These cases have pulse flow controlled
independently through the top coil and the pans.
When setting up the case for refrigeration treat
the top coil and the chilled deck pans as if they
were 2 separate temperature controlled circuits.
Each circuit will use its own temperature sensor
to cycle between the cut-in and cut-out values
show on pages 26-27 by opening and closing
the 2 flow control solenoids on the return side of
the case piping station. The defrost for the 2 circuits
must be synchronized. Timed-off defrost
is all that is required. If warm fluid defrost is
used on the top coil the pans must remain timed
off defrost synchronized to the duration of the
top coils. :gah: