What is BQT????
Type: Posts; User: berg2666
What is BQT????
I am a JCI employee I went to Tampa a few weeks ago to help. If interested I can tell you that the branch there is very busy If you do controls you will be very busy
Can you see what the device instance numbers are for the vmas
Choosing a controls contractor is going to be pretty easy if you want Tridium based Everyone has a Jace based solution, but wat about JCI, Delta, Automated Logic etc. As a JCI employee I am...
IS the BTI required or will the Jace or NAE in a bacnet router confugration work?
I am on a site were the BTI and the Envision 1.0 OWS is gone. There is a NAE on the job and the device is online but it seems to be an issue with the logic in the controller.
So lets talk...
SO your whole trunk is FEC with the instance number of 1, well a NAE doesnt care if a FEC has a unique number as the NAE only rellay cares about the Mac Address number. It is some bacnet service...
You can NOT discover the points out of the controller you need the PRN files from Hvac Pro or GX9100...
What part of it is not working for you it is a bacnet mstp device and BTL listed.
Enable the IP port under the Barnet network so it will route the points out and allow them to be discovered
You probably have a mstp trunk issue. Can you scan the trunk?
Dont beat yourself up. Evryone here started at the beginning at one time or another and needed some help. Experience Experience Experience......
Tha is 95 percent of the infoormation needed to contact a supplier. Where are you and what HVAC suppliers are around you ...
But I see you have six schools with Facilitator front end in place, so you have 1 N2 trunks with less than 50 devices under each. Make a list of each trunk and types of n2 devices under that trunk....
JCI FX also now comes licensed for MSTP out of the box. You will discuss the diferrent licenses needed with who ever yu get it from as they will have to license every option and therefore dicuss...
Each jace you buy will require a license to be purchased for each of them individually, no matter if you buy them one at a time or all at one time. They do come with a station right out of the...
I was under the impression each manufacturer provides a baseline K Factor for there boxes and then the TAB crew adjusts this after they actually dothe TAB on the boxes. Nothing magic there......
Yes were is it you are connecting t them from. Check your IP service at your house/office. That is the common link here, probably VPN issues........
Do you still have any of the MI files available, such as the NET ,GLOBAL, or NC files? Is the PMI OWS still online?
You can try to auto doscover them but I can not tell you that 100 percent for sure as I have personnaly not done a N2 Jace gig yet...
You need the same N2 poins out f the MIG that are located in the NCM. Get the Net, Global and NC files from the drive of the PMIOWS.
I have all the needed java files on my laptop and have no problem at all interafcing into a NAE or a Jace of any brand. Clear your Java cache in the Java control panel.
Why would N2 be listed on the BTL website???????
Cluck over the trunk then click the global search button...This will allow you to search the entire trunk. If you were clciked on a specific cntroller when you enetered the global search it only...
You can upload a NAE that is at a lower revision then your SCT but when you upload it it will be at the revision of your SCT........
Tuning policies check the max write time and see what it is then wait for that time and see if the read value comes back in that time
If you have it prior 4.1, you can download 4.11 or higher , it will license and mske the necessary changes...
Shoot a copy my way also Thanks
Can I get a copy of this program also? email in profile.
THANKS
Most N2 devices are self terminating. I would go find where they cut the wire and make sure there is no wires shorted together.
Check the focus tabs of the NAE and they will tell you the last time they rebooted.
Is it happening at midnight?
GO into Summit and check you CPL programs in it. If any
DOnt foget to check for any logic being done in the BCU Once you replicate that in the jace you will be ok.
What java are you running if its 1.7-25 you should instal the patch on the jace. Also go throuhg the instructions on niagara central about clearing java caches.
So do you have the N2 bus troubleshooting guide? This can help. Have you checked for duplicate dip switch addresses. One of your devices is prolly screwed up and draggin down the bus. Divide...
So first thing you do is check the basics. MSTP wiring basics,wiring temination, duplicate addressing, baud rate selection, max master, max info frames. How many devices are on that link. ...
I like the question about how many bacnet MSTP Climater MPC devices can go on a mstp loop. Lets go back to basics 32 before a repeater and lets go with 64 total.............
Now does it...
Reup this one. I am also interested in getting a copy this. I am not an expert at all about it and have only seen it once. So can you guys tell me the skinny on it.
Since the name of it is...
I personnaly just did a job where we installed a LCI-C in a 1999 RTAA. You could say it was plug and play as I did not have to change any settings in the RTAA itself. All I did is plug the LCI to...
Ok so are the UNTs failing or something I am not understanding why they are being pulled out. If it a quoted price from JCI and if they did not account for the NCE then they are going to be...
So were did the FECs come from? Sounds like someone did not complete their homework...
It would not wirk at the site because the jace did not find the DHCP server to get an IP and you probably wait long enough for it to default to a 169.254 address If a jace even does that. Once it...
It is a product that JCI is releasing on a case by case basis. They dont really want to use it but if the whoevers involved in the jobs will not allow a NAE then the BSC is th eoption. Branch...
Now the BSC(Jace NAE) can integrate anything a jace can.
Clarification I read in this staement that Rover can be used to configure programming in other manufacturers specifacally talking about JCI LN Builder.. Am I reading that...
Has anyone out there sucesfully did this???
Why not just remove the NCM and get the N2 driverr for the jace??? Is there any reason to keep it??? Sounds like more work then it worth.
Is the Jace licensed for modbus????
If so it is up to you but the bacent gateway will be much easier....
So you configured the LCI with the correct flash file for the chiller it is hooked toooo without using Rover