  1. Replies
    11
    Views
    9,112

    I assume you have i-Vu v6.0 as you are installing...

    I assume you have i-Vu v6.0 as you are installing the Carrier front-end?

    Yes, I have 6.0 Pro Installed

    Are you using an OpenLink or CCNLink to integrate the BACnet units?

    I have it connected...
  2. Replies
    11
    Views
    9,112

    I have a site that I am trying to integrate a...

    I have a site that I am trying to integrate a Trane BCI in to iVu. I have the tool and have opened the unit on my laptop. I have verified that all the above is correct (baud, bacnet switch,...
  3. Replies
    10
    Views
    2,502

    bacnet>ccn is correct. I could not remember what...

    bacnet>ccn is correct. I could not remember what the menu was so I called it the port menu when it is the Device Manager. Instead of looking for the drivers automatically you will need to point...
  4. Replies
    10
    Views
    2,502

    There is a two step driver process that involves...

    There is a two step driver process that involves going in to the port menu and manually adding the drivers. I'm not sure if you have done this or if you have seen the bulletin that comes with NSTV...
  5. To my knowledge it is not compatible yet. I use...

    To my knowledge it is not compatible yet. I use win7 for all the laptops I set up with NSTV.
  6. Replies
    3
    Views
    1,237

    You can do it on a controller by controller basis...

    You can do it on a controller by controller basis just to find the sections to do a scan on. If you click "find Element" while connected to a controller that IS NOT on the comm bus you can search...
  7. Replies
    12
    Views
    3,597

    You should be able to have the 6400 send NETOUT...

    You should be able to have the 6400 send NETOUT commands that are tied to a Hardwired DI. The NETOUT should be able to write to the Fire Shutdown over the network as long as it is a R/W point. If...
  8. Replies
    30
    Views
    29,403

    So by the time I got to the shop this morning the...

    So by the time I got to the shop this morning the MAP 1810 had already been sent back for a new one but got the new one this afternoon and it had the same problem as the first one. I followed the...
  9. Replies
    30
    Views
    29,403

    Thank you! I will try connecting in the morning...

    Thank you! I will try connecting in the morning and post the results.
  10. Replies
    30
    Views
    29,403

    541801 It connects to the unit and creates a...

    541801

    It connects to the unit and creates a wireless access point to the unit. You then log in to the MAP 1810 thru WiFi and by pointing to a website you are able to configure the unit from a...
  11. Replies
    30
    Views
    29,403

    Johnson MAP 1810

    I am trying to connect to a MAP 1810 we just got for programming Johnson units. I can see the MAP on my wireless network but I cant get the password to work. I have tried resetting the device to...
  12. Replies
    18
    Views
    11,060

    It sounds to me like a problem resulting from no...

    It sounds to me like a problem resulting from no linkage. The DAT sensors at the zone are all the box has to go off of to know what mode the unit is in. The reason they stay at open after the unit...
  13. Replies
    1
    Views
    1,173

    We can do graphics for you but if you are looking...

    We can do graphics for you but if you are looking for sweet 3d floor plans you should check this guy out too:

    http://www.customcontrolgraphics.com/

    Email me with what you are looking for and...
  14. Replies
    6
    Views
    2,017

    I found a sensor that looks like it will meet the...

    I found a sensor that looks like it will meet the customers needs.

    525971

    If it gets approved and we install it I will update everyone on how well it works.
  15. Replies
    6
    Views
    2,017

    Particulate Monitor

    I have been asked to design a monitoring system for 3 cleanrooms. Temp and humidity is a no-brainer but they are also asking for continuous monitoring of the particulate count with alarms associated...
  16. Replies
    5
    Views
    1,661

    Grab a snack and settle in for some reading (it...

    Grab a snack and settle in for some reading (it may save you from picking a scab):

    what-BMS-system-would-you-install
  17. Replies
    16
    Views
    5,958

    Which is also why the Bacview isn't working. Once...

    Which is also why the Bacview isn't working. Once touch support is enabled the bacview no longer works.
  18. Replies
    16
    Views
    5,958

    I'm not 100% sure but a possibility may be that...

    I'm not 100% sure but a possibility may be that the controllers are 6.0 and your FA is 5.1

    Do the controllers show up when you click "Find Devices" and then just don't upload or can you not even...
  19. Replies
    16
    Views
    3,774

    I'm a union controls engineer and was union when...

    I'm a union controls engineer and was union when I was a tech too. There are a lot of union controls techs here and ones that are non-union still work for union companies but on the office/shop...
  20. Can you just choose one of the AHU's to be the...

    Can you just choose one of the AHU's to be the one that controls both fans? Leave the other signal and transducer connected but run both VFD signals through a DPDT so that when the main one is...
  21. Replies
    5
    Views
    1,764

    To add to this: If you select download after...

    To add to this:

    If you select download after you delete the program then FA or iVU will acknowledge that there is no program on the controller so you truly have a blank controller.
  22. Replies
    2
    Views
    832

    This is probably better for the HVAC section but...

    This is probably better for the HVAC section but it sounds like you have a restriction. Either in the cap tube or the liquid line. You are starving your evap with results in the low pressure and...
  23. Replies
    5
    Views
    1,943

    Agreed. HVAC experience is huge. TO control...

    Agreed. HVAC experience is huge. TO control something correctly you have to know how it works. You also need to be able to look at a sequence of operation and be able to decipher if it is correct...
  24. It looks like those are the wire labels. ...

    It looks like those are the wire labels. YL=Yellow wire and there will be a number on that wire so you can tell the difference between the different yellow wires. For instance there is a yellow...
  25. Replies
    7
    Views
    3,256

    UPDATE: I received the 6.0 drivers and loaded...

