent from my iPhone using Tapatalk
  9. Replies
    10
    Views
    1,976

    I’ve had very good luck with this one, purchased...

    I’ve had very good luck with this one, purchased it at united refrigeration. Use it for my 85lb recovery tanks.
    ...
  10. Replies
    5
    Views
    733

    Your welcome. [emoji482] Sent from my iPhone...

    Your welcome. [emoji482]


    Sent from my iPhone using Tapatalk
  11. Replies
    5
    Views
    733

    The seal is built into the valve. ...

    The seal is built into the valve.

    https://images.platforum.cloud/uploads/20220914/21ab9f366377198da781e483029be24f.jpg


    Sent from my iPhone using Tapatalk
  12. Replies
    5
    Views
    733

    There is no separate gasket. Your going to have...

    There is no separate gasket. Your going to have to replace the valve.


    Sent from my iPhone using Tapatalk
  13. Replies
    5
    Views
    682

    Here is the RP manual. 834631 Sent from my...

    Here is the RP manual. 834631


    Sent from my iPhone using Tapatalk
  14. Replies
    1
    Views
    2,208

    Are you sure your on the correct Comm port? ...

    Are you sure your on the correct Comm port?

    You may need to download a driver for your cable. Look up any Information from your cable and see if you can find a driver online. Just be wary of...
  15. Replies
    2
    Views
    1,378

    Annex Air Compressor VFD

    If your having issues with the variable speed compressor Your better off calling Danfoss Technical Support.


    Sent from my iPhone using Tapatalk
  16. Replies
    4
    Views
    1,496

    Check your email if you still need it. ...

    Check your email if you still need it.


    Sent from my iPhone using Tapatalk
  17. Replies
    12
    Views
    2,964

    My apologies king I thought it was posted in...

    My apologies king I thought it was posted in 8/2013.


    Sent from my iPhone using Tapatalk
  18. Replies
    4
    Views
    1,496

    York vsd drive

    It’s been posted Already if you search you can find it.
  19. Replies
    12
    Views
    2,964

    They last posted in 2013, I’m hoping they figured...

    They last posted in 2013, I’m hoping they figured it out by now.


    Sent from my iPhone using Tapatalk
  20. Replies
    12
    Views
    6,816

    You need to look that up on the hub. Shouldn’t be...

    You need to look that up on the hub. Shouldn’t be shared on a open forum.


    Sent from my iPhone using Tapatalk
  21. Replies
    16
    Views
    4,088

    The service manual is in the Turbotool. ...

    The service manual is in the Turbotool.


    Sent from my iPhone using Tapatalk
  22. Replies
    16
    Views
    4,088

    Have you tried to download the Turbotool app. I...

    Have you tried to download the Turbotool app. I believe you can access the Turbocor service manual from there. If not I can send it to you tonight once I get back into town.


    Sent from my iPhone...
  23. Replies
    15
    Views
    4,015

    What exactly are you trying to do? If you have a...

    What exactly are you trying to do? If you have a RTHD with a UC800 that means it already has a TD7 display.
  24. Replies
    2
    Views
    2,837

    Trane RTAA is a great machine. Sent from...

    Trane RTAA is a great machine.


    Sent from my iPhone using Tapatalk
  25. Replies
    10
    Views
    3,671

    Set the point out of service, and set the state...

    Set the point out of service, and set the state to Normal. Not really a diagnostic.

    Binary input 152 is used to help keep track of the supply fan run hours.


    Sent from my iPhone using Tapatalk
  26. Replies
    12
    Views
    6,816

    Yes. RTAF mostly. Stulz uses the same motor,...

    Yes. RTAF mostly.

    Stulz uses the same motor, they were having the same problem. Some of the replacement motors are from another manuf.


    Sent from my iPhone using Tapatalk
  27. A decent log might get you some more answers. I’d...

    A decent log might get you some more answers. I’d be looking at EXV%, liquid level operation and make sure your gas pump is operating correctly. Check temperature sensors for accuracy as well.

    ...
  28. Thread: YORK FORMS

    by manny238
    Replies
    5
    Views
    2,587

    Thank you got them. Sent from my iPhone...

    Thank you got them.


    Sent from my iPhone using Tapatalk
  29. Thread: YORK FORMS

    by manny238
    Replies
    5
    Views
    2,587

    Can you share with me as well. Thank you ...

    Can you share with me as well. Thank you


    Sent from my iPhone using Tapatalk
  30. call another tech

    call another tech
  31. Replies
    2
    Views
    3,021

    if your losing a lot of refrigerant you need to...

    if your losing a lot of refrigerant you need to recover the refrigerant or pump the system down. your also gonna need Techview service tool.
  32. Replies
    4
    Views
    1,899

    What kind of oil issues are you having?

