There are no stoppers. This particular damper has only two setscrews the lock the shaft in.
There are these 45deg and 60deg pins that can be installed into the damper motor, optional purchase,...
Type: Posts; User: aircent1
There are no stoppers. This particular damper has only two setscrews the lock the shaft in.
There are these 45deg and 60deg pins that can be installed into the damper motor, optional purchase,...
Anyone familiar with redlink mard8 vav.? I'm having problems with air leakage or bypassing damper blade in the 100% closed or "off zone" period. It's enough to overcool the space in a couple rooms...
Sounds like h10 is a winner! No complaints yet from anyone
Is the battery one just as good as the plug in version?
Looking into this h10 too, but need some pros and cons of which to get.
I setup a conference call with him to run through setup with my client
He was very helpful.
Thx anyway chuck, been there done that, called west region network tech today. He explained its too technical to explain over the phone and he agreed that their manuals are very thorough and...
anyone familiar with the setup of the gb50 centralized controller?
could anyone breakdown the setup and network initial settings for me? setting up email error and online maintenance ?
That's funny!
What is hyper terminal?
Oh, like a snap shot of the page?
Is there a way of using the vendor version of techview on trane website, to log units?
C'Mon I know others have worked with techview.
Please, need some inside scoops.
Anyone familiar with techview? I don't work for Trane , but we use techview as a service tool to manage chiller controls, check operations and log manually.
Can anyone explain a way to log...
Thx nucl
No one work with techview?
Anyone?
Anyone with trane techview experience? I don't work for trane, but we use techview as a service tool to check control operations, logged chiller data.
I want to create log sheets directly from tv. ...
How about split case pump bearings?
At what temperature does bearing failure occur at?
Any tips for calibration setup/install?
Anyone got an iom manual?
Thx all
I have a rtac140 air cooled chiller we are thinking about going with the
U40100 ifm effector flow switch kit.
Anyone used it ?
I can't find the install manual anyone got one?
Anyone got any...
Thx all, I used the manual, there is a set of Ohm readings that must be read to confirm proper operations
Anyone ever worked with tracer es? Have any comments?
is this similar to tracer es :sev. pk 1??
Thx I will look into trying which will work
Any ideas or thoughts??
I have a air cooled trane , rtaa model. The chw pump is on a trane tr1 model danfoss vfd. The pump is as i describe "surging" the running frequency is quickly ramping up and down constatnly...
Someone had to of worked on this unit. Please help
Pefy p36 nmhu e
I found the Lev coil faulty and needs to be replaced.
Does anyone know if it can be replaced by accessing the side triangular panel? Or only through the bottom access panel?
Thx controldude!
Trane m#: Tch480a4oroa6kc5a
How should the dip switches be setup on the rtam board.
I would like to eliminate the ecomomizer from being used if possible.
Thanks davem
Here's the part
http://www.honeywellparts.com/4074eny-actuator-accessory-3-8.html
Now the actuator
http://www.amazon.com/gp/aw/d/B003CVV5SA/ref=redir_mdp_mobile
Any thoughts???
Digo its weird bc when you look online, the picture they show is a 90 degree angle piece of metal. Doesn't look anything like the slot on the actuator where your supposed to insert.
Thx all
anyone know how to go abot installing????
ML6161b2024 does anyone know how to keep.damper from opening up 100%, ?????I would like to make the max open at about 40-50% open instead of 100%.
Part #: 4074enj. Is that what it is used for???
Yes its a manual reset. I understand what you mean with the ramp up. The only thing is, that the
1. The fan has already been off fpr a minute or so, so I know theres no static let alone a high...
Factory wired to the mp581 panel. 3 wire..... in, out, gnd. 5vdc.
There are vav's down the line.
Read the.thread, I ran a test,..... ahu fan off , unplug 24vac to mp581 ( represent a power loss)...
Can see alarm from remote desktop workstation, reset from same place.
Alarm locks out s/s from starting ahu. Then when reset s/s.energized to start ahu.
Alarm reads.... High static.alarm
Ahu fan...
I have a mp581 trane ddc panel, upon power loss to the board, The ddc alarms a high static and locks out.
I ran a test. All I did was unplug the power to the mp581(24volt). Indoor fan shut down...
Got the static #s
Inlet at fan...... -1.85
Return plenum at filters........ -0.33
Dis duct.............................+0.15
What you guys think ????
If its food service be careful, gotta get everthing sized correctly, its a design issue.
Ohm phase to phase, 3ph. Should all be very near the same
Each leg at comp terminals to gnd, 0L at ALL phases.
If contactor is in ......line side to load side power is passing and compressor...
Thx for.all the respnoses, i gotta grab the manometer and check static. Its also possible that the fan is running outside the fan curve for the particular unit? And thats where the fan is...
I'm gonna chexk for any fire.dampers, i already opened up.all air dampers trying to see if that would alleviate sound
Could it be that the chw coils are plugged plugged???
No noise didnt stop when opening door
Thx all for your help,
Amps is well below, I was try to slow down fan to calm sound but it wasn't really working, rla... 9.7. Run amps... 4.7-5.0
Just from the sound of things without taking static...
Yeah could be, any ideas to test to be sure of this? I'm trying to find experiments to test this type of problem to make sure I make the right call, coil plugged restricted ret. Duct etc? Got any...
I have a 39LA carrier chw ahu, 1992 yr manufactured., belt driven. Making whoomping sound from supply duct side of unit, its a deep bass sound, traveling either from unit
I already replaced the...