From an alternate perspective, you need to know What the Sensible Load requirments are for day/night based on a selected Inside Air set-point.
x
...
Type: Posts; User: dan sw fl
From an alternate perspective, you need to know What the Sensible Load requirments are for day/night based on a selected Inside Air set-point.
x
...
From an alternate perspective, you need to know What the Sensible Load requirments are for day/night based on a selected Inside Air set-point.
CFM = Sensible Load / ( 1.08 * approx. 18)
ie....
__Q = CFM * dT * 1.08
_CFM_ = Q / [ dT * 1.08)
_CFM_ = Q / 20 using dT =~18'F of coil
http://www.engineeringtoolbox.com/cooling-heating-equations-d_747.html
If the bedroom cooling loads are...