    The problem is the vapor barrier, You have a...

    The problem is the vapor barrier, You have a vapor barrier on the inside by using poly. The wall can't dry. You are getting a vapor drive from the bottom of the footer and that is probabky...
  2. To control humidity in the basement use foam...

    To control humidity in the basement use foam board on the walls. Do not use poly vapor barrier, as it will trap moisture and not let the wall dry. For the fish tank area use a dehumidifyer.
  3. Replies
    13
    Views
    6,283

    Unless you live in Minn., you should not use poly...

    Unless you live in Minn., you should not use poly on the inside of the wall. This prevents the wall assembly form drying. Take off the poly and repace with one of the new varying permeable...
  4. Replies
    26
    Views
    6,421

    Tundraotto--You are missing the point. The...

    Tundraotto--You are missing the point. The person who started this thread was worried about ice dams, not that he had ice dam problems. Why stick a hole in your roof that uses electricity and can...
  5. Replies
    26
    Views
    6,421

    Not trying to be a "harper" but pv's have never...

    Not trying to be a "harper" but pv's have never shown to save energy and usually increase energy use. Pv's are holes in the roof that use electricity, and cause problems. Its amazing how this myth...
  6. Replies
    26
    Views
    6,421

    Keepitsimplestupid--Your analogy of a fan in the...

    Keepitsimplestupid--Your analogy of a fan in the middle of the room does not pertain to a fan on the roof decking plane or a gable vent fan. Your analogy of a window frame fan not pulling air from...
  7. Thread: attic insulation

    by uktra
    Replies
    17
    Views
    3,575

    Johnsmitty---you didn't read what I said.

    Johnsmitty---you didn't read what I said.
  8. Replies
    26
    Views
    6,421

    Keepitsimplestupid--Wrong! Need to go back to...

    Keepitsimplestupid--Wrong! Need to go back to science class. If pressure is greater on one side of an opening air will go from high pressure to low no matter what size the hole is. Test after test...
  9. Replies
    26
    Views
    6,421

    newhomeboston---wrong! a fan will place a...

    newhomeboston---wrong! a fan will place a negative pressure in the attic. It will pull different amounts of air through any hole depending on the size of the hole. One cannot make the attic floor...
  10. Thread: attic insulation

    by uktra
    Replies
    17
    Views
    3,575

    Heat does not rise. Heat dissapates in any...

    Heat does not rise. Heat dissapates in any direction to a lower level of heat. Hot air will rise above lower heat air. Basements per square foot of surface tend to lose less heat to the...
  11. Replies
    26
    Views
    6,421

    From what you have said, I think you are overly...

    From what you have said, I think you are overly concerned about a problem that won't happen. Ice dams are caused by heat transfer from the rooms below to the attic roof. This normally happens along...
  12. Replies
    11
    Views
    1,834

    Better yet--get a whole house dehumidifyer to...

    Better yet--get a whole house dehumidifyer to handle the latent load and control humidity all year long.
  13. Replies
    11
    Views
    1,834

    You have to size heat pumps for both summer and...

    You have to size heat pumps for both summer and winter loads. 6 ton for your winter load is fine. For the summer load it is oversized. The solution that I use is a 2 stage system. The intial cost...
  14. Replies
    6
    Views
    1,909

    Fiberglass insulation is for conductive heat...

    Fiberglass insulation is for conductive heat loss. It will not stop air (convective heat loss). You must seal the holes from the attic to the rooms below, as well as having adequate insulation...
  15. Replies
    2
    Views
    1,043

    Most energy auditors can provide this if they...

    Most energy auditors can provide this if they have the manual J software program. Just ask.
  16. Thread: Radiant Barrier

    by uktra
    Replies
    120
    Views
    44,960

    Ibanda---Quit worrying about the temperature in...

    Ibanda---Quit worrying about the temperature in the attic, and be concerned about the energy transfer from the attic to the rooms below. The best things you can do is seal all the holes from the...
  17. Replies
    30
    Views
    6,402

    I have a hard time believing heating with Natural...