    What kind of oil issues are you having?
  33. Replies
    9
    Views
    3,417

    Merry Xmas and happy new year. Sent from my...

    Merry Xmas and happy new year.


    Sent from my iPhone using Tapatalk
  34. Replies
    13
    Views
    4,693

    Sounds like your pressure reducing valve is...

    Sounds like your pressure reducing valve is bleeding by. one way to find out is if your city pressure matches your loop pressure.


    Sent from my iPhone using Tapatalk
  35. Replies
    12
    Views
    6,020

    811840 i found the same thing when i was...

    811840

    i found the same thing when i was replacing the IGV's on a compressor. Handful of companies worked on this smardt before us. Owner had just purchased building, we had no history on chiller....
  36. Kinda sounds like what happen here....

    Kinda sounds like what happen here. https://images.platforum.cloud/uploads/20190804/51c619fd79738703a54686dff9bfbc77.jpg


    Sent from my iPhone using Tapatalk
  37. Replies
    6
    Views
    1,591

    Process chiller they only shut down 2 times a...

    Process chiller they only shut down 2 times a year. circuit #1 had a low charge we took out charge to confirm and go back with nameplate. circuit #2 had small leaks that needed to be repaired on...
  38. Replies
    4
    Views
    1,236

    Trane RTHC panel upgrade from UCP@

    It’s not really a big secret, I’m sure a lot of guys here have done panels on centrifugals.


    Sent from my iPhone using Tapatalk
  39. Replies
    4
    Views
    1,236

    If upgrading it needs to be upgraded to UC800....

    If upgrading it needs to be upgraded to UC800. Get your with your local Trane office for assistance.


    Sent from my iPhone using Tapatalk
  40. Replies
    6
    Views
    1,591

    I did a chiller over a weekend. 1 day to recover,...

    I did a chiller over a weekend. 1 day to recover, install, leak check and evacuate. Next day to re-charge and check operation.


    Sent from my iPhone using Tapatalk
  41. Replies
    2
    Views
    1,358

    Start disconnecting each llid 1 by 1 until you...

    Start disconnecting each llid 1 by 1 until you see your sensors come back online. It would be a good idea to replace the ribbon cable anyway.


    Sent from my iPhone using Tapatalk
  42. Replies
    23
    Views
    7,125

    https://images.platforum.cloud/uploads/20190629/28...

    https://images.platforum.cloud/uploads/20190629/2821c1489ce457886cfabd02eedb73a2.jpg

    Are these the parameters your looking for? They are under the configuration tab.



    Sent from my iPhone...
  43. Replies
    23
    Views
    7,125

    yeah Trane did a good job on putting these retros...

    yeah Trane did a good job on putting these retros together. Does get a bit confusing when you do a 4 compressor chiller but overall once you do 1, the next are a cake walk
  44. Replies
    23
    Views
    7,125

    The software update is pretty easy. Just make...

    The software update is pretty easy. Just make sure you choose the correct product (RTA). Me and a co worker did a VFD retro on a 2 compressor RTAC and it took about 6 hours. You'll need to bind 2...
  45. Replies
    7
    Views
    2,862

    In my town Trane used to rep them, I think they...

    In my town Trane used to rep them, I think they still do in some locations. Good luck with there tech support.


    Sent from my iPhone using Tapatalk
  46. Replies
    6
    Views
    4,556

    Just google for the IOM. The default setting for...

    Just google for the IOM. The default setting for compressors overload is 0. Check all your configuration settings. Sometimes when the chiller module is going bad it will lose all configuration...
  47. Replies
    7
    Views
    2,647

    Trane RTAE chiller running in hand

    I don’t really understand your question but I’ll give it a shot. If your chiller was operating under BAS controls and they were to fail. You would need to change the chiller setpoint source to front...
  48. Replies
    19
    Views
    12,850

    I’ve only worked on water cooled machines....

    I’ve only worked on water cooled machines. Thought they all used the same compressor.


    Sent from my iPhone using Tapatalk
  49. Replies
    19
    Views
    12,850

    Have you replaced the internal oil filter max...

    Have you replaced the internal oil filter max psid should be 25. I had the exact same problem on a 30HXC, ended up replacing the oil solenoid and internal filter. Good luck.
  50. So the unit will be used as a VAV unit? Not...

    So the unit will be used as a VAV unit?

    Not saying it cant be done but ive never seen a newer Trane VAV unit with a conventional thermostat. You will need a simple Trane zone sensor installed on...