Search:

Type: Posts; User: jemawalton

Page 1 of 10 1 2 3 4

Search: Search took 0.01 seconds.

  1. Replies
    4
    Views
    1,899

    If you could post a Serial number and...

    If you could post a Serial number and specifically what error codes or faults you are seeing that would help us know more about the issue.
  2. My money is on the slide valve being stuck or...

    My money is on the slide valve being stuck or rotor locked. Either way you need to isolate and evacuate the compressor and do some internal checks. The tolerances in these compressors is so tight...
  3. Replies
    13
    Views
    2,459

    Good looking install. Any reason behind where...

    Good looking install. Any reason behind where the nipples got placed in the condenser?
  4. Replies
    15
    Views
    2,747

    I would highly recommend reaching out to the...

    I would highly recommend reaching out to the sales office of the big 3 in your area. With those types of quantities, they can get down and dirty cheap. You wave a PO for 150, 10 ton units under the...
  5. Replies
    3
    Views
    1,429

    Got a model #? I have changed out a few way back...

    Got a model #? I have changed out a few way back in the day but I don't even know that the parts would be available now.
  6. Thread: Trane cgam

    by jemawalton
    Replies
    3
    Views
    1,424

    Always a good idea to capture data and chiller...

    Always a good idea to capture data and chiller logs prior to update to have the information backed up but you shouldn't have to manually input the info unless changing the dyna view panel itself.
  7. Replies
    17
    Views
    9,740

    If I remember I was told that it started in the...

    If I remember I was told that it started in the spring of this year. Not sure if they got mfg'd before the roll out date maybe?
  8. Thread: trane rtwd

    by jemawalton
    Replies
    24
    Views
    11,620

    You need to find the design of this machine. ...

    You need to find the design of this machine. Drawings, T&B report, something to tell you where you need to be. Pueblo can tell you specs on the machine and what it was designed to do. Get the...
  9. Thread: trane rtwd

    by jemawalton
    Replies
    24
    Views
    11,620

    How is water flow in relation to design?

    How is water flow in relation to design?
  10. Replies
    14
    Views
    7,244

    Go for what you want. If you don't like it move...

    Go for what you want. If you don't like it move on. The skills you pick up on one or the other will translate to the next oportunity. Don't know of a company that does both though.
  11. Replies
    17
    Views
    9,740

    Factory installed on RTAC and CGAM now!!!! ...

    Factory installed on RTAC and CGAM now!!!! Whoot!

    Love them.

    Not sure why we can't get them to factory install on CTV. Our office seem to like Orange Research for Centravacs....I will...
  12. Replies
    15
    Views
    4,299

    I have seen my share of Redi-Purges foul up. ...

    I have seen my share of Redi-Purges foul up. Plenty of crap on the liquid float that seems to need to be replaced annualy. Lots of liquid drain solenoids stopped up with crud.....

    Just my $.02
  13. Thread: trane rtwd

    by jemawalton
    Replies
    24
    Views
    11,620

    Can you give us a full set of numbers? Water...

    Can you give us a full set of numbers? Water temps, ref pressures and temps etc?
  14. Replies
    33
    Views
    22,994

    OK Jay, why no 515 on the suction cover to...

    OK Jay, why no 515 on the suction cover to suction ell? You have to put something on it because it is the shallowest groove and the ring won't stay. Especially since it often has to slide into...
  15. Replies
    25
    Views
    16,919

    We just replaced every heater in a central plant...

    We just replaced every heater in a central plant with 4 duplex machines. All of them drawing between 3 and 4 amps a piece and struggling to maintain temp.
  16. Replies
    14
    Views
    9,230

    Only if you hold it in your left hand.

    Only if you hold it in your left hand.
  17. Replies
    14
    Views
    3,842

    Hope you never have to work on it. What a mess!

    Hope you never have to work on it. What a mess!
  18. Replies
    52
    Views
    19,526

    When you say trouble, do you mean that they need...

    When you say trouble, do you mean that they need help with electrical troubleshooting or with actually reading the diagram symbols and tracing the circuit?
  19. Replies
    14
    Views
    3,635

    Who needs a heat pump thermostat? A handy switch...

    Who needs a heat pump thermostat? A handy switch like this will solve the problem! Too bad Billy Mays is not around to market it.
  20. Thread: Trane RTAA

    by jemawalton
    Replies
    18
    Views
    10,863

    The biggest problem I have with these sensors are...

    The biggest problem I have with these sensors are the wiring connections on the board. I hate those connectors. A poor connection here will give you strange readings.
  21. Not to be rude but I think you need to spend some...

    Not to be rude but I think you need to spend some more time researching and reading on this site. All the questions you asked have been answered several times over here. Use the search function and...
  22. Replies
    38
    Views
    8,463

    Phisher nailed it. Circuit 2 is closer to the...

    Phisher nailed it. Circuit 2 is closer to the EWT sensor, therefore with low flow the temp drops there first.
  23. Thread: OH DAMN IT!

    by jemawalton
    Replies
    12
    Views
    3,655

    WHEW! Glad you cleared that up for us! Please...

    WHEW! Glad you cleared that up for us! Please let me know which brands you think aren't crap so I can post some pictures of them in less than flattering circumstances. They all break and if they...
  24. I can't confirm the 90 day money back trial but I...

    I can't confirm the 90 day money back trial but I can confirm the Dolphin being removed from several sites around here after about a year due to poor performance.
  25. Replies
    40
    Views
    8,863

    If the oil line solenoid did not shut the chiller...

