Thank you for this, that out of service got me on this. Once i set that to false it worked.
Type: Posts; User: droptchevy
Thank you for this, that out of service got me on this. Once i set that to false it worked.
Thanks @digo, i did watch a video on WPT but i dont have access to Schneiders tools. We are trying to figure out how to download Lon Smart Controllers from Visual Controls. It had a lonmaker database...
Does anyone have experience using Lon tunneling to download applications through a jace? My understanding is that it worked in Ax, but doesnt seem to work in n4 anymore. Im looking to use a external...
I had a old ax jace that failed, and all the graphics were done with gfxlibrary. Does anyone know who makes this and if they have a n4 version?
Have you had good luck with that one? I heard one of my buddies from another company say he found some issues with it. Does Vykon Pro work with all brands of workbench? It seems like it worked on...
I never liked using the one that comes in there. Grouping the failures together was not something that i ever liked. I had a nice 8 load lead lag block in ax that i could select how many loads i...
I was considering using the sunrise and sunset times. I see there is a sun down boolean point, but I wanted the ability to turn the outside lights on some amount of minutes before sunset. I cant...
I have a water meter consumption project. The gpm meters will pulse for a given amount of gallons. For instance pulse once for 10 gallons being used or whatever it is set at. Now i have this...
I haven't been using Spyders since the 3.6 build. I have a project that was spec'd out to be Bacnet Spyders so i am jumping back in the fun pool. I have not upgraded to 3.8 yet. Would you recommend i...
Thanks for the info Matrix. What is the Isoft Modbus?
It seems danfoss wants to make is as difficult as possible to bring their Vfds in over modbus. Does anyone have a Tridium for a Danfoss Fc series? I am struggling to get these points in. Any help...
I had one that kept jumping to february 16, 2016. It would exceed the max time change and the NDIO would fail everytime. It would come back after i rebooted it, but would happen again within a week....
Do you guys use/like the optimized start stop block that is in the Kit control palette? I wanted to see how well it works as i have not tried it on a live building. I have previously used my own...
Wow great post. Thanks that really helped a lot. Got it working now.
I need to link the current state, next state, and time until next state to about 50 Lon controllers. What is the easiest way to do this? I was trying to do it through the program service like i was...
I was using COV on all the controllers. I was told to disable COV and that would help. My understanding is that when you run Bacnet Ip and Mstp on the same jace, all the Ip points slow down to match...
Damn firewall got me
I have done quite of few projects with 3.4,3.5,and 3.6 but this is my first time using 3.7. For some reason i cannot get the jace to connect to the supervisor over the niagara network. I can get the...
Thanks guys you both solved my issues.
Im looking to create some logic if someone shuts the power off to one of the chillers. Since it will not see a actual alarm from the chiller i want to switch over to the other chiller when the comm...
Thanks guys i got it all figured out. Was pretty simple
Does anyone know if you can run a report to see which points are in override.
I have about 15 Bacnet Ip controllers on a jace right now. I got a call that air handlers were showing they were running when they were actually off. It appears the points are stale, because logging...
I need to learn a little more about writing custom blocks. My skills are not up to par to write my own yet.
I need to limit a percentage output over time. The spyder has a rate limiter that works and is exactly what i need. If only i can come up with something similar in a jace. I have had no luck so far....
yes i have suction pressure transducers and suction line temp. This is r134, but i can take the r-22 table and edit all the values to change it to 134.
Yea I am going to use a pid but I need the chart to know what the superheat is. I would need 50 reset blocks to try to make this so I'd rather write a custom module
Does anyone have refrigerant pressure temperature logic blocks or something they can share with me? I need to control exv's from superheat directly in the jace. I was trying to play around with...
I have some Mcquay units with bacnet cards. 2 separate buildings with 2 rooftop units on each jace. Sometimes it happens a few times a day and sometimes it will go days without happening. The units...
It is Bacnet Mstp ftom the sitelink to my jace. I have brought in other several different types of Bacnet devices in the past and never saw this happen
I was working with Liebert yesterday to connect 4 units to their Site Link and then communicate over Bacnet to the Jace. We we able to get the devices communicating and i was able to discover the...
I am using the n2 driver for the first time to test before taking over the first building. I was able to bring in the devices and manually add points to my VND device (TEC1102 and TEC1202). I know...
exactly what i was looking for. Thanks
When you right click on a point and go to actions it gives you options like override,emergency override,emergency auto,auto, and set. How do you remove some of those to only display something like...
Nevermind, answered my own question. Spyder inputs are only good to 100k ohm, and the sensors at 100k at 77 degrees. Not gonna work. Guess i need to order some 20k.
Im taking over a older control system with Spyders.The existing system has 100k ohm sensors. Does anyone have a solution for bringing in custom sensors that are not listed? I figured i could create...
yes orion you are right. I am getting a analog value from the bacnet card on a mcquay turbocor chiller. I was trying to convert that to kwh. Ill give the totalizer function a try.
im a little confused by this block. It looks to take a pulsed input. How do i convert the kw to go into this block to get kwh? Maybe im missing something
A Mcquay chiller i have only gives me Kw. I need to get Kwh. I read somewhere someone used a numeric totalizer and divided it by the interval time. I was going to take a minute interval, and divide...
After rebooting the Jace, the points are now starting to come in. I dont know if the problem is resolved. Ill wait and see if they go to stale mode.
I am having trouble bringing in the Danfoss Bacnet Vfd points. I was able to address them and discover them on the network. The points can be discovered and show actual values in the upper screen....
Good point on the legal aspect.
It looks like tridium makes a module that you can license designed specifically for tenant billing. Im checking into pricing on that
May have just answered my own question. Found the multi vibrator which i can use with the counter. I can reset the counter and just use a switch to pass through the vibrator when enabled.
I have a customer that wants to create an after hours timer to monitor and bill the tenant on their usage. I dont see any blocks to use to start counting. I see the counter, but it looks as i will...
Yes this can be done. I dont remember exactly how I have done this in the past without having it in front of me, but i know i have done it. After you replicate it i dont think it will let you drop it...
Some of my nvo_Io UI's are not working properly. The ones i am noticing are for temperatures. Some of them are reading much lower than they should. This is happening on several controllers. I have...
also does anyone have a yorktalk2 that they have brought in also? Looks like this one has to be brought in manually because nothing is named?
Does anyone know what the conversions are? I changed the facets when i brought in my proxy points, but the temps and pressures are way off. Temps,pressures, voltages are all off
Temps are in in...
1. You are right, they should have just taken the top platform out and set it on the existing one.
2. You are right again- It was a government building.
Doesnt it feel good to to be right
The frame was welded to the i beams. You can see the welds in my other post " Weld of the year award". This unit was a change out so they just dropped it on the existing i beams. Must have been low...