Search:

Type: Posts; User: rover

Page 1 of 2 1 2

Search: Search took 0.01 seconds.

  1. Replies
    8
    Views
    3,248

    Open drive york, sat idle for to long??, we have...

    Open drive york, sat idle for to long??, we have strapped heaters to motor belly, no motor likes moisture at windings??
  2. Replies
    8
    Views
    3,259

    Efficient why, you just rebuild and chiller not...

    Efficient why, you just rebuild and chiller not tight???
  3. Replies
    8
    Views
    3,259

    York purges don't suck, york use gaskets not...

    York purges don't suck, york use gaskets not o'rings or flat face like trane's new gear.

    If your purge is doing work you have a leak.
    I
  4. Replies
    22
    Views
    6,988

    No, you could run it at minimum load and allow...

    No, you could run it at minimum load and allow purge to take care of it, would need to be watched carefully though, negative pressure can be a real pain, if every manufacturer of negative pressure...
  5. Replies
    12
    Views
    8,972

    I agree 255 rthb exv could be on the cusp of a...

    I agree 255 rthb exv could be on the cusp of a bigger capacity machine, limit the exv steps, bank up in condenser give it some liquid to boil off and raise low side pressure, were you seeing low...
  6. Replies
    33
    Views
    22,994

    Carrier or york never had this problem with there...

    Carrier or york never had this problem with there chillers, maybe Trane go to single stage , then casing movement horizontally and vertically at elbow lockdown wouldn't be a problem.

    Can anyone...
  7. Replies
    33
    Views
    22,994

    Are they using goretex tape on elbow to...

    Are they using goretex tape on elbow to compressor these days??
  8. Replies
    33
    Views
    22,994

    Never seize, not a problem , I have heard of...

    Never seize, not a problem , I have heard of trane factory techs saying a wire wheel is TOO abrasive at flange faces ??. Regarding reassembly torque and sequence, is that really a problem?? would...
  9. Replies
    53
    Views
    24,705

    I believe email/ westinghouse could have...

    I believe email/ westinghouse could have developed the movable diffuser, not that easy to set though back in the day, also think a lot of the problems could have been due to the float system, have...
  10. Replies
    16
    Views
    4,393

    Refrigerant was previously removed, waterside...

    Refrigerant was previously removed, waterside drained (we are not looking at tube failure), there will be no issues with igv or comp bearings, nitrogen was purged and heat lamps utilised at vessels,...
  11. Replies
    33
    Views
    22,994

    Economiser, suction elbow etc, just pay a proper...

    Economiser, suction elbow etc, just pay a proper insulation tradesperson to carryout work, vapour seal no air, no corrosion.
  12. Replies
    53
    Views
    24,705

    So york developed the movable diffuser?, one...

    So york developed the movable diffuser?, one reliant on oil pressure or electronics?, just curious, who knows what banner they are flying under now, got a few pe (westinghouse), 1972 design still...
  13. Replies
    53
    Views
    24,705

    95% of times the chiller is blamed. Try...

    95% of times the chiller is blamed.

    Try checking for field related problems, (UNLESS york /jc r&d is not up to scratch)
  14. Replies
    16
    Views
    4,393

    York R123 Cleanup

    Working on york R123 chiller at moment, this machine open for sometime ( due to customer not approving works) , just briefly I usually install driers across cooler/evap, utilising high side pressure...
  15. Replies
    33
    Views
    11,241

    Chances are if you have a leak, those needle...

    Chances are if you have a leak, those needle bearings are already close to binding.

    On our leakers, we always give client the option to changeout bearings on first stage, funnily enough not to...
  16. Replies
    33
    Views
    12,600

    My experience, My experience, Run into...

    My experience,


    My experience,

    Run into one of these Trane gurus??, 15 years working as a mechanic.

    Installed an after market soft start upside down, (cheaper for the company he was...
  17. Replies
    18
    Views
    8,708

    No one has had issues with IGBT, soft start or...

    No one has had issues with IGBT, soft start or PWM modules???
  18. Replies
    33
    Views
    12,600

    A few split pins, dowelling, one seal tight, the...

    A few split pins, dowelling, one seal tight, the rest so wide ???.

    Why don't we make some easy money, and get the chw plant doing what it should be.

    Any monkey can rebuild a chiller , takes a...
  19. Replies
    18
    Views
    8,708

    Thanks for response. Thought parts would be a...

    Thanks for response.

    Thought parts would be a problem, especially vintage chiller I'm looking at.

    Whats your opinion on Turbocor compressor chillers???
  20. Replies
    18
    Views
    8,708

    Westinghouse/ Email PE centrifugal compressors

    Fellow workers,

    Anyone currently overhauling this brand and age of chiller, from what I know McQuay/ Daikin have basically re-badged them.

    I have rebuild service instruction on PE compressors...
  21. Replies
    33
    Views
    12,600

    GEEZZ boys was just having a bit of a joke, was...

    GEEZZ boys was just having a bit of a joke, was fully aware trane make gear driven, have worked on a few, however I always like to throw the trane vs york thing in.:cheers:
  22. Replies
    33
    Views
    12,600

    Trane chiller techs

    Gents,

    Why is the rebuild so easy on a trane chiller compared to a york , have trane done a geared drive in recent years , yes. many years ago, 20 thou ho ho
  23. Thread: rtaa 80 question

    by rover
    Replies
    16
    Views
    3,995

    A nuisance when it came to logging

    A nuisance when it came to logging
  24. Thread: rtaa 80 question

    by rover
    Replies
    16
    Views
    3,995

    Of track what about rthb on R22

    Of track what about rthb on R22
  25. Replies
    13
    Views
    2,949

    Cant read

    Cant read
  26. Replies
    13
    Views
    2,949

    Give him a service bulletin or rebuild bulletin...