    I have a hard time believing heating with Natural gas in Texas is going to be cheaper than a two stage high seer heatpump even now, much less in the future. Natural gas production in North America...
  18. Thread: trane 15i or 19i

    by uktra
    Replies
    5
    Views
    3,032

    Baldloonie is absolutly correct. Here in...

    Baldloonie is absolutly correct. Here in Florida, humidity control year around is critical. Your home should be very tight (if the roof is airsealed properly--this is VERY important if you want the...
  19. You need to get an energy audit done. Call your...

    You need to get an energy audit done. Call your local utility and find the name of a person who can check the whole house. The exam should include a blower door test to see how much air leakage is...
  20. Thread: Foam Home

    by uktra
    Replies
    23
    Views
    4,557

    To design a energy efficient and comfortable home...

    To design a energy efficient and comfortable home with good IAQ, you need to take a "systems approach" to the home. This will provide the largest improvement from the least amount of building cost. ...
  21. Replies
    100
    Views
    30,760

    Pstu--the article in Home Energy also re-inforces...

    Pstu--the article in Home Energy also re-inforces why Lstiburek likes sealed conditioned attics!
  22. Pay to have an independant energy auditor/rater...

    Pay to have an independant energy auditor/rater do a load calc. Make sure that person performs a blower door test to check for air infiltration rate (every body else is just guessing-usually wrong)....
  23. Replies
    100
    Views
    30,760

    Number 1 is incorrect, number 2 is correct. That...

    Number 1 is incorrect, number 2 is correct. That is why even if you lower the attic temperature to the same as the outside the dominant energy transfer will still take place. There is no question...
  24. Replies
    100
    Views
    30,760

    Yes, once temperatures decline that will happen. ...

    Yes, once temperatures decline that will happen. Radiant barriers in Texas in new construction ae cost effective, in existing construction it all depends on cost of install and how long you will be...
  25. Replies
    100
    Views
    30,760

    jdb52--Insulation does not "unlode heat". It...

    jdb52--Insulation does not "unlode heat". It just slows the heat transfer. There are only three ways heat can transfer in an attic assembly. 1. Radiant (the dominant method). 2. Conductive (hot...
  26. Replies
    44
    Views
    27,190

    Tundraotto--check...

    Tundraotto--check http://www.buildingscience.com--you will find the answers there.

    Xavier--your analogy SUCKS just like power ventilators.
  27. Replies
    44
    Views
    27,190

    Whirlybirds are a poor way to ventilate an attic...

    Whirlybirds are a poor way to ventilate an attic assembly. Power vents are a very poor way to ventilate an attic assembly.
  28. Replies
    100
    Views
    30,760

    pstu--I am not trying to start a flame war...

    pstu--I am not trying to start a flame war either--however, you keep making statements like Pulte is not doing sealed attics anymore to try to prove Lstiburek is wrong, and "I keep looking for a...
  29. Replies
    44
    Views
    27,190

    Nothing like putting a couple of large holes in...

    Nothing like putting a couple of large holes in your roof during hurricane season here in Florida!

    Whirlybirds great for ice dams also. They pull the warm air from rooms below the attic, that...
  30. Replies
    100
    Views
    30,760

    It also involves how many heating degree days in...

    It also involves how many heating degree days in your location.
  31. Replies
    100
    Views
    30,760

    pstu--I don't uderstand your "dissatisfacton"...

    pstu--I don't uderstand your "dissatisfacton" with Lstiburek advising what to do with existing home attic construction. Joe is not in the renovation business, he is in the new construction and...
  32. Replies
    100
    Views
    30,760

    pstu--Joe likes the Aircycler because it is very...

    pstu--Joe likes the Aircycler because it is very low cost mechanical ventilation that he can sell to production builders. Does he say that is the only way to mechanically ventillate? No. Does he...
  33. Replies
    100
    Views
    30,760

    ptsu---the "hobby horse" that you claim Dr....

    ptsu---the "hobby horse" that you claim Dr. Lstiburek is riding is Secretariat. If you really took the time to study the man, you know that Joe gives several ways to do things depending on climate...
  34. Replies
    15
    Views
    3,081

    Mdrookie---If you want comfort as well as low...