    If the oil line solenoid did not shut the chiller should throw a diagnostic that it did not see the oil pressure differential trip the switch on shutdown. Can't remember the specific diagnostic off...
  26. Replies
    26
    Views
    6,871

    http://hvac-talk.com/vbb/showthread.php?t=145816&p...

    http://hvac-talk.com/vbb/showthread.php?t=145816&page=4


    Is this the thread?
  27. Thread: Trane RTAC

    by jemawalton
    Replies
    12
    Views
    4,385

    Some Trane chillers use a brazed plate as well.

    Some Trane chillers use a brazed plate as well.
  28. Thread: Trane RTAC

    by jemawalton
    Replies
    12
    Views
    4,385

    He said he wasn't bright.

    He said he wasn't bright.
  29. Thread: Trane RTAC

    by jemawalton
    Replies
    12
    Views
    4,385

    Digit 15 is "F" which indicates a standard evap,...

    Digit 15 is "F" which indicates a standard evap, not remote.
  30. Replies
    17
    Views
    4,052

    Break out the heat gun and the patience. Don't...

    Break out the heat gun and the patience. Don't let the customer or the boss push you cause replacing tubes sucks!
  31. Replies
    13
    Views
    4,461

    You might want to start a new thread with this...

    You might want to start a new thread with this issue. You will have better results getting responses.
  32. Replies
    20
    Views
    4,295

    I thought the same thing at first but then I...

    I thought the same thing at first but then I realized he is probably refering to a chiller than dumps directly into a chilled water sump or other storage vessel.
  33. Replies
    20
    Views
    4,295

    I would think that would make the outlet pressure...

    I would think that would make the outlet pressure 0 and your calculation would be based on the inlet pressure.
  34. Replies
    20
    Views
    4,295

    If the startup guy was nice to you, he would have...

    If the startup guy was nice to you, he would have written the design specs on the inside of the control cabinet with a Sharpie.
  35. Replies
    8
    Views
    9,375

    Filter is supposed to be changed within the first...

    Filter is supposed to be changed within the first year of startup but it never does. But you are right, I have found the line about being a "lifetime filter" to be less than accurate on more than...
  36. Replies
    38
    Views
    7,447

    Thats helpful! Funny and original too. An all...

    Thats helpful! Funny and original too. An all around insightful, high quality post that makes this forum that much better! Bravo!
  37. Thread: RTAA340

    by jemawalton
    Replies
    19
    Views
    4,380

    Can you tell that the unload solenoid is in fact...

    Can you tell that the unload solenoid is in fact energized? (Small screw driver works nicely for this) What is the piston pressure doing while the machine is trying to load? Serial number on the...
  38. Replies
    23
    Views
    9,908

    It's in there, I promise........

    It's in there, I promise........
  39. Replies
    23
    Views
    9,908

    CVRD-SVN06A-EN is the CH-531 Starter only...

    CVRD-SVN06A-EN is the CH-531 Starter only installation manual. There might be some info in there to compliment what you already have. I don't have an electronic copy on my laptop or I would have...
  40. Replies
    9
    Views
    2,152

    I have always wondered why we dont measure...

    I have always wondered why we dont measure condenser approach as the liquid temp and the entering water temp. When we measure evap approach we want to know how well we transfered heat from the water...
  41. Replies
    7
    Views
    2,396

    I wonder if that same company gets to profit from...

    I wonder if that same company gets to profit from changing compressors out after they take a crap from eating too much liquid refrigerant.
  42. Thread: trane cvhe

    by jemawalton
    Replies
    15
    Views
    10,060

    Not to get picky but the black classic does see...

    Not to get picky but the black classic does see momentary loss of power. It's called a distribution fault.
  43. Replies
    39
    Views
    8,678

    But you still have to haul that stuff up a...

    But you still have to haul that stuff up a ladder, freeze in the winter, fry in the summer and get wet when it rains.
  44. Replies
    12
    Views
    2,157

    Y-delta or across the line start?

    Y-delta or across the line start?
  45. Replies
    12
    Views
    2,157

    If you have proper voltage across all three legs...

    If you have proper voltage across all three legs and are not seeing an amp draw on the second leg, combined with poor meg readings, sounds like an issue with the compressor itself. Does the...
  46. Replies
    7
    Views
    2,634

    Yes. There should be a twisted wire and a tab on...

    Yes. There should be a twisted wire and a tab on the side of the valve that will be broken if your valve has poped. Let us know the model and serial # and we can probably do a better job helping.
  47. Replies
    5
    Views
    1,428

    You are correct. As the air flow increases, the...

    You are correct. As the air flow increases, the VDC signal also increases. When you recalibrate the VAV, what should happen is the damper should drive completely closed, it will then measure the...
  48. Replies
    12
    Views
    2,157

    Did you meg the compressor with the motor leads...

    Did you meg the compressor with the motor leads on or off? Issues with the motor leads in the conduit can cause erratic meg readings. Does it trip on start-up, or while running? Y-delta or across...
  49. Replies
    18
    Views
    9,559

    Post the serial number so we know what era...

    Post the serial number so we know what era machine you are working with.
  50. Replies
    8
    Views
    2,414

    I know that Marley will package their tower in...

    I know that Marley will package their tower in pieces. They should be able to give you component sizes so you can figure how best to get them to the roof. I am not sure if Marley feild assembles...
Results 1 to 50 of 474