    Give him a service bulletin or rebuild bulletin thats all he wants
  27. Thread: rtaa 80 question

    by rover
    Replies
    16
    Views
    3,995

    Lets face it temp sensors are cheaper than...

    Lets face it temp sensors are cheaper than tranducers. However transducers are still utilised for more important safeties on some machines.

    Have heard of control software problems on UCP2 ...
  28. Replies
    15
    Views
    3,314

    What exactly

    What exactly
  29. Replies
    22
    Views
    4,043

    If you dont have an independant purge , id be...

    If you dont have an independant purge , id be pressurising and leak test. Especially if you suspect significant leaks. Do oil analysis to.

    Yorkies, have fun with the discharge flange to condenser...
  30. Thread: welch pumps

    by rover
    Replies
    10
    Views
    2,555

    Been chasing a good one for a while now, do they...

    Been chasing a good one for a while now, do they have non return valve if power fails etc , pass on details if you guys recommend them , I have always been a fan of the belt driven ones though,...
  31. Thread: screwy sound

    by rover
    Replies
    40
    Views
    8,863

    RTAA I assume you have more than one compressor...

    RTAA I assume you have more than one compressor on this chiller, do nothing , let it run , if it blows then you know it was a screwy sound.
  32. Replies
    56
    Views
    19,868

    Touchy subject??? Some do mechanical some do...

    Touchy subject??? Some do mechanical some do software /controls , however im always the one do mechanical at 2 am in the morning.
  33. Replies
    20
    Views
    5,457

    Would I be correct in assuming tolerances are to...

    Would I be correct in assuming tolerances are to tight to do repairs in the field and the only option is send back to manufacturer
  34. Replies
    56
    Views
    19,868

    Have had a few motors go on cvhe's haven't worked...

    Have had a few motors go on cvhe's haven't worked on to many cvhf's.

    We get motors overhauled by shop that predominately does heavy equip, mining and process plant.

    Havent had any dramas.
    ...
  35. Thread: SB 5 RTAA

    by rover
    Replies
    12
    Views
    3,561

    I agree 100% . I wasn't commenting on exv upgrade...

    I agree 100% . I wasn't commenting on exv upgrade being a solution to head pressure problems etc. Just trying to inform that there are upgrades available. However is soft loading the only option .
  36. Replies
    26
    Views
    5,905

    Interesting, what seal pressure do york recommend...

    Interesting, what seal pressure do york recommend when you buy this valve. You got any info on these
  37. Thread: SB 5 RTAA

    by rover
    Replies
    12
    Views
    3,561

    Majority of calls to these chillers I have found...

    Majority of calls to these chillers I have found are due to oil problems but are not oil related as such , head pressure control to these chillers is essential, if you have failed fans etc you will...
  38. Replies
    26
    Views
    5,905

    I agree with 123 statement

    I agree with 123 statement
  39. Replies
    26
    Views
    5,905

    Install washers to increase flow

    Install washers to increase flow
  40. Replies
    26
    Views
    5,905

    2-3 works

    2-3 works
  41. Thread: SB 5 RTAA

    by rover
    Replies
    12
    Views
    3,561

    I got it , whats the go though, you seem to ask...

    I got it , whats the go though, you seem to ask for a lot of service bulletins , manuals etc reading won,t teach you everything
  42. Thread: CVHE teardown

    by rover
    Replies
    9
    Views
    2,997

    Wouldn't be to concerned about diffuser plate,...

    Wouldn't be to concerned about diffuser plate, rebuild both igv assemblies, have had refrigerant meet its critical point in the past, freon fire, who knows though???
  43. Thread: CVHE teardown

    by rover
    Replies
    9
    Views
    2,997

    You would have heard a rattle/ hum at the 2nd...

    You would have heard a rattle/ hum at the 2nd stage end if the igvs are lazy when chiller was running. Sounds like oil pressure loss or bearing failure at drive end and and she smashed up. How were...
  44. Thread: York Screw 2

    by rover
    Replies
    8
    Views
    2,474

    Let me help you. MORE INFO

    Let me help you. MORE INFO
  45. Replies
    82
    Views
    43,744

    You don't control chiller plant call or stage up...

    You don't control chiller plant call or stage up do you . See if chw pumps are running on or starting when they shouldnt be. Oil sump on rthd sits above cooler vessel.????
  46. Replies
    32
    Views
    15,522

    Right on

    Right on
  47. Replies
    32
    Views
    15,522

    Missing screw from igv asembly????

    Missing screw from igv asembly????
  48. Replies
    3
    Views
    1,458

    Plenty of info for you, what machine in specific...

    Plenty of info for you, what machine in specific screw, turbocor.
  49. Replies
    10
    Views
    4,107

    Two chillers lead/lag I would assume. EXV...

    Two chillers lead/lag I would assume. EXV position should tell the story. Pretty sure these chillers rely on adequate pressure differential to load.
  50. Replies
    53
    Views
    13,664

    Starve the cooler , ratio increases, suction...

    Starve the cooler , ratio increases, suction sheat increases as does discharge superheat. If u have a chiller controlled by condenser level (hi side float) that float will look after only one...
Results 1 to 50 of 81