Your problem with WIC freezing used to intermittantly occur from
solenoid coil residual magnetism.
You said that a solenoid was changed in jan, what about the other one?
The problem is likely...
Type: Posts; User: IRBH
Your problem with WIC freezing used to intermittantly occur from
solenoid coil residual magnetism.
You said that a solenoid was changed in jan, what about the other one?
The problem is likely...
Running for 2 weeks, eh?
If the vapor barrier were on the wrong side, the insulation would probably now be getting damp.
I would inquire.
Sounds like the old cooler also had problems.
Bbeerme, the concern is the immediate capacitor failure due to welding of the points,
not the attempt of extending point life, which Tecum doesn't even mention.
cheers
Tecumseh Products co in disagreement
One more time... directly from Tecumseh Service Data manual
"RSIR-Resistance start-Induction Run
This motor is used on many small hermetic compressors...
The motor has low starting torque...
Is it too late for you to edit your reply?
Scan back to post #13, second paragraph explains that sticking
potential relays kill capacitors.
What the heck?? YOU POSTED IT!
Halloween prank of a devious mind??
Hay, Farm tech
I scanned the thread, and if this farm is on a lengthy AC grid,
you may be getting excessively hi voltage at early am milk time.
The replacement capacitors had bleed...
Unless I misread the above 71Chops quote, it is incorrect.
A capillary system's off cycle equalization allows use of a RSIR
compressor that would be clicking on overload on a txv system.
An...
In this neighborhood, would lead to confusion
vis a vis connecting to a Remington 870 pump.
Won't be surprised if they're assembly line cold solder joints,
or overheated oxydized joints that are foil-thin.
Previous pic... note the tiny 1/4w resistors popped,
all signal diodes under the hi-water line are open.
Trace side of board, note corrosion setting in.
In conversation, customer complained...
Been asked to find the cause of half a dozen WF geo
failures, mosty for "no apparent reason".
First one quite obvious.
Since you're known to toy a bit with firearms, ga-hvac, you'll know that
the Whitworth name is also associated with an accurate
mid 19th century percussion firearm.
Sub-calibre (for its day...
Snapperhead, I've watched the decline of the domestic fridge through forty some years.
Used to be a stat, clock and dts that were reliable & cheap.
They learned to pile everything on an...
Your president Trump's wall... sounding better & better.
Remember, on a 20 deg f day your car ac compressor will not cut in because of the lps, or an ambient sensor.
And the fact that you're losing heat thru the evap before the heater coil?
Up here...
David, what is the defrost schedule?
What's happening is that you are believing that sentence to actually carry accurate technical information-which it does not.
Well CRussell, we've solved enough for tonite.
I'm heading for...
Really?
You would change the TXV element based on the given info?
So, what's the purpose of the TXV?
That's right... to control SH.
So, what's the SH of this system?
We have no idea...
Huh, never heard of them, must be a 'Merican thing?
So if a mere 1/4 turn of the TXV brings you 3 deg c closer to your setpoint, why not just do a proper SH adj on the txv?
At least before changing txv, element or screen.
Ok, "Batoche Bob" eventually see you over there.
Just by your other handle, the design temp raises to -36c
Our co used to send in the Simpsons for regular calibration.
Re: scope and watching your grnd potential...
I sure learned that in my snow machine racing days.
Hooked up oscilloscope to sled ...
Get caught like that a few times and my analog Simpson doesn't look quite so silly.
An analog meter can perform some tasks that a digital cannot do.
Welcome aboard, Bill mcC.
It's also helpful to amp out a control ckt thats burning xmers, coils & fuses.
Any coil that isn't pulled fully in & shunted is in overload condition.
Hi, SaskBob, I can't help you, just curious what your discharge air is in the closed loop to air system.
And the units were sized for -30c(-22f)?
You know that, for example, PA has an
...
Something's off in this thread.
If we can accept op's statement that he had 24v
"ACROSS THE COIL " (not at the flag ends),
why are you all.. except Indy, running around saying that you...
balakumar, if I may go on a tangent...
Have you looked into the increase of a liquids' thermal transfer coefficient with the addition of a "water wetter"?
Seems the lowering of the surface...
With 28/400 maybe the showers cooled that 60c (140f ) condenser?
Isn't -5 (5"hg) pumped down enough? Sure would be with a scroll.
Adjust the LPS.
good luck
It's all ok, as answers and final analysis may be somewhat off.
Farm tech, all the dairy & pmu tanks I've seen have receiver equipped cond. units.
Why bother with sc readings, or is it specifically asked for in the equipment manual?
This IS a milk tank...
...
They were a well built, long lasting unit.
The compressor's dual capacitor has one section connected between S & R via the contactor load terminal, as normally done.
The other section is...
Seriously could hear the "kerplunk" of hundreds of motors.
" Techs" elated that Samgevas found the solution to the throw-away motor!!!
:troll2:
Sam, awaiting the
"Had you going there-just kidding"
post.
Sam, awaiting the
"Had you going there-just kidding"
post.
Fatkey, you should be clear to send me your resume' via PM now.
My email is tied in with my outdoors ventures, so I'm kinda loath to involve it.
I will even kick in the stamp to Ireland for...
We need the size of the other coil so I don't have to guess by max txv capacity.
I doubt this system ever really worked.
Why have it short on evaporater capacity if changing from 13f td to...
I believe the LAL 310 has about 33kbtu @ 25f . Coupled with the 7k coil and allowing 12kbtu for the 1 ton txv fed coil, it appears balance point is about 25000btu @ 22f with 13f td. That's ...
Is a cv like your resume or what?
If so, pm it to me and I can translate it so no one from the British Isles can understand it.
That is the objective.
You may have to accept Matt as your...
First thing Asm, your hi side shouldn't even be hitting 300.
Clean the condenser.
Then, with all the crap you found, make sure a previous "tech" never upsized just the compressor on the...
Also, I believe that the thinner, longer wires in the start winding have more inductive reactance.
Interesting bit on the uneven rotation of motor...
Geothermal AHU from new was rumbling &...
A bit of troubleshooting right there... it being temperature-dependant & not a total false alarm.
I think he means "max capacitor operating voltage"
in which case he's correct...v drop divides evenly across the two diaelectrics.
Actually, no, PHM.
My problem is that I seem to have an opinion on everything, which is ok if I could keep my mouth shut.
Teacher said that his friend's bow is so powerful that the arrow...
Yeah, it comes with old age.
{Spoken in the voice of an old man}.
My attitude came at age fifteen- that's when the physics teach slid my desk into the hall for the year.
Icy... I too must apologize, my thought was that I would approach the troubleshooting differently.
Your wrapup of us all arriving at the same conclusion is dead on.
The terrible loss of the...
With all due respect-you're wrong.
What you have is cause AND effect at the same location.
Re-read my post... L2 handled the SAME current that destroyed L1, just fine.
If you chose to...
The rest is of no consequence...the heat & destruction is caused by resistance at the point of damage.
Remember, on a working system L2 is carrying the identical current as L1.
HVAC's nursery...