    UPDATE:

    I received the 6.0 drivers and loaded them up. The momentary switch worked perfectly for what I needed and the program does exactly what I need it to. Thank you for everyone's help.
  26. Replies
    7
    Views
    3,256

    513411 I used the BV with momentary enabled. ...

    513411

    I used the BV with momentary enabled. I had to create a holding circuit to keep the timer running once the momentary reset. It has passed the simulator test but I have to wait until...
  27. Replies
    7
    Views
    3,256

    I originally tried the momentary and it wouldnt...

    I originally tried the momentary and it wouldnt load becuase it was an older controller. I am going to update my controller and try it again.
  28. Replies
    7
    Views
    3,256

    I will try that right now. Thank you!

    I will try that right now. Thank you!
  29. Replies
    7
    Views
    3,256

    iVu/ALC Microblock Programming Question

    513361

    I am trying to make a network override button for a iVu program. My goal it to give the customer a button on his screen that will allow him to enable the occupancy override but I cant...
  30. Replies
    20
    Views
    12,090

    I have been able to connect to other devices that...

    I have been able to connect to other devices that have an rnet connection. I am not able to open the programs of non-Carrier controllers but I can discover points in the BACnet discovery tab. I...
  31. Replies
    11
    Views
    2,944

    There are three possible things that I can think...

    There are three possible things that I can think of:

    The first is the layering - I had a site that the bubble didn't seem to line up right or show up. I had to open the floorplan up in viewbuilder...
  32. Replies
    4
    Views
    1,881

    Does he not want to use what is there, does he...

    Does he not want to use what is there, does he want to use a uniform temp or do they not have actual OA for all the units?
  33. Replies
    16
    Views
    4,197

    I was looking for that and couldn't find it. I...

    I was looking for that and couldn't find it. I only have the OSA conditions. There is a really cool looking one that links to NWS but I don't have that available in my equipment builder. Do you...
  34. Replies
    16
    Views
    4,197

    kontrol I am new to BACnet and working on...

    kontrol

    I am new to BACnet and working on learning as much as possible. I work almost strictly with Carrier right now and I am using iVu for the BACnet. I am trying to setup a weather station...
  35. Thread: Trane BCI-R

    by mcguire07
    Replies
    1
    Views
    1,331

    Trane BCI-R

    I am potentially going to be doing some integration of Trane Boxcars into a Carrier iVu system.

    I have been told that it is pretty easy to setup the BCI-R cards. I have downloaded the Trane...
  36. Replies
    1
    Views
    889

    Not that I know of. Look on the desktop, there...

    Not that I know of. Look on the desktop, there may be a window that says "Controller ready for use" or something like that that you need to select OK for and it should take the gray off. If it...
  37. To the best of my knowledge you can only work...

    To the best of my knowledge you can only work with Best++ on the CCN side and not the iVU side. The Best++ resides on the controller where as the graphics and control programs reside on the iVu or...
  38. Replies
    3
    Views
    1,232

    Sensor Group should have worked but also try...

    Sensor Group should have worked but also try setting up an alarm for that point but don't enable it or give it any routing. This is also another way of giving it an algorithm to validate the input.
  39. Replies
    6
    Views
    1,929

    Correct! All the algorithms for CCN reside on...

    Correct! All the algorithms for CCN reside on the controllers themselves. If you look up CC6400 you will find a book that details all the canned algorithms available for use. I have been...
  40. We do primarily commercial HVAC and a lot of...

    We do primarily commercial HVAC and a lot of building automation. We have an account overseas on a cargo ship but that is a small percent of the business at this time. We would love for you to send...
  41. Replies
    17
    Views
    13,687

    Also, as others said, we're commercial and don't...

    Also, as others said, we're commercial and don't slow down in the winter.

    Sent from my SCH-I535 using Tapatalk 4 Beta
  42. Replies
    17
    Views
    13,687

    If you lie, employers will find out, especially...

    If you lie, employers will find out, especially in a place like Arizona where the trade is relatively small and everyone knows each other. Also, a smart employer would likely look to see if you had a...
  43. Have you considered getting into automation and...

    Have you considered getting into automation and controls? Better pay, fewer rooftops, opportunity to train junior techs.

    Sent from my SCH-I535 using Tapatalk 4 Beta
  44. Bump! Sent from my SCH-I535 using Tapatalk 4...

    Bump!

    Sent from my SCH-I535 using Tapatalk 4 Beta
  45. Relocation assistance may be available as well,...

    Relocation assistance may be available as well, if you're looking for a small town feel with the amenities of a big city and low cost of living (not to mention climate driven job security), Tucson is...
  46. HELP WANTED Commerial HVAC Service and Controls in Tucson, AZ

    McGuire MECH, a family owned and operated business serving Tucson and Southern AZ currently has several opportunities available for Jr, Sr and Controls technicians.

    We are a young company that has...
  47. Replies
    19
    Views
    9,896

    I am thinking on going with the 28' to try and...

    I am thinking on going with the 28' to try and cover most applications. My shop will be out of the way to be going back too often to get a larger ladder but I need something that will be manageable...
  48. Replies
    19
    Views
    9,896

    Extension Ladder

    I am looking at purchasing an extension ladder for my service truck. Its been a long time since I have needed one so I'm not sure what size to get to cover most applications. Do I need to go with a...
  49. 5 years seems a little early. Maybe just do a...

    5 years seems a little early. Maybe just do a front end now but even that may not be necessary. The best thing to do is take an oil sample and see what shows up in the oil. If there is no tin in...
  50. Replies
    25
    Views
    13,193

    Check the cooling tower sump heater. The towers...

    Check the cooling tower sump heater. The towers should have sump heaters to keep the loop temp warm so you don't lose oil due to cold condenser temps. I have seen both failed heaters and also...