    Mdrookie---If you want comfort as well as low utility bills, you must consider the house as a "system". I design energy efficient homes for a living. In your area a single zoned heat pump with...
  35. Replies
    14
    Views
    11,445

    Attic fans DO NOT save energy--period. ...

    Attic fans DO NOT save energy--period. Insulation above a non conditioned garage won't lower the temperature in the garage enough to justify the cost.
  36. Replies
    7
    Views
    2,305

    Majormickey--I can assure you the type of roof...

    Majormickey--I can assure you the type of roof makes a world of difference as to how much radiant heat, in summer, is transfered to the insulation below.
  37. Replies
    42
    Views
    90,105

    That is total B.S. There is no way you can...

    That is total B.S. There is no way you can determine energy savings by that method. Way too many variables.
  38. Replies
    42
    Views
    90,105

    cem-bsee---I don't think the edge you are on is...

    cem-bsee---I don't think the edge you are on is "leading". And since you cannot measure your consumption of electricity with all the variables involved, you don't have a clue about how much energy...
  39. Replies
    42
    Views
    90,105

    Ed--the scientific evidence of lowering energy...

    Ed--the scientific evidence of lowering energy use by power ventilators is in homes with little or no insulation in a vented roof that luckily had very few penetrations from attic to the rooms below....
  40. Replies
    7
    Views
    1,787

    The key is building the house as a "system". ...

    The key is building the house as a "system". Build the thermal envelope correctly to lower hating and cooling loads. For heating, if you build the home right a wood stove will heat it well. Make...
  41. Replies
    42
    Views
    90,105

    pstu--You did not step on my toe--the remark was...

    pstu--You did not step on my toe--the remark was not directed to you. The remark was directed to those that claim they save energy, but don't have any scientific data to back it up.
  42. Thread: New Construction

    by uktra
    Replies
    5
    Views
    1,599

    How big is the home?

    How big is the home?
  43. Replies
    42
    Views
    90,105

    There is no problem with the amount or accuracy...

    There is no problem with the amount or accuracy of research on powered ventilators. The huge amount of research clearly shows that code insulated ventilated attics do NOT save energy from power...
  44. Replies
    6
    Views
    2,080

    The problem with an accurate manual J calc in...

    The problem with an accurate manual J calc in regarding the two bedrooms over the garage is that the calc will not show the difference in airflow in those two rooms. Also the insulation in the...
  45. Replies
    41
    Views
    7,343

    Sorry, I just opened your plan. If you have to...

    Sorry, I just opened your plan. If you have to have airhandler and ducts in the attic, then you should seal the attic with foam. The only problem will be slightly lower shingle life (3-5% less), so...
  46. Replies
    41
    Views
    7,343

    Is it one story or two above foundation? Where...

    Is it one story or two above foundation? Where is (are) your airhandler(s) going to be placed?
  47. Replies
    41
    Views
    7,343

    Are you slab on grade, basement, or do you have a...

    Are you slab on grade, basement, or do you have a crawl? Are you one story above foundation, or two?
  48. Replies
    41
    Views
    7,343

    What stage are you in in the process of your new...

    What stage are you in in the process of your new home?
  49. Replies
    5
    Views
    1,805

    Filters in forced air systems are to keep the...

    Filters in forced air systems are to keep the airhandler coil clean. The idea that a forced air filter can make a real difference in indoor air quality is a myth. Uv lights are another myth--save...
  50. Replies
    41
    Views
    7,343

    It's not a question of being too lazy to open...

    It's not a question of being too lazy to open windows. As I said before opening windows may do no good and can present problems. The real key here is do you want to control ventilation properly or...